How to Recertify or Address Old FRT Wood?

11/21/2023

5 Comments

 
I am working on a project that has Fire-Retardant-Treated (FRT) wood that is over 50-years old.

The wood is installed in a conditioned space (not subjected to sunlight or rain, heated and cooled with moisture levels maintained like any building). The wood had different manufacturers with varying labels, but two did list the chemical used as PROTEXOL.

I'm struggling to find information for the efficacy of the FRT wood after so many years.

Do you have any information or recommendations for recertifying FRT wood with lab testing for the presence of the correct chemicals or subjecting samples to ASTM/UL/NFPA?

Any help is greatly appreciated.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
Dan Wilder
11/21/2023 08:59:29 am

Depending on how it was applied will play into its lifespan. Surface applied, dipped, pressure treated....also the location..was it near heavy humidity and/or heat areas (boilers, steam lines, pipe chases, heaters, southern exposure vs northern, snow/ice loading). Conditioned spaces aside, there will still be variations so providing a solid test sample criteria will be important, also assuming that the pieces can be removed without impacting the structure.

You could reach out to NGC and see if they have procedures and protocols for recertification.

https://www.ngctestingservices.com/

Like many things with older construction (when they built things to last, not just to be easily replaced), it is likely still viable and has years left, proving it is another matter.

https://ia802503.us.archive.org/18/items/protexol-corp.-1946/Protexol%20Corp.%201946_text.pdf

Reply
Conrad
11/21/2023 11:56:15 am

If the intent is to avoid adding sprinklers to an existing combustible concealed space (or to prove it is limited combustible), it may be more cost effective to clad the 50 year old wood in something acceptable to the AHJ like a layer or two of drywall.

Might be a reach so forgive me if I am incorrect.

This is reminding me of a smoldering fire in the fireproof coating on steel beams in a commercial attic. The coating worked but somehow it also smoldered which involved scraping off the coating in an attic you could not standup in. Maintenance used it as a storage room and to charge tool batteries.

Reply
Jack G
11/21/2023 01:00:59 pm

I ve found that “ fire treated wood “ shrinks thru the years causing weakened structural strength fasteners popping. Lasalle Library in Philadelphia they had to rip the roof off and replace it with normal wood and fire sprinklers. Have an engineer check it out before doing anything to it.

Reply
Greg
11/27/2023 11:08:30 am

As it happens, I was observing some construction in my home town that was using d-blaze plywood. Thinking about the full lifecycle of the commercial-residential building, I looked up the manufacturer's cut sheet to understand how long the treatment would last. Basically, the same question you are asking but at the beginning of the building's life. A bit of reverse engineering in comparing the old product to a similar new product may be useful. In other words, a comparison to the pressure impregnation process and the chemical used in that treatment to the chemicals used today and treatment process. Also, was there any UL testing that covered the product then, and is it similar to the testing of today. Interestingly, the fact sheet for d-blaze is not stating any period of ineffectiveness, assuming all conditions are maintained.

From the Fact Sheet online, it states,
"HOW LONG WILL THE TREATMENT LAST?
D-Blaze® fire retardant treated wood is designed for above ground use that is sheltered from precipitation and direct wetting. Under these conditions, D-Blaze chemicals will not leach out and will remain stable and effective"

Reply
Greg
11/27/2023 11:18:08 am

this might help in your efforts to backtrack across listings. d-blaze is stated as listed on this webpage from California. Possibly, there is a trail to follow to previous similar listings.

https://osfm.fire.ca.gov/what-we-do/fire-engineering-and-investigations/building-materials-listing

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT