Is Horizontal Screen an Obstruction to Sprinklers?

5/2/2022

8 Comments

 
I have a laboratory space which original had an open ceiling. The renovated space plans to provide a screen, similar to a window insect screen across the open ceiling, which will contain lizards which they are working with. 

Is this screen considered an obstruction to the sprinklers above?

The screen would be located approximately 3-feet below the main ceiling at 8'-0" above the floor. Although water would pass through, it seems that it would significantly disrupt the distribution pattern from the sprinklers.

This also does not seem to meet the requirements for an open-grid ceiling. Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Alex
5/2/2022 07:48:23 am

Hi,

This is a good question. I'm sure we will see differing views on this issue in regards to open ceilings versus other horizontal obstructions. Hopefully today, someone can cite a code section that puts the issue to rest!

On one hand, you have NFPA 13 (2022) 9.5.5.3 that states that horizontal obstructions that interrupt water discharge shall comply with 9.5.5.3 and the following subsections.

9.5.5.3.1 states that any obstruction over 4 feet require sprinklers installed beneath.

The annex material states that for slat decks, walkways, or open grating, the use of opening or enlarging the openings are not a substitute for automatic sprinklers. If you go this approach, I would say you require sprinklers beneath your screen no matter your percent open.

On the other hand, the code doesn't call out this specific scenario. Nor will it ever (there are far too many scenarios out there)! Think of providing a screen above a storage compartment within an apartment complex. The screen is installed to prevent storage being stacked too high, thus obstructing sprinkler discharge. But then do you need to install sprinklers beneath the screen? I would say no!

So if you are looking at it this way, I would say treat it like an open ceiling. NFPA 13 (2013) 8.15.14 states to have the screen 70 percent open. Personally, this is how I would prevent sprinklers beneath.

In the end you state that you do not fall under the requirements to be 70% open. Therefore, I would say you do need to install sprinklers beneath the screen.

Thanks,
Alex

Reply
Jesse
5/2/2022 08:13:48 am

This is a tough one. The screen will disrupt development of the spray pattern. However, sprinklers underneath the screen probably won't collect enough heat to activate.

I think it does indeed pose an obstruction. I would recommend protecting using either horizontal sidewalls with a heat collector (depending on room size), or regular pendents with heat shields.

Reply
DL
5/2/2022 09:54:43 am

No disrespect intended, but "heat collectors" are proven not to work, and are now specifically prohibited in NFPA #13: "Heat collectors shall not be used as a means to assist the activation of a sprinkler. (See also Annex commentary.) Furthermore, sidewall sprinklers shall only be installed beneath smooth, flat ceilings.

Reply
NK
5/2/2022 08:23:36 am

I would send an RFI inquiring about how open the screen is. If it's 70% open or more (you can figure this out by doing some simple math that I would recommend showing on your drawing), then I would follow NFPA 13, 2016 8.15.14 for Open-Grid Ceilings. If the screen is not 70% open I would put the decision in the A/E teams hands regarding changing the screen to a screen that is 70% open or adding an intermediate sprinkler with a water shield below the screen to provide above and below protection. I don't think you're going to find this specific situation in NFPA 13, but an Open-Grid ceiling is probably the most similar concept to what you are describing.

Reply
Dan Wilder
5/2/2022 08:24:20 am

What's the material? Anything not metal will likely burn away near the fire location anyway. If it is metal, there may be a stronger point for a water shield and sprinklers beneath.

Are they putting any additional "plants" above (Live or dead)? At best (or worst depending on how you look at it), this looks more like a Rain Forest Café to a point but if this is occurring, those locations of "plants" may be your best bet for a lower sprinkler location with a water shield.

Open-grid ceilings have a specific minimum opening, typically 1/4", and have the ability to prevent the sprinkler pattern from developing horizontally. Being 36" below, you could make an argument for a smaller spacing layout to alleviate the spray pattern disruption. An example would be an F1FR56 sprays about 4.5' horizontally at the 3' mark (at 7 PSI) so an 8x8 sprinkler spacing removes the gaps potentially created by the screen. An approach you could talk with the AHJ about as an AMM.

Reply
Hunt
5/2/2022 09:17:29 am

Good call.. The screen material and percentage of openness needs to be identified first. Possible deluge?

Reply
Glenn Berger
5/2/2022 08:40:24 am

Potential Obstruction - yes, depending on the material and the openness of the screen material.

Reply
franck
5/2/2022 04:21:19 pm

As indicated by Dan, if the material is combustible (plastic for example), this is not a problem as it will burn quickly so that the sprinkler above can operate without problem

I made of metal (or even wood, as it will remains for a ling time), this could create an obstruction and should be considered as such.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT