MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

How to Seismically Brace a Schedule 7 Main?

12/27/2023

6 Comments

 
We have a tree, wet system, we are using Schedule 7 for the mains and branch lines.

We are trying to design the seismic bracing, and the main is only strong enough for one side of branch lines, not the opposite side too.

Should we use stronger pipe, or install more laterals?

Is there a way to brace the branch lines to take the weight off the mains?

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
JI
12/27/2023 08:32:08 am

When I have this problem, I tend to lower the spacing for laterals to 30 ft which allows for a greater zone of influence to be used as per the charts in NFPA 13, and also lowers the footage of pipe required in the brace calculation.

I cannot recall using schedule 7 pipe with seismic bracing, however schedule 10 will allow for a larger zone of influence than schedule 7. I would imagine that the difference in zone of influence versus the increase of pipe weight will work more in your favor when performing the calculations in a software package such as Tolbrace.

There is always the idea to increase main sizes and decrease line sizes (within the bounds of the hydraulic calculations) which will give a larger zone of influence for mains and decrease the weight of the line piping.

As per NFPA 13 2019, you may omit the branch lines from the main calculation if you satisfy 18.5.9.6. and install longitudinal braces on the branchlines.

Reply
Casey Milhorn
12/27/2023 09:57:28 am

I agree with the first comment. I would probably do a quick and dirty cost analysis on the two scenarios. Also check your hydraulic calculations to make sure the change to sch. 10 doesn't hamstring you and cause larger main/line sizing.

Something else to consider is corrosion. I'm always a fan of going with thicker wall pipe when it is in the budget.

If you are the contractor on this, and it's not a design build, I highly advise laying out the options for the owner/EOR/design team and let them decide. Ultimately if ANYTHING happens with this system you will be liable for making a call concerning actual specification changes.

Reply
Dan Wilder
12/27/2023 10:11:44 am

My designs always added more main bracing to avoid branch line bracing at all costs. You would need to add longitudinal bracing to the BL’s to remove weight from the main.

If it gets to the point of extremely close bracing, maybe look at changing the main to Sch 10 and keep the BL Sch 7. There’s a price point break where the material costs for the main pipe schedule increase would be better than the material and labor costs of all the bracing being added.

Reply
Pete D.
12/27/2023 11:27:58 am

What size is the main? Note that the schedule 5 table for maximum horizontal loading stops at 4" diameter. In the notes it states, larger diameter can be used when justified by engineering analysis.

They're trying to prevent sheer in the conveying pipe due to bending. With lateral bracing, you will have a distributed load with fixed reactive forces at the braces, resulting in 3-point bending. If 4" or smaller, you can use the Schedule 5 table. If over 4" you will need an engineer to compute the section modulus of schedule 5 pipe (whatever diameter you're using), and based on the horizontal load, Fwp based on the shortwave spectral response in the area of the installation, determine the maximum bracing interval to minimize bending to within the elastic region of deformation on a stress/ strain curve. Or... replace it with Schedule 10.

Reply
sean
12/31/2023 06:36:07 pm

I think I too would lean towards sch 5.

Reply
Michael Christensen
1/18/2024 11:53:39 am

All of the manufactures that I am aware of (such as Eddy-Flow or Mega-Flow) publish their own tables that have the information. When I have used Sch 7 piping I reference the table from the manufacture when doing these calculations.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT