How to Sprinkler Protect Open Baffle Ceiling?

8/14/2023

7 Comments

 
What are the requirements for sprinkler coverage for baffled ceilings?

In Florida we use the 2016 edition of NFPA 13. I know that the sprinklers have to be within 12 inches of ceiling for heat collection. The contractor says the pictures shown are correct.

I think they need to place a 12 by 12 above the baffle for heat collection?

I found 8.6.3.4 Minimum Distances Between Sprinklers.
  • 8.6.3.4.1 Unless the requirements of 8.6.3.4.2, 8.6.3.4.3, or 8.6.3.4.4 are met, sprinklers shall be spaced not less than 6 ft (1.8 m) on center.
  • 8.6.3.4.2 Sprinklers shall be permitted to be placed less than 6 ft (1.8 m) on center where the following conditions are satisfied: (1) Baffles shall be arranged to protect the actuating elements. (2) Baffles shall be of solid and rigid material that will stay in place before and during sprinkler operation. (3) Baffles shall be not less than 8 in. (200 mm) long and 6 in. (150 mm) high. (4) The tops of baffles shall extend between 2 in. and 3 in. (50 mm and 75 mm) above the deflectors of upright sprinklers. (5) The bottoms of baffles shall extend downward to a level at least even with the deflectors of pendent sprinklers.

If sprinklers are installed above and below the ceiling, a baffle needs to be installed around the lower sprinkler to avoid cold soldering. Cold soldering occurs when discharged water from the sprinkler above cools the thermal element of the sprinkler below, preventing or delaying its activation in the event of the fire. The required baffle will prevent that water from contacting the thermal element of the sprinkler, thus circumventing the possible issue.
​
​Talked to some folks and we need the product paperwork as it may mention sprinkler coverage.
Picture
​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Anthony
8/14/2023 07:33:34 am

It looks like you may be able to use 8.15.14* Open-Grid Ceilings rules. I'm not sure you have the 18'' above the grid ceiling however.

If you are unable to use the open grid rules you'll have to have a layer of sprinklers above the ceiling and one at the bottom of the obstruction. You should probably use intermediate level sprinklers with splash guards.

There are no apparatuses that aid in heat collection other than a ceiling.

Reply
Dave
8/14/2023 11:06:03 am

Another variation, sometimes for aeshtetic purposes these slatted ceiling systems recieve a black layer of insulation laying over the tops of the slats.

Reply
Glenn Berger
8/14/2023 08:11:13 am

Anthony has an acceptable approach stated above. If an issue still persists, then use obstructed construction rules.

Reply
Jesse
8/14/2023 10:01:49 am

I tell my young designers that at times it will seem architects are the bane of their existence. This is an example of why. I think Anthony is on the right track.

Reply
Dave
8/14/2023 10:56:52 am

Heat collectors / pie tins that us old f**ts were accustomed to were not addressed in NFPA #13 for a long while, but after being proved ineffective (downturned edges actually proved worse) they became prohibited in NFPA 13 several cycles ago.

8.5.4.1.4 (2016 ed.)
9.5.4.1.4 (2019 ed.)

There is always a new trend / fad that challenges us - cloud ceilings; slatted ceilings; lately, arrays of hanging vertical baffles; BAF's; soffit material that has favorable flame-spread but is not non or limited combustible by definition....

Reply
Dave
8/14/2023 11:02:37 am

...which I have to teach trainees were different in function and purpose from intermediate level shields

Reply
Janak Patel
8/16/2023 01:43:38 pm

It appears from the photograph that the sprinkler deflector is more than18" from the flat ceiling above. Since beams are so 'closely spaced' (not 7'-6" apart) it will be difficult to apply the Ceiling Pockets rule, NFPA 13 (2019), Section 10.2.9. Therefore, the situation does not comply with NFPA 13.

A heat collector, (12" x 12" or 12" diameter metal plate) at each sprinkler, would not work unless a fire is directly below the heat collector. It will take longer to descend/form a 'hot gas layer' to activate a sprinkler, i.e., a potential fire will be of a larger size. On the other hand, if there is no sufficient combustible load on the floor, sprinklers may never activate in an event of a fire. (A study has shown that heat collectors are 'not reliable' and Listed heat collectors are not available in market anymore.)

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT