MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Is Low-Piled and Miscellaneous Stoage the Same?

1/21/2022

12 Comments

 
I would like to differentiate between the density requirements for low piled and miscellaneous storage using NFPA 13-2019 Edition.

I have reviewed the the definition and literature in the code. That is all completely understandable.

Does miscellaneous storage meet or excteed the requirements for low-piled storage?

Based on the commodity, total storage area, total storage percentage, pile size dimensions, and storage spacing requirements - does all this factored in mean that the design density for the non-storage areas (like manufacturing or assembly) can be used under the miscellaneous storage area, instead of the densities provided in NFPA 13 Table 4.3.1.7.1?

For Table 4.3.1.7.1 - there is no mention of low piled storage in the title of the table - is this the table that would be used for the determining the densities for any low-piled storage areas? Is there not a separate table for low-piled storage?

I am likely overthinking things but some clarification or opinions would be appreciated.

Thanks in advance for the help.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments
Pete H
1/21/2022 06:59:10 am

Not 100% the same. But they work out the same in most practice. From NFPA 13 (2013)

20.1.1: Miscellaneous and low-piled storage, meeting the criteria of Chapter 4, shall be protected in accordance with the relative occupancy hazard criteria reference in that section.

-

4.3.1.4 Misc. Storage
4.3.1.4.1 - Misc. storage shall not constitute more than 10 percent of the building area or 4000 sq. ft of the sprinklered area, whichever is greater.
4.3.1.4.2 - Misc. storage shall not exceed 1000 sq ft in one pile or area
4.3.1.4.5 - Misc. storage shall be separated from other storage piles or areas by at least 25 ft.

-

4.3.1.5 Low Piled Storage
4.3.1.5.1 - For storage of Class I through Class IV commodities of 12 ft or less in height that do not meet the definition of Misc. storage that is on solid shelf racks, in rack sprinklers shall be provided in accordance with 25.6.1, and ceiling sprinkler protection shall be provided in accordance with this chapter for the applicable occupancy hazard criteria.

4.3.1.5.2 For storage of Group A plastic commodities 5 ft or less in height that do not meet the definition of Miscellaneous Storage that is on solid shelf racks, in rack sprinklers shall be provided in accordance with 25.6.1, and ceiling sprinkler protection shall be provided in accordance with this chapter for the applicable occupancy hazard criteria.

-

4.3.1.7 - Protection Criteria for Misc and Low-Piled Storage
4.3.1.7.1 - The protection criteria for misc and low-piled storage protected by ceiling sprinklers ONLY shall be selected from table 4.3.1.7.1 and Figure 19.3..3.1.1 ion accordance with the density/area method of 19.3.3.2.
4.3.1.7.1.1. - The protection criteria for rack storage of miscellaneous and low-piled storage with in-rack sprinklers shall be in accordance with 25.2.2
4.3.1.7.2 - Except as provided in 4.3.1.6.1 the maximum design area for misc and low-piled storage shall not exceed 3000 sq. ft.

4.3.1.8 - In Rack Sprinklers - Misc. and Low Piled storage per 4.3.1.5 through 4.3.1.7 that require in-rack sprinklers shall follow chapter 25 for their installation and design requirements.

-

4.3.4 - Ordinary Hazard (Group 2) - The following shall be protected with OH2 Occupancy criteria in this standard:
1) Spaces with moderate to high quantity and combustibility of contents
2) Stockpiles of contents with moderate to high combustibility that do not exceed 12 ft.

-

Yes, table 4.3.1.7.1 directs the discharge for misc. storage up to 12 feet in height: BUT you are directed (as per section 4.3.1.7) to use the same table for Low-Piled storage (which unlike misc. storage is not limited to a square footage of 4000/10% of the building, whichever is greater. And doesn't need to be in 1000 sq. ft. max stockpiles).


Reply
Pete H
1/21/2022 06:59:49 am

Er. 2019 edition. Not 2013.My bad on that.

Reply
Pete H
1/21/2022 07:06:22 am

The other fun thing to notice is that when you do meet those ever elusive requirements to be misc. storage and not low-piled storage, you aren't directed to use in-rack sprinklers on solid shelves as per 25.6.1 (but still might want to if you meet the +1 level of in-rack sprinkler note found in Table 4.3.1.7.1, in which case refer to 25.2.2.1 for design criteria.)

Reply
ML
12/8/2023 06:47:15 pm

Pete if our storage is classified as Misc Storage do we not have to have in rack sprinklers on solid shelves?

Reply
Jesse
1/21/2022 08:25:11 am

Not 100% quite the same thing, but for the purposes of this, yes.

Misc. Storage is thought to be incidental to the greater occupancy for the most part - which is why there is the 4000 sq. ft / 10%. Think of it as a small manufacturing plant which would be OH2 that has a small raw materials / finished product storage area. Low piled doesn't have that incidental nature in it, and becomes "Storage" protected under 13s storage chapters once it hits the height threshold for each commodity.

Reply
Franck
1/21/2022 08:40:15 am

The main purpose is to be sure that if you are below the requirement of height for pile storage in the storage section chapter, you don't define a density that would be lower than for misc. storage.

Misc. storage was initially defined to cope with the little amount of storage within production areas. To be sure that if you have a design for OH gr 2 you can cope with some storage along the production lines.

Low pile storage is when you are below a certain height (12 ft) or when you apply the correction factor for storage height, to be sure that in no case you end up with a density lower than what would be required for misc. storage with the same height.

Reply
Franck
1/21/2022 08:42:01 am

The main difference with low pile storage and "normal" storage would be the selection of sprinklers (temperature rating) and installation of sprinklers (spacing, coverage area / sprinkler...), as you can follow the rules for OH Gr 2 and not the one for storage.

Reply
Jay
1/21/2022 09:31:10 am

The table you're referring to is only applicable to storage that meets the definition of miscellaneous storage.
The most common situation you'll come across that requires different densities between miscellaneous and low-piled storage is the storage of group A plastics. If it is low-piled storage of group A plastics greater than 5ft in height, you cannot use Table 4.3.1.7.1.
2016 and earlier editions spelled this out clearly in the beginning of chapters 15 and 17, but now not so much.
See Table 21.3.1, Table 21.3.3, 21.5.2, Table 21.5.1.1, and Table 21.5.3.
For example, if you have 10ft rack storage of exposed/nonexpanded group A plastic with a ceiling of 20 ft and is defined as miscellaneous storage the design is EH2 or .4/2500.
The same storage arrangement defined as low-piled has a design of .8/2500 (Table 21.5.3).

Reply
Todd B
1/21/2022 12:49:44 pm

Thank you everyone for your comments and help

Reply
Pete D
1/22/2022 10:20:40 pm

Be warned. In the definition chapter, 3, there is a definition of miscellaneous storage and another definition of miscellaneous tire storage, and they're different.

Reply
Todd Wyatt
1/24/2022 08:47:23 am

The 2021 IBC (the scoping Code for automatic sprinkler systems) references the 2021 IFC regarding "high-piled stock or rack storage" per 413.1 General.(https://codes.iccsafe.org/content/IBC2021P1/chapter-4-special-detailed-requirements-based-on-occupancy-and-use#IBC2021P1_Ch04_Sec413.1)

2021 IFC Ch 32 High-Piled Combustible Storage outlines the requirements for automatic sprinkler systems for both high-piled and rack systems and references the NFPA 13 in (11) instances in this chapter.

Reply
OSMAN OMRAN OSMAN
7/23/2023 03:52:04 pm

I am thinking that there are a contradiction between:

4.3.1.4.1 Miscellaneous storage shall not constitute more than 10 percent of the building area
or 4000 ft2 (370 m2) of the sprinklered area, whichever is greater.

4.3.1.7.2 Except as provided in 4.3.1.6.1, the maximum design area for miscellaneous and
low-piled storage shall not exceed 3000 ft2 (279 m2).

Could you please explain it to me.

Thank you

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT