MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Is Missing Coverplate a Deficiency in NFPA 25?

1/12/2023

7 Comments

 
Is missing a coverplate for a concealed sprinkler a deficiency in NFPA 25 that would be required to be corrected?

​​​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Dan Wilder
1/12/2023 07:34:10 am

In the 2023 Edition - Yes

5.2.1.1.5
Escutcheons and cover plates for recessed, flush, and concealed sprinklers shall be replaced with their listed escutcheon or cover plate if found missing during the inspection.

The outer ring on a 2-piece escutcheon (skirts as I have heard them called) or any concealed cover plate.

This excludes the beauty rings or oversized rings found in seismic areas or to cover holes that are made too large in the ceiling or for clearance. I've heard both ways for the 401 style skirt but I personally would put that as a beauty ring.

Reply
Todd E Wyatt
1/12/2023 08:20:15 am

Additional "escutcheon" references from 2023 NFPA 2025 :

5.2* Inspection.
5.2.1 Sprinklers.

5.2.1.1.5.1
Where the listed escutcheon or coverplate from a listed assembly is missing and is no longer commercially available, the sprinkler shall be replaced.

ENHANCED CONTENT
Sprinklers with missing escutcheons and coverplates must be replaced with their listed escutcheon or coverplate, or the entire sprinkler must be replaced. Many times a generic escutcheon or coverplate is installed. This is improper and is addressed by 5.2.1.1.5. Sprinklers do not need to be replaced unless the missing and unavailable coverplate is part of a listed assembly. The focus should be on the “listed assembly” as opposed to the listed coverplate.

5.2.1.1.6

Escutcheons for pendent sprinklers that are not recessed, flush, or concealed shall not be required to be replaced if found missing during the inspection.

ENHANCED CONTENT
Paragraphs 5.2.1.1.5 through 5.2.1.1.6 generate many questions during the inspection process. Many recessed, flush, and concealed sprinklers are listed as part of an assembly with their escutcheons or coverplates. When these pieces are missing, the sprinkler may not perform as designed and must be replaced. For more information, refer to the definition of deficiency in 3.3.8. Missing standard escutcheons (sometimes called beauty rings) do not affect the performance of the sprinkler system and, therefore, do not meet the definition of a deficiency. Exhibit 5.19 shows a sprinkler with an incomplete escutcheon assembly.

Here is the definition of "deficiency" :

3.3.8 * Deficiency.
For the purposes of inspection, testing, and maintenance of water-based fire protection systems, a condition that will or has the potential to adversely impact the performance of a system or portion thereof but does not rise to the level of an impairment.


Reply
Anthony
1/12/2023 08:28:16 am

That was added in the 2013 ed of NFPA 25 so I'd think that applies to most states.

There "should" be several cover plates (2 minimum) in the spare head cabinet that can be used.

G5 cover plates (a common model of concealed sprinkler from Reliable) depending on finish costs apx 43$~75$ list.


see source:
https://reliablesprinkler.com/pricebooks/Americas_USD/Americas_USD.pdf?x11550

Reply
Bill Greene
1/22/2023 06:27:27 pm

In my opinion, replacement of such devices is not required.

Reply
Dwight H Havens
1/12/2023 08:48:10 am

Missing escutcheons on recessed sprinklers may be an indication that the ceiling has sagged, causing the outer escutcheon to disengage from the inner escutcheon. If this happens, the distance of the deflector below the ceiling may no longer comply with installation requirements and could impact the water distribution pattern.

Similar concerns with concealed cover plates. When the cover plate no longer engages the sprinkler assembly the distance between the deflector and the ceiling may not be adequate for the water spray pattern to fully clear the ceiling.

Too often I have seen this problem resolved, but not corrected, using caulk to glue the escutcheon or conceal plate to the ceiling, vice adjusting the level of the piping or level of the ceiling grid.

Reply
Ryan Hinson
1/12/2023 09:19:48 am

If the metal outer escutcheon which is part of the listed assembly is gone, there may be a building code violation if the penetrating building feature is a fire-resistance-rated assembly through a membrane per IBC 2021 Section 714.4.2 Exception 5. Further digging may be necessary to determine whether the membrane being penetrated is rated which is beyond the minimum scope of NFPA 25...but can be included if the inspection contract stipulates. If recognized during an inspection, I would document and indicate as such.

Reply
Jesse
1/12/2023 09:46:09 am

It is now, yes in the most recent edition of 25.There were other editions of 25 previously that didn't expressly state it though.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT