Hydraulic Calc's Req'd for "Like-for-Like" Repair?

7/6/2022

14 Comments

 
In a strict "like-for-like" repair, are hydraulic calculations required?

Is there a code basis either way?

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
14 Comments
James Phifer
7/6/2022 08:08:53 am

If it's like for like, then nothing has changed and the calculations should be fine. Must be like for like though. Same k-factor or same friction loss characteristics, same equivalent length.

Reply
Jesse
7/6/2022 08:12:22 am

That is entirely an AHJ question, and AHJs in my area differ. For most, no. But a few want updated hydraulic calculations to assess how any degradation in the latent water supply may affect design density.

Reply
Peter
7/6/2022 08:13:56 am

No. Provided that legacy system didn't use specially listed sprinklers.
Must match pipe schedule.
Must match all sprinkler characteristics. Activation temp, response, orifice.


In some cases, the AHJ may require to recalculate if a permit is pulled, but it's sufficient to show that the water supply hasn't degraded since the legacy installation.

Reply
JI
7/6/2022 08:23:29 am

Like for like may be okay in some circumstances, however the code does change. If an old sprinkler system is to be completely redone from the alarm valve or whatever the scope of work happens to be, then everything upstream may require an upgrade. Generally work of this scope will require a permit, and the AHJ will dictate what is to be done. For example, the AHJ may want the system to be updated to current code if the existing system is not up to standards.

I would say any AHJ with knowledge of sprinkler systems would at the very least accept the old hydraulic calculations if given a current flow test that shows the water supply is still adequate.

My code basis for a new flow test being the minimum required is as follows:

NFPA 13 2013 23.1.1* Working plans shall be submitted for approval to the authority having jurisdiction before any equipment is installed or remodeled.

I would still consider this install a "remodel"

I would start by resubmitting the existing plan with a new flow test showing the old hydraulic demand is under the new water supply curve.

23.2.1.1* Where a waterflow test is used for the purposes of system design, the test shall be conducted no more than 12 months prior to working plan submittal unless otherwise approved by the authority having jurisdiction.

Hopefully your AHJ will accept this.

Reply
Dan Wilder
7/6/2022 08:32:26 am

13 19' Edition for Existing System Modifications

Nothing specifically (to my knowledge) says "Like for Like" doesn't trigger additional requirements, it just deals with "When" system modifications occur, this is what to do.

I would argue that is the required signage is on the riser, the water supply has not changed, and everything is going back in the same (just newer) that calculations would not be required.

Most of my jurisdictions follow this approach via modifications or agreements after the fact.

Reply
Glenn Berger
7/6/2022 08:34:18 am

The above is a very good discussion on this subject. Just curious, why is there going to be a "like for like" repair being preformed?

Reply
Adam Jensen
7/6/2022 10:34:37 am

I posed the question.

This is a large (multiple acre) manufacturing facility with a detached pump house. A 16' long section of 12" steel flanged pipe sprung a leak, and further investigation showed pocking throughout this section. The damage is pretty well isolated to this one section of pipe. The cause is unknown. Other repairs include several instances of ongoing leaks and excessive corrosion at threaded joints. All the work is in the pump room. Previous plans for the plant are not to be found.

Reply
Glenn Berger
7/7/2022 08:14:36 am

Recommend getting a water analysis preformed. What is the source of the water supplied to the site?

AB link
7/6/2022 08:37:36 am

You as the designer will have to decide if you are comfortable with the changes you are making - comfortable that they are not affecting the original design; pipe is the same, elevations are the same, drops are the same (flex versus hard-pipe), sprinkler heads are still flowing the same GPM as originally calculated, fittings, etc.

Is there an occupancy change? Are the changes being made in an area close to the system riser? Are you making changes to the hydraulically most demanding area? Did they remove/add walls that may affect your sprinkler spacing/demand?

In the end, it all comes down to what the AHJ wants.

We do work in Raleigh, NC and are required to provide hydraulic calculations for ALL renovations, including a one-head add. We do not have to provide a full analysis - however, we have to provide calculations back to a point on the existing system (if we have the existing system calculations showing the original demand). We design and submit system modifications referencing NFPA 13, 2016, 8.15.20.5 Revamping of Hydraulic Design Systems while also referencing the Annex note: "It is not the intent of this section to require a full hydraulic analysis of the existing piping system in addition to new sprinkler layout". (It's probably good to note that the Annex note has been removed from newer editions of NFPA).

Now... I don't necessarily agree with providing a one-head calc for a light hazard room adjacent to the riser room... however silly I think it is - I'm held to it by the AHJ's requirements for plan submittal.

Honestly... it took me longer to write this comment than it would to provide a calculation. If you're using a computer based program, it's typically a quick process. Maybe that's the answer and you'll be able to sleep at night knowing you did the "right" thing. I don't know...

Ultimately, if the AHJ doesn't have a standard regarding when to provide calculations, it's a judgement call.

Reply
Anthony
7/6/2022 08:47:02 am

In a like for like replacement 'most' code treats it as a repair and leaves it alone.

Remember if you're replacing hard pipe with flex drops that's not 'like for like' and many over seeing bodies will ask for a clac then.

Reply
sean
7/8/2022 09:13:53 pm

One question would be from the AHJ what proof does the existing system is in compliance. Could the original be pipe schedule? Were modifications made from the original design?

Reply
AHJ
7/9/2022 06:22:20 am

As an AHJ and FPE (Go Terps!), I require a scope of work letter that states the nature of the repair/replacement. In most cases, a like for like will not trigger a plans review. I also have field inspectors that usually visit the work site to view the progress and scope of work. If in his judgement, the work goes beyond the original scope, then a work stop order is issued and a formal plans review will be required in order to continue.

Work of that nature is usually done by local fire protection contractors, all if whom are known by our office, so we usually don't have any problems.

In my opinion, it really is a judgement call as to when to require formal plans for repair/replacement and like for like work.

Reply
Alex
7/9/2022 09:50:45 pm

Hi,

Responding a few days late here - spent the time away with family for the 4th.

This is too funny. I just responded on the flex head requiring calculations (before reading this question) and said if it was a like to like, I wouldn't require calcs.

I wouldn't require for a 1 for 1 if it is truly similar.

Thanks,
Alex

Reply
Howard M. Wren link
6/20/2023 02:01:23 pm

Great blog post! I appreciate your insightful perspective on fire repair. If you're interested, we have a site that offers valuable information on hydraulic calculations for such repairs. We'd love to hear your thoughts!
https://www.teamossanna.com/commercial-water-damage-restoration-phoenix-az/

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Dec '25 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    Nfpa-409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT