Can the pipe from a remote FDC at the front of our building route under the building slab to connect to our fire pump room at the back of the building? The Fire Pump Room is on the basement level. This is for a six-story hotel with a partial basement along the back portion of the building that is open to a lower grade level in back. Here's a sketch below. The fire marshal requires a remote FDC at the sidewalk in front of the building. Our fire pump room happens to be on the opposite side, in the back.
The most straightforward routing is below the building, but it is minimum 60' of run which certainly exceeds the 10' maximum distance allowed for the fire supply from NFPA 13. Going above the first floor ceiling is challenging given all the interiors/ceilings, public spaces, and glass at the street front. Given that the FDC pipe is normally-dry and not pressurized, do we have the same restrictions of 10' max below grade? Even if not, can't say I'm thrilled about having that many joints below our building above. Thanks for your help/thoughts! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
13 Comments
chad
2/3/2023 08:14:53 am
FDC's are routinely routed outside away from the building. Under slab is outside/exterior to the building, in my opinion.
Reply
Anthony
2/3/2023 08:19:00 am
There are provisions in 13-16 for running pipe underground in chapter 10.
Reply
chad
2/3/2023 08:29:44 am
Agreed.
Reply
Glenn Berger
2/3/2023 08:25:39 am
My recommendation is never install fire protection piping below a building. Depending where the check valve is place this pipe will see both wetted areas and dry areas and will corrode.
Reply
Alex
2/3/2023 08:39:20 am
FDC piping is of course run underground with free standing connections. The main issue I see with yours is running under your building and the possibility of future repairs. You could always run up to the second floor to avoid complicated ceilings and drop within a column.
Reply
Eric R
2/3/2023 08:44:29 am
As a NFPA 25 inspector I (and the owner) will hate you forever if in 5 or 10 years that pipe fails it's required 150psi hydrostatic test, and I have to explain to the owner that we need to tear up their floor to find out where the pipe failed.
Reply
2/3/2023 09:15:00 am
As a fire sprinkler contractor, my job is doing what is best for the building owner, both cost effective and code compliant. I would do whatever it takes to not feed the remote FDC under the building. I would NOT want to explain to the owner a few years down the road when the piping needs to be replaced for whatever reason. You can always do things the quick and easy way, or you can do things the best possible way. No matter which way you choose, it will say volumes about you as a designer, and the company you represent.
Reply
Kevin
2/5/2023 08:23:40 am
In reading the comments, our experience is that all underground to a FDC whether out in the yard or under the building slab is to be Cement Lined Ductile Iron Class 52 or greater. Mechanical joint is preferred. It seems the comments about corrison are for steel pipe underground which is never to installed undergorund.
Reply
John Monsebroten
2/5/2023 11:59:58 am
There is language about connecting the FDC to a cross main. You may be able to avoid going underground which may or may not work for your project.
Reply
JH
2/8/2023 10:56:09 am
It seems FD access may be driving the Fire Marshal's requirements. What are the existing site conditions? Would be curious to see overall site utility plan to fully address this issue, as many factors are considered when placing an FDC.
Reply
Franck
2/9/2023 09:36:07 am
As indicated above, I would never run a pipe under a building.
Reply
James Art FPE
3/2/2023 11:54:36 am
Code prohibits running pipe UNDER a building more than about 10 feet of length if needed to the riser.