I'll preface this that I'm not a engineer. There is 17-foot storage with an existing sprinkler design of 0.20 / 1,500 sqft.
Based on NFPA 13, I believe we would need 0.21 / 2,000 sqft for a Class II commodity (non-encapsulated rack storage). How would you recommend going about increasing both the remote area size and the density on an existing system? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Glenn Berger
6/11/2021 08:36:29 am
Start off by having new hydraulic calculations prepared on the existing system. The result and this analysis and understanding the age of the system would determine my next move. There are too many variable to discuss at this time.
Reply
Dan Wilder
6/11/2021 08:49:14 am
Too many storage questions, but assuming your density & area scenario is accurate, just putting a new remote area on the drawing at the new size and density is all you need (along with a current flow test) as long as you have the system surveyed/verified for layout.
Reply
Mike
6/11/2021 09:07:54 am
Survey the system. Do a complete hydraulic design. Hopefully, the underground is 6". Start with increasing 1" pipe at the end of lines, then do an analysis of high friction loss pipes and work backwards.
Reply
Brian Cockburn
6/11/2021 09:32:25 am
I would survey the existing system and do a hydraulic calculation to see how much capacity there is. It is possible that the existing sprinkler system could deliver higher amounts of water.
Reply
CJ Bonczyk
6/11/2021 09:39:31 am
There are still some factors about the storage arrangement & commodity in the occupancy to confirm if adjusted your remote density area calculation is allowed. However, if you have fully surveyed the existing system, and completed a RECENT flow test including any appurtenances back to the hydrant location you can determine the actual hydraulic capability of the system. You might get lucky and see that the water supply availability actually got better since the original design was installed (but most of the time this is not the case). Complete a total survey of the existing system. Prior to completing any calculations have the owner fill out to its entirety an owners commodity classification form. This information is critical so that if/when you modify the existing system you can place with the new hydraulic placard the additional sprinkler system general information placard as required per NFPA 13.
Reply
Jon Sullivan
6/11/2021 12:39:54 pm
Recent being within the past year.
Reply
Wes
6/11/2021 09:59:53 am
We partner with local sprinkler contractors and help perform these calculations regularly. If the capacity of the existing system won't match the new storage arrangement, we'll find ways of economically upgrading or replacing the system to get it to work.
Reply
Dorg T
6/17/2021 03:01:27 pm
As mentioned you cant do anything without a hydraulic calculation.
Reply