Is NFPA 13R OK for Any Type of Live/Work?

1/18/2024

7 Comments

 
I am working on a permit for a 1,500 sqft (750 sqft/ floor) new construction live/work building R-2 in California (2022 California Building Code, which is based on IBC). It has a 1-bedroom apartment above with only "work" space below.

The building code allows for Live/Work R-2 to be protected with NFPA 13R. In the building code the only uses not allowed in the "work" area of Live/work are Group H & S.

Where all of this gets hazy is that I interpret the code as 13R being allowed to protect this whole building regardless of use except for uses S or H.

For instance would a small pizza joint be allowed in this "work" space as long as it did not have special hazards that would require an ANSL or NFPA 13 system?

Or is Live/Work with 13R just purely limited to office, barber, professional space, etc.?

From multiple angles I am trying to understand the true limits of Live/work when there are no local ordinances that limit the "work" space use except S & H.      

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Jesse
1/18/2024 08:10:48 am

I would consider the "work" portion of live / work to be incidental and Light Hazard. The pizza place you refer to is OH1 in the service area. I wouldn't consider this applicable

Reply
Joe
1/18/2024 09:35:07 am

The live/work projects we have worked on were required to be designed to OH2 due to a potential M or Mercantile Occupancy. Light Hazard or OH1 would also be allowed within the live/work units.
However if the R2 areas are properly fire separated from the M/S/H occupancies of the unit, the fire sprinkler demand for the work area would typically be based on room design method which is typically smaller and less demanding than the area density requirements.
The R2 areas could be designed according to 13R, again only with proper fire separation.
The problem was not being able to install CPVC pipe within the work areas (Ordinary Hazard), we had to install Steel or Copper Piping.

Reply
Anthony
1/18/2024 10:04:58 am

In the hundreds of such mixed use buildings I've designed over the years I have always approached the process as such: "R" = residential, everything else is commercial. At best you have a ground floor that is NFPA13 and an upper floor, as long as the minimum fire separation is met, as NFPA 13R.
In the dozens of AHJ's that I have worked with I have yet to meet any who would accept 13R to cover any commercial use. Nonetheless there is always that " one guy" so I strongly recommend that you talk with the project AHJ for their input before you expend any more energy.

Reply
Nick Zmay
1/18/2024 11:18:18 am

After researching more:

[F] 903.3.1.2 NFPA 13R Sprinkler Systems (Also in NFPA13)
Automatic sprinkler systems in Group R occupancies shall be permitted to be installed throughout in accordance with NFPA 13R as amended in Chapter 35 where the Group R occupancy meets all of the following conditions:
NFPA 13R
6.2.2 Outside Dwelling Units
6.2.2.2 The following types of spaces shall be permitted to be protected by residential sprinklers in accordance with Section 7.1: Ordinary-hazard areas in accordance with 7.2.4.1

7.2.4.1 Residential sprinklers shall be permitted to be used in ordinary-hazard areas that meet the following conditions:
The area is compartmented into 500 ft2 or less by 30-minute fire-rated construction.
The sprinklers are spaced at 130 ft2 per sprinkler.
Openings have a lintel at least 8 in. in depth.
The total area of openings, excluding any overhead garage doors that open to the exterior, does not exceed 50 ft2 for each compartment.
Discharge densities are in accordance with NFPA 13 for ordinary-hazard.

Reply
James Art, FPE
1/24/2024 01:05:45 pm

Hey, Anthony!

This is a little tricky,
I believe the issues are NOT just whether the AHJ will accept it,
or the code allows a weaker system, designed mostly to enhance people exiting ("Life Safety System)
but also whether the system is capable of controlling or extinguishing a fire?
Certainly something is better than nothing,
but many Live/Work Occupancies,
esp. Artist Studios
can resemble paint shops but without booths or proper electrics,
or Woodworkers without dust collection.
Tenants can change, and Housekeeping can vary.

Reply
Dan Wilder
1/18/2024 03:39:00 pm

Strictly from the IBC path...

Section 419 for Live/Work Units
419.1 General.
A live/work unit shall comply with Sections 419.1 through 419.9.

419.2 Occupancies.
Live/work units shall be classified as a Group R-2 occupancy. Separation requirements found in Sections 420 and 508 shall not apply within the live/work unit where the live/work unit is in compliance with Section 419. Nonresidential uses that would otherwise be classified as either a Group H or S occupancy shall not be permitted in a live/work unit.

[F] 419.5 Fire protection.
The live/work unit shall be provided with a monitored fire alarm system where required by Section 907.2.9 and an automatic sprinkler system in accordance with Section 903.2.8.

[F] 903.2.8 Group R.
An automatic sprinkler system installed in accordance with Section 903.3 shall be provided throughout all buildings with a Group R fire area.

[F] 903.3 Installation requirements.
Automatic sprinkler systems shall be designed and installed in accordance with Sections 903.3.1 through 903.3.8.

[F] 903.3.1.2 NFPA 13R sprinkler systems.
Automatic sprinkler systems in Group R occupancies up to and including four stories in height in buildings not exceeding 60 feet (18 288 mm) in height above grade plane shall be permitted to be installed throughout in accordance with NFPA 13R.


By that path of code sections, the entire space can be designed with 13R. Inside dwelling units per 7.1 and the other spaces will comply with 7.2 for Outside the dwelling unit with either QR or Res sprinkler types and the discharge densities per 13 (so a 4 head calc at a .15 or .2 density) as Nick posted.


Reply
Todd E Wyatt
1/22/2024 05:26:10 pm

Live/work units are classified as a Group R-2 Occupancy Classification (OC) per the scoping Code (2022 California Administrative Code) which requires NFPA 13 or permits NFPA 13R if it meets the (4) conditions of 903.3.1.2.

REFERENCES
2022 California Administrative Code

Chapter 9 Fire Protection and Life Safety Systems
Section 903 Automatic Sprinkler Systems
903.2 Where Required
Approved automatic sprinkler systems in new buildings and structures shall be provided in the locations described in Sections 903.2.1 through 903.2.12 and Sections 903.2.14 through 903.2.21.
903.2.8 Group R
An automatic sprinkler system installed in accordance with Section 903.3 shall be provided throughout all buildings with a Group R fire area.

903.3 Installation Requirements
Automatic sprinkler systems shall be designed and installed in accordance with Sections 903.3.1 through 903.3.9.
903.3.1 Standards
Sprinkler systems shall be designed and installed in accordance with Section 903.3.1.1 unless otherwise permitted by Sections 903.3.1.2 and 903.3.1.3 and other chapters of this code, as applicable.
903.3.1.1 NFPA 13 Sprinkler Systems
Where the provisions of this code require that a building or portion thereof be equipped throughout with an automatic sprinkler system in accordance with this section, sprinklers shall be installed throughout in accordance with NFPA 13 as amended in Chapter 35 except as provided in Sections 903.3.1.1.1 through 903.3.1.1.3.
903.3.1.2 NFPA 13R Sprinkler Systems
Automatic sprinkler systems in Group R occupancies shall be permitted to be installed throughout in accordance with NFPA 13R as amended in Chapter 35 where the Group R occupancy meets all of the following conditions:
1. Four stories or fewer above grade plane.
2. The floor level of the highest story is 30 feet (9144 mm) or less above the lowest level of fire department vehicle access.
3. The floor level of the lowest story is 30 feet (9144 mm) or less below the lowest level of fire department vehicle access.
4. The number of stories of Group R occupancies constructed in accordance with Sections 510.2 and 510.4 shall be measured from grade plane.

Chapter 3 Occupancy Classification and Use
Section 310 Residential Group R
310.3 Residential Group R-2
Residential Group R-2 occupancies containing sleeping units or more than two dwelling units where the occupants are primarily permanent in nature, including: Live/work units

Section 508 Mixed Use and Occupancy
508.5.7 Fire Protection
The live/work unit shall be provided with a monitored fire alarm system where required by Section 907.2.9 and an automatic sprinkler system in accordance with Section 903.2.8.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT