MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

How to Treat Storage Room in 13R Apartment?

11/2/2023

8 Comments

 
We have an NFPA 13R (2019), 4-story apartment. It's Group R-2, Class V-A construction, with open interior breezeways hallways in "garden style". Combined, all floor levels are ~60,000 sqft (~15,000 sqft per floor).

The design includes one 320 sqft storage room and about four 55 sqft storage closets in the interior breezeway per floor that tenants can rent if they choose.

All storage rooms and closets have gypsum ceilings.

From what I can tell, NFPA 13R-2019 doesn't really address storage like this, so I'd assume to revert back to NFPA 13 in order to protect? Is that a correct approach?

Due to the combustible construction - would that trigger coverage above and below ceilings in these spaces?

And then - am I permitted to tie into an NFPA 13R system, or would this even need a separate riser?

We could have two scenarios - one with rooms 2-hour fire resistance rated from the R-2, and another where it's incidental and not separated.

Thanks in advance for your input.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Pete H
11/2/2023 07:18:12 am

Check NFPA 13R (2022 edition referenced)

Sections 7.2.3.1:

For compartments 500 sq. ft. or less that meet all of the following conditions and are protected with quick response sprinklers, the design area shall be permitted to be limited to the number of sprinklers in the compartment but not shall not exceed four sprinklers:

1) The area is protected with 30 minute-rated construction,
2) The sprinklers are spaced at 225 sq ft max for light hazard, 130 sq ft max for OH, or in accordance with their listing
3) Openings have a lintel depth at least 8 in. in depth
4) The total area of openings, excluding any overhead doors that open to the exterior, does not exceed 50 sq. ft.
5) Discharge Densities are in accordance with NFPA 13

[Due to #5, you may need to throw on an additional calc to justify the density]

Also worth consideration:

7.2.4: Where residential sprinklrs are used outside the dwelling unit as allowed by 6.2.2.2, the discharge criteria shall be in accordance with Section 7,.1, except as modified by 7.2.4.1,
7.2.4.1 Residential sprinklers shall be permitted to be used in ordinary hazard areas that meet the following conditions:

1) The area is compartmented into 5000 square feet or less by 30 minute fire rated construction
2) the sprinklers are spaced at 130 sq. ft. per sprinkler
3) Openings have a lintel depth at least 8 in. in depth
4) The total area of openings, excluding any overhead doors that open to the exterior, does not exceed 50 sq. ft. per compartment
5) Discharge Densities are in accordance with NFPA 13 for ordinary hazard.

---

Additionally consider that garages, which are also ordinary hazard, are listed to also have protection in accordance with Section 7.2 if they are accessible by people from more than 1 dwelling unit.

--

I believe you're still in NFPA 13R, so the above and below in combustible construction is still not required as per Section 6.6.6.

But obviously, check the references yourself and make your own judgments on whether you agree or not.

Reply
Todd Wyatt
11/2/2023 08:58:43 am

SUMMARY
The limited areas of the storage on each story constitutes an “Accessory Occupancy”. These storage areas can be assigned to the primary Occupancy Classification (OC) of Group R-2. They are permitted to be protected by the same automatic sprinkler system (ASPS) that protects the Group R-2 spaces.

EXPLANATION
The scoping Code (e.g. IBC-2021) determines WHERE an automatic sprinkler system (ASPS) is required to be provide based on either the Occupancy Classification(s) (OC) (Sections 903.2.1 through 903.2.10) and/or "Specific Building Areas and Hazards" (903.2.11).

A Group R-2 Residential OC is required to be “provided throughout all buildings with a Group R fire area” with an ASPS per 903.2.8 Group R.
The type of ASPS (NFPA 13, NFPA 13R, & NFPA 13D) for a Group R is determined by 903.3.1.2 based on the floor level of the highest/lowest story(s) and the number of stories. If it meets all of the conditions, then NFPA 13R is permitted to be installed versus NFPA 13.

The areas of the storage spaces on each story … 320 sf + 4(55) = 540 sf/story … and the area of each story … 15000 sf … constitutes an Accessory Occupancy since the storage areas are <10% of each story (540/15000 = 3.6% < 10%). For this reason, the building is not required to be classified as both Group R-2 and Group S Storage; just Group R-2 (per 311.1.1 Accessory Storage Spaces). No separation is required between accessory occupancies (storage) and the main occupancy (residential).

If the storage areas were >10% (>1500 sf) of each story’s area (15000 sf), then the storage areas would be required to be classified as Group S Storage and would need to meet the ASPS per Section 903 Automatic Sprinkler Systems. Depending on the hazardous nature of the stored items, it would be classified as Group S-1 Moderate-hazard Storage or Group S-2 Low-hazard Storage. Each have different thresholds for when an ASPS is required. If an ASPS is required, it is required to be NFPA 13; NFPA 13R is not permitted for Group S.

Reply
Todd Wyatt
11/2/2023 08:59:18 am

REFERENCES
IBC-2012
Chapter 9 Fire Protection and Life Safety Systems
Section 903 Automatic Sprinkler Systems

903.2.8 Group R
An automatic sprinkler system installed in accordance with Section 903.3 shall be provided throughout all buildings with a Group R fire area.
903.2.9 Group S-1
An automatic sprinkler system shall be provided throughout all buildings containing a Group S-1 occupancy where one of the following conditions exists:
1. A Group S-1 fire area exceeds 12,000 square feet (1115 m2).
2. A Group S-1 fire area is located more than three stories above grade plane.
3. The combined area of all Group S-1 fire areas on all floors, including any mezzanines, exceeds 24,000 square feet (2230 m2).
4. A Group S-1 fire area used for the storage of commercial motor vehicles where the fire area exceeds 5,000 square feet (464 m2).
903.2.10 Group S-2 Parking Garages

903.3 Installation Requirements
903.3.1.2 NFPA 13R Sprinkler Systems
Automatic sprinkler systems in Group R occupancies shall be permitted to be installed throughout in accordance with NFPA 13R where the Group R occupancy meets all of the following conditions:
Four stories or fewer above grade plane.
1. The floor level of the highest story is 30 feet (9144 mm) or less above the lowest level of fire department vehicle access.
2. The floor level of the lowest story is 30 feet (9144 mm) or less below the lowest level of fire department vehicle access.
3. The number of stories of Group R occupancies constructed in accordance with Sections 510.2 and 510.4 shall be measured from grade plane.
903.3.1.2.1 Balconies and Decks
903.3.1.2.2 Corridors and Balconies in the Means of Egress
903.3.1.2.3 Attics

Chapter 3 Occupancy Classification and Use
Section 311 Storage Group S
311.1 Storage Group S
Storage Group S occupancy includes, among others, the use of a building or structure, or a portion thereof, for storage that is not classified as a hazardous occupancy.
311.1.1 Accessory Storage Spaces
A room or space used for storage purposes that is accessory to another occupancy shall be classified as part of that occupancy.

Chapter 5 General Building Heights and Areas
Section 508 Mixed Use and Occupancy
508.2 Accessory Occupancies
Accessory occupancies are those occupancies that are ancillary to the main occupancy of the building or portion thereof. Accessory occupancies shall comply with the provisions of Sections 508.2.1 through 508.2.4.
508.2.1 Occupancy Classification
508.2.2 Allowable Building Height
508.2.3 Allowable Building Area
The allowable area of the building shall be based on the applicable provisions of Section 506 for the main occupancy of the building. Aggregate accessory occupancies shall not occupy more than 10 percent of the floor area of the story in which they are located and shall not exceed the tabular values for nonsprinklered buildings in Table 506.2 for each such accessory occupancy. No separation is required between accessory occupancies and the main occupancy.
Exceptions:
1. Group H-2, H-3, H-4 and H-5 occupancies shall be separated from all other occupancies in accordance with Section 508.4.
2. Group I-1, R-1, R-2 and R-3 dwelling units and sleeping units shall be separated from other dwelling or sleeping units and from accessory occupancies contiguous to them in accordance with the requirements of Section 420.

Reply
Jack G
11/2/2023 09:26:17 am

In reading thru the question, about a storage room in a 4 story 13R apartment building, I question if 13R is applicable ( if building is subject to inc) as table 601 does not allow 13R in V-A construction. Please review.

Reply
Joe F
11/2/2023 10:45:21 am

If NFPA-13R is allowed for your project, then according to NFPA-13R (2019)
Δ 6.6.7 Sprinklers shall not be required in closets (regardless of size) on exterior balconies and exterior corridors, as long as
the closet does not have doors or unprotected penetrations directly into the dwelling unit.

Reply
R. Scott
11/2/2023 02:30:03 pm

they are "interior" open-ended corridors per the IBC definition, but I see the argument that they are "exterior" of the dwelling unit. We plan to provide coverage in them regardless of if the exception was acceptable.

Reply
Jack G
11/2/2023 11:24:55 am

Again I reiterate: the answers above include reference to a 30 minute rating ( reduced from 1 hour per IBC chapter 6)
If the rating of the construction was reduced, then 13R is not the right choice for the suppression system—- NFPA- 13 should be the applicable design. Consult Meyer Fire 13, 13R, or 13D .

Reply
R. Scott
11/2/2023 02:30:59 pm

the ratings are not reduced, they are 1-hr

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT