How to Sprinkler a Dome?

1/6/2022

14 Comments

 
How do I go about designing protection below a dome?

We have a church project, and the dome is 30'-0" in diameter and is about 15'-0" high. It's basically a hemisphere. 

Looking for tips/guidance/creativity on getting this one started. Thanks.

​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
14 Comments
Mike L
1/6/2022 07:39:33 am

The layout of the sprinklers should follow the requirements for steeped pitched roofs.

Use back-to-back 90 degree elbows to allow the sections of branch piping to follow the contour of the dome.

Reply
Jesse
1/6/2022 08:06:52 am

You can protect using the requirements for steep / pitched roofs in NFPA 13 chapter 8. If its within your hydraulically remote area, remember you may need to increase the size of the design are due to the slope.

Reply
Glenn Berger
1/6/2022 08:09:13 am

Dependent on the slope, just follow standard NFPA 13 rules. I had to sprinkler a Jefferson-style dome years ago and enjoyed watching the Contractor figure out the exact lengths of pipes required before each "swing joint" to follow the curve of the ceiling.

Reply
Alex
1/6/2022 08:30:18 am

Agreed with the responses above! Make sure you increase your remote area based on the pitch. Ensure you work closely with the contractors when it comes to installation that heads are not too far off the dome.

Reply
Emil Ohler
1/6/2022 08:34:02 am

If hydraulics allow, use flexible sprinkler drops. Your installers will appreciate it.

Reply
Dan Wilder
1/6/2022 08:49:54 am

Having done a retrofit on the NAU Walkup Sky Dome...

My layout was heavily dictated by the structure (triangles with 36" deep beams, segmented into slices by reducing beam sizes down to 12"). Sprinkler layout started around the perimeter walls for spacing, then I filled in moving up.

Do not layout everything flat at max spacing, as soon as it gets elevated the distance between sprinklers will exceed maximum spacing. If the dome is typical (structure), laying out a section and then copying that around will save a lot of time 1/4 or 1/5 typical sections have worked out well for me.

I've seen both concentric rings and a spoke pattern for domes so whatever works with your layout.

Reply
Jessica Lutz
1/6/2022 09:33:20 am

This is my jam!

My suggestion would be to first figure out what all of your "deal-breakers" are...i.e. new or existing architecture?, can the pipe be exposed/concealed?, what are my hanger/seismic attachments limitations?, is there an architect's aesthetic which should be considered?, are there any pipe type/material limitations?, are there lighting obstructions?, what's my deflector distance/spacing going to be?, etc.

THEN, get creative & brainstorm!
I start roughly modeling my ideas, and the solutions start to reveal themselves...

Also, if this is at the contractor/installation phase, I highly recommend getting the opinion of your Super/Foreman...

Good Luck!

Reply
David
1/6/2022 10:15:18 am

I agree with all the comments but no one touched on attachment fasteners. I recommend the Sammy Swivel attachments for dome applications.

Reply
Dave
1/6/2022 10:50:09 am

I concur with Jessica’s excellent points and approach - Where you can run, hang, and brace/restrain the pipe is where I would start. Is there a conditioned space above the dome? If so, concealed sprinklers (perhaps one of the smaller-diameter ones that are available), custom-painted, if necessary, would look decent. Put on your architect cap for an acceptable, code-compliant sprinkler layout. If the piping must be exposed below, then it gets tricky, but sprinkler pipe is beautiful. Bending of pipe, as allowed in NFPA 13 can lead to impressive installations. (Check out photos of the main hall at LeMay / America’s Car Museum.) I am aware of dome structure similar to yours where the AHJ allowed protection by a ring of sidewalls down low, on an electrically-activated deluge system.

Reply
CONNOR
1/6/2022 11:52:04 am

For aesthetic purposes, I would like to add a caution on using back-to-back elbows to make the bends. Especially with grooved fittings and mechanical couplings, it can quickly become busy and distracting compared to other installation methods.

If bending pipe is not an option, another solution for making low-angle bends in piping is a short braided flexible hose. There are UL-Certified flexible hoses which are suitable for use on mains and branch lines. One example is here: https://mason-ind.com/gwn-gwn-ul/

If the hydraulics are accounted for, a few strategically placed flexible bends may make fabrication easier, and most models can even be painted to match the pipe.

Reply
Anthony
1/6/2022 12:52:00 pm

8.6.3.2.5 Under curved surfaces, the horizontal distance shall
be measured at the floor level from the wall, or the intersection of the curved surface and the floor to the nearest sprinkler shall not be greater than one-half the allowable distance between sprinklers.

fyi

Reply
sean
1/7/2022 02:17:20 pm

no matter what it will suck, but a consistent design look will over better if exposed

Reply
hamilton roofing link
5/9/2023 07:20:01 am

ADM Roofing Ltd is a highly-efficient, reliable roofing contractor providing first class roofing services in Glasgow, committed to putting you, the customer, first.

Reply
Screens Porch link
12/27/2023 12:15:50 am

Welcome to Blue Tide Exteriors! Elevate your outdoor living with our premium Screens Porch solutions. Transform your space into a haven of comfort and style. Our expert team crafts durable, customizable screens to enhance your porch experience. Explore the perfect blend of innovation and design

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT