MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Is FDC and PIV Required to be 50-ft Apart?

1/17/2024

15 Comments

 
I have a building that has both a free standing fire department connection (FDC) and a post-indicator valve (PIV) out at the drive entrance to the single-story building as requested by the Fire Marshal.

Construction has now started up for the site and the Fire Marshal is saying there is a code requirement for the PIV and FDC to be 50-ft apart and wants them moved. He is unsure of the exact distance, but he insists this is a code requirement and that it's not a local requirement.

For reference, we are under the 2015 IBC/IFC and 2013 NFPA code editions.

Is there any requirement for the PIV and FDC to be 50-ft apart?

I cannot find any requirement like this in the IBC, IFC, or NFPA 13 or 24. There are sections in both NFPA 13 and 24 that vaguely say PIVs shall be protected against mechanical damage, but they give no minimum distance from objects. IFC/IBC both list minimum 36-in clearance around the FDC.

I think the Fire Marshal might be confusing the 40ft requirement from buildings for the PIV, or, this is a local preference, but they do insist otherwise.

I know at the end of the day the Fire Marshal gets whatever they want for the PIV and FDC placement, but I really want to make sure that there is not some hidden requirement I cannot find.

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
15 Comments
Glenn Berger
1/17/2024 08:17:35 am

NFPA 24 has a "basic" requirement of 40 feet for hydrants and PIVs from buildings. Many exceptions and deviations have been allowed.

As far as FDC, it is mostly dependant on the location of hydrants and the approach of the responding fire department. Most FDCs are located on the building wall.

Reply
Greg
1/17/2024 08:46:57 am

As illuded to in the previous comment, NFPA 24 is the Standard for the Installation of Private Fire Service Mains and Their Appurtenances. The key word here is private mains used in industrial complexes, oil & gas, nuclear, etc., as compared to a public utility service.

From my understanding of the fundamental reason for the 40 ft. plus separation is a defense - in depth strategy in the event of building collapse. There is a great deal of assumption in the concept. However, imagine an industrial building collapse where the collapse zone spreads outward from the original building footprint.

If the PIV were outside of the control zone, it allows for shut-off of the collapsed building's sprinkler system (which may now be a broken and open set of pipes). Isolation preserves precious water (volume and pressure), and within an industrial setting, a tanked water system or even an open water pump-draft station can be used more efficiently, if water is not being wasted within the collapse. The position of the FDC could have some of the same theory, although I've only been aware of the PIV distance requirements in private service.

A lessor thought for considering remoteness of PIV and FDC is for highly hazardous chemicals and some scenarios with nuclear materials. The distance from the building allows for operation to occur in an area that might be somewhat safer than a proximate location to the structure. However, in thinking from past experience, I don't recall off hand any specific requirements that would cite this this as a defined philosophy.

Reply
Dan Wilder
1/17/2024 08:58:42 am

I think he is mixing up the Collapse Zone requirements for the building (in general for personnel and apparatus) to the valves themselves, which is typically 1.5x the height of the exterior wall.

There is no specific code section that I am aware of, more good practice and SOP by a responding fire department, to a specific building construction and occupancy.

Reply
Jesse
1/17/2024 12:34:02 pm

Agree with Dan here. I think the local FM is getting a couple different things confused.

I would respectfully ask for a code reference from the FM. Its their responsibility to provide that.

Reply
Colin Lusher
1/17/2024 04:47:57 pm

This is the best answer, your AHJ is confused. There is no separation requirement between FDC and PIV.

Reply
Ivan Humberson
1/17/2024 09:04:48 am

IMHO, as a retired code official, the AHJ should be the one to provide the code section they are citing that requires this - I always stressed to my staff that anytime they required something to be changed, they needed to provide the code section reference for the requirement.

Reply
S
1/17/2024 10:24:28 am

great answer!

Reply
Pete H
1/17/2024 11:55:56 am

Yeah, I can't find a direct code requirement for this 50' separation.

Perhaps you can call/e-mail the AHJ and just try to ask to verify what code section he's alluding to for the purpose of your own education?

Maybe offer the 40'-0" separation of PIV's and hydrants in NFPA 24 as the closest you can find from your own research (with the appropriate code section to show you've looked into it).

Reply
Jerry Clark
1/17/2024 01:01:26 pm

Please...PLEASE! Stop saying the AHJ gets what the AHJ wants. The AHJ cannot just magically require something if it is not included in a legally adopted code or standard, PERIOD! And as stated in another response, it's on the AHJ to provide the exact code citation, not for you to try and figure out what the heck they're talking about.

Reply
Pete D.
1/17/2024 09:18:47 pm

There is a 100 ft. max requirement between the FDC and the public hydrant intended for the pumper to draw suction water from. I have seen code adoption in select jurisdictions reduce this to 50 feet. Saginaw comes to mind. Additionally, your AHJ may be confusing a PIV with a WPIV, and if the valve in reference is a WPIV, I think the FDC should fall outside of the collapse zone measured from the exterior wall, which is where WPIVs are located.

Reply
Dean Melanson
1/18/2024 02:55:48 pm

I believe that the 100 foot max distance of the FDC to hydrant is only for standpipe FDC's. I do not believe that there is any requirements for the hydrant to FDC for sprinkler systems. I cannot find anywhere that the FDC and PIV must be any distance apart. As mentioned previously it is up to the code official to give a written violation order citing the enforceable code(s) and who an appeal can be made to

Reply
Fred Walker
1/18/2024 01:25:41 pm

Normally NFPA 24 applies to “private” water distribution not municpal distribution. Most utilities use AWWA manuals. I did not see any specific separation require in the AWWA manuals I reviewed.
In response to “the AHJ gets what the AHJ wants” , it is correct the AHJ can not write code if there is a legally adopted code, but, he can make the approval process very difficult. Choose your battles.
I agree it is the AHJ responsibility to identify the relevant code citations he is using to establish the requirement.

Reply
Antonio Fernandes link
1/19/2024 08:15:16 am

Wouldn't this issues be address in the local building code or NFPA 1 or 5000? And not in NFPA 13, 24.

Reply
Franck
1/20/2024 03:13:47 am

No distance restriction for FDC. They are commonly located on the external wall (just on the other side of the sprinkler riser system), thus limiting friction losses.

PIV recommendation for 40 ft (not 50) is coming from the « old time » where industrial buildings were 30 ft high as a « general rule ».
As indicated by Dan, this is related to the expected collapse of the building and still being able to safely operate the valve.
This being said, it means that if the building is only 20 ft high, you can have some arguments to have the PIV at 30 ft 😀.
On the other side, with a 50 ft high building… well keep the 40 ft.
The good news is that modern buildings are designed to collapse internally. 40 ft is then very conservative. A concrete building is not expected to collapse (except partially with earthquake event). So the construction can also be an argument for less than 40 ft.
Additionally, 40 ft is sometimes not possible: if your site boundary is at 20 ft, for example, or if you have a road at the 40 ft distance.
In that case, I would say : put it as far as feasible. If it is 15 ft, it is better than 2 ft!
Another argument for PIV on sprinkler systems ? Wall PIV are allowed, and they are located against the wall. So a PIV located at any distance from the wall is already better than a wall PIV.

As indicated by many others: the AHJ has to mention the rules indicating where the requirement is coming from. And your duty is to give technical arguments if this is not feasible and what are the other options.

Reply
James Art, FPE
1/24/2024 01:53:21 pm

Often here in Ca, water companies insist on a Backflow,
usually near the tie in,
despite the state laws that prohibits most
(except where a cross connection or a body of water for suction)

See the following California Law excerpt 13114.7 at:
http://leginfo legislature.ca.gov/faces/ codes_ display Section.xht mi?lawCode=HSC&SectionNum=13114.7

or
https://leginfo.legislature.ca.gov/faces/codes_displaySection.xhtml?lawCode=HSC§ionNum=13114.7.&article=1.&highlight=true&keyword=backflow

But no one wants to be the one to "fight the water co", they are bigger than we each are.
(Sprinkler Organizations take note - you could help a lot of situations, make sprinklers more affordable!)

So there should be Indicating Valves there, usually two OS&Y's,
hopefully tamper supervised.

In many cases, these are near enough to small systems to act as control valves.

Q. Is there any requirement to also have a PIV?

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT