MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Hydraulic Calculations for Fire Pumps in Parallel?

9/18/2020

6 Comments

 
I have a job where there are two existing diesel fire pumps that serve an existing warehouse (2 million sq. ft +).

The building is surrounded by an existing 12" underground fire supply loop. The two diesel pumps serve the space.

According to the property manager the system operate as follows:
(1) Pressure is maintained at 160-175 psi.
(2) Below 160 psi the jockey pump turns on to maintain 160-175 psi.
(3) Fire Pump #1 turns on when pressure drops below 150 psi to maintain 175 PSI. (Fire Pump - Static: 165 PSI ; Residual: 134 PSI @ 2000 gpm).
(4) Fire Pump #2 turns on when pressure drops below 140 psi to maintain 175 PSI (Fire Pump - Static: 190 PSI; Residual: 174 PSI @ 2000 gpm).

The pumps are provided by a municipal supply and a back-up private lake dedicated for the fire service.

The pumps are in parallel, so you would add the flows. And to my knowledge the higher pressure would overtake the smaller pressure.

My question is, how do you determine how to calculate the system hydraulically?

If I only use fire pump #1 for water supply, it will not be an accurate representation on how the system operates. In this case it also is very difficult to get the system to work hydraulically off of one fire pump.

I appreciate any input!

​​​​​​​​​​​​​​​​Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
6 Comments
Brian Gerdwagen FPE
9/18/2020 10:34:06 am

This is a fun question. The simple answer is that you would add the flows at the lower pressure. But it is in reality much more complicated.

You need to calculate the system demand to the pump outlets. This will determine what flow and pressure the pumps need to be able to operate at to supply the sprinklers. This demand, if the pumps are close together will be about the same. Then it is a matter of finding the pressure the pumps are generating with the required flow.

You are right in that a higher pressure from one pump will close the check valve of the other pump, but if one pump can not supply all the flow, the other one will kick on and supply something. There is a point where they are both operating at the same pressure, but with different flows. The less powerful pump will operate higher in its curve as it flows less water. That's what needs to be determined.

Start by putting in both pumps with a separate water supply equal to the domestic and make sure everything is entered in the calculation properly. You will probably need to manually divide and input the water flow to each pump as it will be getting approximately half the water it would normally get at the normal flow from the domestic.

Reply
Ivonn
9/18/2020 11:49:00 am

Pumps are operated in parallel as a means of flow control and for emergency back up (installed spare). However, if the pumps are not properly selected for parallel operation, or operated in the most optimum combinations, pump reliability can be compromised. Operating the wrong pumps in parallel can even cause one of the pumps to operate at shut off, resulting in over heating and failure.

Pumps need to operate at the same head when they operate in paralle,

Pumps with head-capacity curves that droop towards shut-off, or have a dip at a higher flow rate which has more then one flow condition for a given head, should not be operated in parallel.

Maybe one of the pumps is only for back up and the calculations will be doing just with one of them.

Reply
Pete D.
9/18/2020 11:57:14 am

Use the primary pump curve and calculate to the discharge flange.
I'm guessing that one pump will provide the larger of the highest sprinkler system demand or the fire flow. In most cases, parallel pump installations are for increased reliability, not added flow. In reality, the secondary pump may come on, but it wouldn't need to be considered in the demand calculation. If you need a Source Calculation, for example to size a foam bladder tank, I would recommend making a hybrid pump curve adding the flow of the secondary pump at its on pressure threshold on the primary curve.

Be careful setting up on/off thresholds. I have a site with 2 parallel pumps on opposite sides of the property and there's a 17 foot elevation pressure gradient between them. Thresholds cannot be established using gauge pressure local to each pump.

Reply
SK
9/18/2020 06:52:55 pm

This post is real fun. I agree with Brian and will not repeat what mentioned already but I'll try to add bit more based on my limited understanding and conclude as below;

1. Both pumps are rated differently, so can draw pump curves at 150%, 100%, Shutoff with corresponding pressures and use these value in hydraulic cals, will give you duty point for each pumps. If you know rated flow and pressure, then use those values.
2. Based on settings, the best fit is your system demand is 175 psi @ X gpm (but this is definitely over 2000 gpm, can not be met by single pump, so second pumps needs to operate).
3. Pumps setting is not matching with NFPA's recommendations. See below requirement;
(a) The jockey pump stop point should equal the pump churn pressure plus the minimum static supply pressure (in your case consider it 175 psi.
(b) The jockey pump start point should be at least 10 psi (0.68 bar) less than the jockey pump stop point. in your case, it's 160 psi, more is acceptable here.
(c) The main fire pump start point should be 5 psi (0.34 bar) less than the jockey pump start point. Use 10 psi (0.68 bar) increments for each additional pump. Here is difference, In your case, it's 10 psi difference before starting main lead pump, then lag pump should start at 145 psi. But this will not make difference in cals.
4. Either the pumps can be made lead or lag, sequence will follow accordingly. Lag pump will only will start & continue to operate if lead pump not able to meet system pressure (say 175 psi).
5. The final pressures should not exceed the pressure rating of
the system ( ensure this is within the design pressure of pipes) otherwise you will end-up with overpressure protection mechanism.

See one more example;
Examples of fire pump settings follow:
i. Pump: 1000 gpm, 100 psi pump with churn press of 115 psi
ii. Suction supply: 50 psi from city—minimum static; 60 psi from city—maximum static
iii. Jockey pump stop = 115 psi + 50 psi = 165 psi
iv. Jockey pump start = 165 psi - 10 psi = 155 psi
v. Fire pump stop = 115 psi + 50 psi = 165 psi
vi. Fire pump start = 155 psi - 5 psi = 150 psi
vii. Fire pump maximum churn = 115 psi + 60 psi = 175 psi

6. To answer your question, both pumps will remains in operations (both consider duty pumps), only flow will distribute (as pumps ranges 0 to 150 %).

I hope this will help you to proceed.

Reply
Franck
9/20/2020 07:50:42 am

As already indicated, fire pumps ate normally one in duty and one in back up.
Except in some countries where you may have 3 x 50% pumps (UK, for example).
So for your calculations you compare with the less performant pump (which would be used if the other is impaired / under maintenance).
If for some demand points you need more than one pump (insufficient flow and/or pressure delivered) you can compare with both pumps in operation
Pretty easy
1. You draw the flow curve of pump 1 from 0 to 150%
2. You draw the flow curve of pump 2 from 0 to 150%
3. You draw the combine curve by adding the flows at the same pressure for each pump

If you have problems doing this, please contact me at [email protected] and I will do it for you if you provide me the fire pumps test results (steps 1 & 2 above)

Reply
Tony C
9/22/2020 06:05:08 pm

Thank you all for your valuable input and insight! Thank you MeyerFire for putting this topic out there for discussion.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Aug '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT