How to Set Jockey Pump Shutoff Pressure?

2/10/2022

14 Comments

 
Hi everyone - I need advice about jockey pump sizing.

The system we have has a city supply plus a booster pump. The city main shut-off pressure is 42 psi (2.9 bar) and the booster pump shut off pressure is 27.5 psi (1.9 bar).

So, combined, the pressure is 69.6 psi (4.8 bar).

The jockey pump pressure should be about 10 psi (0.7 bar) higher than the booster pump pressure. So, the jockey pump shutoff pressure should be 27.5 psi + 10 psi = 37.5 psi (1.9 bar + 0.7 bar = 2.6 bar)?

Is this correct, or is the jockey pump shutoff pressure the combined 69.6 psi + 10 psi (4.8 bar + 0.7 bar)?

​Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
14 Comments
Nick D
2/10/2022 08:17:09 am

Your jockey pump stop pressure should be set at 69.5 psi. This is based on:
maximum city supply + rated pump shutoff pressure

You would want your jockey pump to start at 10 psi lower (59.5 psi) and then you fire pump to start to start 5 psi lower than that (54.5 psi).

Of course this is just best practice, but has worked for me in the past.

Reply
Glenn Berger
2/10/2022 08:17:19 am

See NFPA 20 A.14.2.6 (4)(f) for additional information. The pump starting pressure should be 10 psi different, not the stopping pressure.

Reply
Colin Lusher
2/10/2022 09:32:15 am

Nick is correct:
Jockey pump stop should be 69.6 psi.
Jockey pump start should be 59.6 psi.

Main pump stop should be 69.6 psi
Main pump START should be 54.6 psi, however, it's not uncommon to drop that another 5 psi to 49.6 psi (10 psi below JP) if you have trouble with the main pump starting during normal day to day pressure fluctuations.

Reply
Alex
2/10/2022 09:37:26 am

Nick outlined the requirements well above.

For a code outline of start and stop points, refer to NFPA 20 (2016) A.14.2.6 (4)(f)

Reply
Whitfield link
7/24/2025 02:32:33 pm

Hey guys I have installed a 200 PSI pressure gauge between a gravity fed tank and jacklie pump but not getting any reading on the gauge. Any suggestion?

Reply
Jesse
2/10/2022 09:38:13 am

Hopefully this helps from 2016 NFPA 20 A 14.2.6 (4)

(4)
Fire Pump Settings. The fire pump system, when started by pressure drop, should be arranged as follows:

(a)
The jockey pump stop point should equal the pump churn pressure plus the minimum static supply pressure.

(b)
The jockey pump start point should be at least 10 psi (0.68 bar) less than the jockey pump stop point.

Reply
Franck
2/10/2022 11:07:53 am

All the above mentioned settings are correct.
It looks like there is a confusion in wording in your question.
What you call city water shuttoff pressure is probably the static pressure of the city water.
And what you call booster pump shutoff pressure is the churn pressure (pressure delivered at no flow).
While the booster pump shutoff pressure is the pressure at which your jockey pump should stop. In other words, the pressure you need to maintain in your sprinkler system downstream the booster pump.

Reply
Franck
2/10/2022 11:27:38 am

Just a correction to my message (this is what happens when you answer with your phone, sorry for that…) for the last sentence
You should read :
« While the Jockey pump shutoff pressure is the pressure at which your jockey pump should stop ».

The purpose of the jockey pump is to maintain a pressure in your system close to the pressure that will be delivered when your booster pump will start.
The different settings (difference of 10 psi and then 5 psi) is to limit a possible waterhammer effect when the booster pump starts (which could happen if the fire pump starts at a very low pressure compared to the one that will be delivered by the pump).

Reply
Jake
2/10/2022 11:52:33 am

Hi! I am glad that the issue sparked a debate.
English is not my native language so some of the terms may be wrong. thank you for correcting.

So when the static pressure of The City Water is 2.9 bar and the booster pump churn pressure is 1.9 bar. Compined 4,8 bar.

And same static pressure of The City main
affects to the Jockey pump so 2,6 bar churn IS enough for it? Compined (2,9+2,6) 5,5 bar.

Theres no need to calculate IT like this:
Static pressure of The City Water+ Booster pump churn+ static pressure + 0,7 bar..







Reply
Franck
2/11/2022 10:43:30 am

English is not my native language as well ;)

Jesse
2/10/2022 02:25:05 pm

Thanks for the clarification. I kinda wondered about the "shutoff" comment too.

Reply
HAHANE AROMA
5/22/2023 11:12:42 pm

Should the jockey pump be left on manual switch on/off. The property owners that I am dealing with have always been switching the pump on when they see the pressure is low and switch off when the pressure reaches the level they have marked.

Please advise if this is OK.

Reply
lalith ramachandra
4/28/2024 07:58:17 pm

Given that water is incompressible, as soon as a hydrant is opened, the water pressure in the whole system will drop to the standing pressure?

Reply
Whitfield Joshua link
8/12/2025 07:16:05 am

Hi Guys I am new. I am having problem with Jacky pump stop setting. The pump has a system pressure approximately 70 PSI; the pump is also fed by an external tank at the same level as the pump. The pump is not shutting. Any idea

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top April '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    Nfpa-409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT