How to Treat "Flammable Solids" for Sprinklers?

7/5/2022

11 Comments

 
Working from an insurance perspective through a sprinkler design for a warehouse.

The warehouse contains "flammable solids" in carton storage. These are considered to be H228 "flammable solids", according to the California Highway Patrol (CHP).

Can these be protected as plastics?

Would we need to store these in a separate area?

Unsure how to begin to address these, thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Glenn Berger
7/5/2022 08:21:28 am

Separation of this hazard is typically required - exterior wall, fire separated from all other spaces. Exterior access may also be required.

Find the actual Safety Data Sheet and determine whether or not this material is water-reactive. If water-based system is acceptable than Extra Hazard Classification should be okay.

Reply
Dan Wilder
7/5/2022 08:32:09 am

No to plastics as a general condition, reading definitions (at a glance) some of these products don't react well to water, others look to have a small density requirement up to massive water dumping...and some just says "don't store where sprinklers are present if possible". There are some foam options I'm sure.

NFPA 1, NFPA 400, IFC Chapter 59, FM Global 7-85 sheets all have both building and fire protection approaches (prelim search) but best to hire a recognized FPE Consulting firm to leave the "no stone unturned" approach.

Reply
Anthony
7/5/2022 08:36:32 am

From a quick google search it seems that the H228 designation is form " Globally Harmonized System of Classification and Labelling of Chemicals." Further reading indicates this designation can indicate a wide variety of products. Much of the admittedly quick searching calls for a type "d" fire extinguisher indicating a metal fire hazard or a hazard where water would be inappropriate as an extinguishing medium.

I would suggest asking for an MSDS sheet for the products being stored. Assuming this is in the US they "should" have that information available for your perusal.

From the MSDS you can tell if its something NFPA 13 has already covered. Check the definitions for plastic/paper/wood in NFPA 13 to see if ESFR/CMSA etc. is appropriate.

I'd consult FM 7-85 or 8-1 once you have specific information. Generally if its been done before FM will have a data sheet on it. Its not 'code' but its a great guide to get you started thinking in the right direction.

Good luck.






Reply
Jon
7/5/2022 08:47:19 am

If the project you are working on is in California, I suggest going through the California Fire Code to determine how to protect the flammable solids. In particular, Chapters 50 & 59 would be a good place to start your search.

Reply
Todd E Wyatt
7/6/2022 10:26:56 am

I agree ... the initial Code evaluation should start with the 2022 California Administrative Code (CAC) and the 2022 California Fire Code (CFC) to determine the classification of the Hazardous Materials (HM) and the Maximum Allowable Quantities (MAQ) of HMs per Control Area (CA).

Reply
Jesse
7/5/2022 10:16:09 am

I would consider a separation of hazard to begin with. And spend a lot of time carefully reviewing specifically what the flammable solid is, to make sure it's not water reactive.

Reply
FCS link
7/5/2022 11:16:12 am

Unfortunately, you'll need more information about about the specific type of flammable solid, quantities, state (powder, solid, shavings, etc.), storage configuration and builidng occupancy classification to determine the minimum fire protection design.

Some flammable solids (sodium, potassium, etc). can explode on contact with water) and water systems are prohibited if it is the only hazard present (NFPA 484-8.3.2). Assuming you are an IFC jurisdiction there are pile size limits (IFC 5904.1), and a number of other requirements that may affect sprinkler design.

Reply
sean
7/5/2022 01:35:09 pm

we need a ton more info about the material and storage arrangement to check design choices.

Reply
Franck
7/5/2022 04:03:36 pm

As indicated above, we need information on the nature of these « flammable solids ». By nature, I also mean its « form ». For example, with pyrophoric metal, titanium is flammable when present in the form of finely divided scraps or dust (can even become a dust explosion hazard) and water is generally prohibited as a fire extinguishing media. But the same metal in bars, plates… is not a problem.
And fines of this metal submerged in water is not a problem as well (it is the best way to collect and store them on site).
The hazard of water with metal fires is that water immediately breaks into hydrogen and oxygen, because of the very high temperature, and you have a potential for hydrogen explosion.

Reply
Christine Hoefflin
7/6/2022 12:26:57 am

Thank you for the responses. I now know it is a cellulose nitrate membrane material, cartoned (not a metal). It is not water reactive. This directs me to FM 7-86, although it is not a wetted powder or fibre. It is also not stored in drums. However the fire hazard may be similar, at least once it burns. If we do not receive fire test results, it seems to me that storing it in a separate room and choosing sprinkler protection according to FM 7-29 (as explained in FM 7-86) is justified.

Reply
Alex
7/9/2022 09:54:06 pm

Hi,

Responding a few days late here - spent the time away with family for the 4th.

I would recommend reaching out to the code consultant on board for the project. If there isn't one, advise the OPM to hire one. This is a multi-layed question that stems further than how to design the sprinkler system for the hazard. Contingent on the quantity, you will be a Group H occupancy and will need to follow additional design requirements.

Alex

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT