I could use some help with sprinkler obstructions.
Generally, I’m looking at piping and ductwork, that is installed within 18” below the plane of the standard upright sprinkler deflector. Light or ordinary occupancies. I called NFPA 13 and got an interpretation that these would be considered a sprinkler obstruction, and I would need sprinklers on either side, regardless of the size of the duct/pipe (no rule here about only being over 4’). This was per Section 10.2.7.2 in the 2019 edition. I didn’t think to ask, but could I still apply the three times rule of 10.2.7.2.1.3, even though these aren’t structural members? As long as I was three times, or 24-inches away, it wouldn’t be an obstruction, right? I’ve seen these close configurations all over the place in many different peoples’ designs, so I’m wondering if I’m missing some allowance. Most recently, I observed a 14” wide (horizontally) x 6” deep duct (vertically), with a sprinkler installed directly above with the deflector 5” above the top of the duct. The next sprinkler head is approximately 12 feet away. Also observed in the same room, was a 5” diameter pipe about 8” diagonally down from a deflector, measured at a 45-degree angle. If I’m understanding NFPA 13 correctly, these would both be considered obstructed. I have a question into NFPA 13, but would appreciate others’ opinions as well. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
4 Comments
Wayne Ammons
1/10/2020 07:52:22 am
The annex material for section 10.2.7.2.1.4 clarifies that nonstructural members are exempt from the "three times rule" and that other obstruction rules such as the "beam rule" and "wide obstruction rule" still apply.
Reply
Franck
1/10/2020 10:16:51 am
You have a good indication for the answer to your question in 10.2.7.2.1.8.
Reply
Franck
1/10/2020 10:19:22 am
In your 2 examples, they have to be considered as obstructions (more than 3 in. and sprinkler position less than 3 x the obstruction size).
Reply
Ron Pierce
1/23/2020 10:26:05 am
As our campus safety manager, I seem to know a little about a lot of things, but not a lot about the little things; so, not an expert by any stretch regarding sprinkler systems, NFPA, etc. I digress.
Reply