MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Is Multi-Level Ceiling Sprinkler Spacing Correct?

5/18/2023

11 Comments

 
We have an NFPA 13 system, using residential sprinklers, in a dwelling unit that has 2-levels of smooth flat ceilings. There are two levels of ceilings (9'-0" on left, 8'-0" height on right).

​Image provided below:
Picture
Sprinklers are hydraulically calculated at their listing with a 20 x 20 spacing, and there is not an issue providing 0.10 gpm/sqft.

See the spacing above - is this an allowable arrangement though considering how it was calculated?

​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Pete H
5/18/2023 06:51:29 am

It looks ugly, but it's fine.

The head within 10'-0" of the ceiling divide is on the lower ceiling, so it will spray further and cover the floor area of the higher ceiling where the head is over 10'-0" from the ceiling divide.

Ideally, I'd move the head that is 13'-0" away from the ceiling divide to 7'-6" away because then I know it'll spray underneath the 12" difference in ceiling (Table 8.10.6.1.2 in NFPA 13 2016) and it looks like it'll still be well within 10'-0" of the wall, but that's just making it look nicer rather than sheer compliance.

In terms of sheer code/listing compliance, this arrangement works. Most I could see causing an issue is if the ceiling the pendants/uprights are protecting underneath a combustible ceiling with no further overhead protection. Then because of the combustibility of the construction, I could see an AHJ wishing to go beyond the listing and want the head to be within 10'-0" of the divide so it's at least wetting the combustible construction members.

Reply
Pete H
5/18/2023 09:00:41 am

I'm wrong, Anthony's right. Unless listed otherwise, residential heads are to be within 1" to 4" deflector to ceiling.

So ultimately, move the head 13'-0" away from the ceiling divide to be within 10'-0" of the ceiling divide.

If you want to be awesome, keep it over 7 ft off the ceiling divide but under 10'-0" so there's zero doubt the sprinkler sprays underneath.

Reply
Anthony
5/18/2023 07:01:16 am

This is not an appropriate lay out of sprinklers unless the sprinklers are allowed to be 12'' down from ceiling. In many cases pendant res sprinklers are only allowed to be 8'' maximum down from ceiling per their listing. Thus the area 3' left from the edge of the step in ceiling height is in an unprotected area.

There is no such rule similar to 8.6.4.1.1.3(b) (NFPA 13-16) for residential sprinklers.

There is an argument to be made about ceiling pockets and the whole area under the sprinkler being protected. However, I do not believe the arrangement shown indicates a "pocket."

Reply
Dave Sornsin
5/18/2023 11:25:40 am

I agree with Anthony (and Pete's revised comment): Residential sprinklers don't have an equivalent to 8.6.4.1.1.3(b) (NFPA 13-16). I'm guessing this is because of the high wall wetting requirement for residential sprinklers.

What's interesting, is that in later editions (see NFPA 13-19 12.1.8.1.2), with limitations including a 600 sq.ft. compartment, the committee allows installation of residential sprinklers in or next to beams up to 14" deep which could delay the operation AND not achieve the high wall wetting. So if operating in the 2019 or later edition could you consider the entire ceiling to the right of the dashed line a really wide beam? LOL.

Reply
SCHULMAN
5/18/2023 08:13:46 am

i would add another sprinkler 2' left of the center line. your chandelier or ceiling fan at the high ceiling won't be a problem and you solve the question of coverage... and it will look nicer.... I'm assuming you will be installing concealed flush and not dropped sprinklers... please. ...

Reply
R Jackson link
5/18/2023 08:36:34 am

Just because you can design something per code doesn't mean it will have the best appearance. I would center both heads, as long as this would meet code. If not, then 2 heads.

Reply
Franck
5/18/2023 11:01:14 am

As indicated above, the possible issue is that a fire originating under the 9 ft ceiling, but at the edge with the 8 ft ceiling will first only operate the sprinkler under the 9 ft ceiling, with 3 ft not correctly covered… until the sprinkler under the 8 ft operates.
Being allowed to go up to 20 ft spacing does not mean you have to have these 20 ft.
For a better coverage and efficiency, I would space both sprinklers by 15 ft, starting 7 ft 6 in from each wall (centered in each “pocket”).
Much nicer to see and more efficient (reliability).
And this won’t really impact your hydr. Calculation to reach 0.1 gpm/ sq ft in this area.

Reply
Franck
5/18/2023 11:06:07 am

Note that this would have been a lesser reliability issue if the sorinkler located 13 ft from the edge would have been the one under the 8 ft ceiling.
A fire originating close to the edge between both ceiling, but under the 8 ft ceiling area, between 10 ft and 13 ft from the sprinkler, would activate more quickly the sprinklers on both sides as the heat tends to collect to the highest point : heat plume under the 8 ft ceiling would reach the sprinkler located under the 8 ft ceiling, but on the other side, the heat plume will quickly reach the 9 ft ceiling level and activate the second sprinkler…

Reply
Naj link
5/18/2023 11:46:58 am

Vertical change in ceiling elevation less than 36 in. sprinkler positions are fine.
In this case sprinklers can be designed as ceiling was flat.

Reply
danefre
5/19/2023 07:21:30 am

That section is for standard spray sprinklers only and doesn't apply here. See comments above.

Reply
Naj
5/23/2023 08:04:23 am

Yes, that's for standard sprinklers but reference to NFPA 13-2019 section 12.1.10.1.2 (1) sprinklers shall be in accordance with 9.5.5.2, table 12.1.10.1.2 and figure 12.1.10.1.2 (a)

9.5.5.2 Sprinklers shall be positioned in accordance with the minimum distances and special requirements of Section 10.2 through section 14.2 so that they are located sufficiently away from obstructions such as truss webs and chords, pipes, columns, and fixtures.
As per section 10.2 ; Figure 10.2.6.1.1.3 (A) vertical change in ceiling elevation greater than 36 in then maximum distance to change in obstruction is ½ S.

so it should apply




Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT