Irregular-Room Spacing Apply to Only One Wall?

3/25/2024

9 Comments

 
Hello, First post for me here, thanks in advance for the assistance.

In regards to the irregular room and spacing off the walls, I understand the .75 allowance up to 11'3" for the irregular or less than 90 degree wall (NFPA 13, 2019, 10.2.5.2.2).

​However, I have a set of plans I'm reviewing showing four rooms with only one sprinkler and they are applying this section as one wall in each room is irregular - however - the other walls are all regular 90 degree walls but they are exceeding 7'6" off those walls as well.

In my interpretation, they should only be able to apply the above section for the irregular walls only, not normal 90 degree walls.

In this situation I would request an additional head in each room.

Am I missing something here?
Picture
Thank you.

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Glenn Berger
3/25/2024 08:22:07 am

IMO, you are correct. The irregular room rule should only be utilized as required and not as a carte blanche rule.

Reply
J GOLDEN
3/25/2024 08:32:32 am

The other "small room" rule allows up to 9' but only off of 1 (one) 90-degree wall.

"The small room rule can be stated as: In a room of 800 sq. ft. or less, having unobstructed ceiling construction, and light hazard contents, sprinklers may be located up to 9′ from any single wall with the maximum area of coverage being determined by dividing the size of the room by the number of sprinklers.

To apply the small room rule, the space must meet all the requirements of a small room as defined in NFPA 13. A “small room” (NFPA 13:3.3.22) is a space that is classified as a light hazard, has unobstructed ceiling construction, and is no greater than 800 sq.ft. Application of the small room rule will affect two critical system design elements, maximum area of protection and sprinkler spacing."

Reply
Jack G
3/25/2024 08:44:40 am

Agree with above.
Small room if applicable.
If not and as originally described must addasprinkler.
Opinion— err on side of caution, for safety’s sake.

Reply
Dan Wilder
3/25/2024 08:52:15 am

This would be a great time to post a photo of the room if you can get Mr. Meyer to upload! I tried the ASCII way and it did not end well LOL.

Initial thoughts are they are applying small room rule to one wall and using the irregular shape room allowance for the other side which would be allowed IF all the rules were followed for both instances...so being 9' (measured perpendicular) to more than one wall would not be allowed, the SxL is followed to not exceed maximum square footage (225ft² for the sprinkler and 800ft² for the room), being no greater than the 11'-3" AND not exceeding the 7'-6" from the 2 irregular walls. It would boil down to the actual layout and dimensions, but it could be done in some cases.


NFSA EOD - October 2014 #12 13-2013 Edition
https://nfsa.org/2020/12/01/the-nfpa-13-small-room-rule-frequently-asked-questions/

Reply
Jesse
3/25/2024 09:55:28 am

Would love to see a photo or a sketch of the irregular shape. The small room rule may apply which will allow 9-0 spacing of a standard coverage sprinkler off of one wall

Reply
Dave
3/25/2024 11:01:12 am

Note that the 11'-3" spacing is not off the wall of the irregular area, but to any point of the floor area (see the diagram in the annex). I assume these are not extended-coverage sprinklers. My initial reaction is that there is nothing wrong with a properly applied small-room rule used in conjunction with this allowance for an irregular corner of the room if the perpendicular spacing off the other walls is not exceeded.

Reply
Chris Heyer
3/26/2024 08:42:33 am

Thank you all...I'm going to try to post a quick sketch shortly

Reply
MODERATOR
3/26/2024 10:13:14 am

A sketch of this situation has just been updated on the original post. See it here - https://www.meyerfire.com/daily/irregular-room-spacing-apply-to-only-one-wall

Thanks everyone!

Reply
S
3/26/2024 02:29:32 pm

I do not agree it would be a good idea to use two code references that reduce coverage in one room to save one sprinkler head. If that room became a storage room due to it's odd shape, which it more than likely will be, then it is way under protected. IMO

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT