How to Protect Storage with a 10'-20' Clearance?

2/13/2023

6 Comments

 
I am trying to figure out how to protect an existing building that has never had a sprinkler system.

The building peaks at 46'-5" and in that area you can only have a max height of 25'-0 in storage, due to operable cranes in the bay.

Additionally, the building is constructed using 12" purlins, so ESFR pendants are out unless we want to put them on return bends.

I am trying to give the owner as much storage space as possible, and commodities as they plan to rent the building out to tenants in the future. I have searched through CMSA, CMDA, ESFR and storage to find a situation that best describes it.

The issue I always come up on, is the distance from top of storage to ceiling. Every scenario I have looked at, we seem to exceed the 10' or 20' maximum distance.

Does anyone have some criteria they used that is close to the situation above?

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Peter Howard
2/13/2023 07:54:58 am

A couple of ideas, please take all with a grain of salt:

with ESFR pendents on return bends, is there one that gets you 18" below deck? That'll get you under 45'-0" for deflector height and make it so you could have a 20 foot difference.

-

You're calculating to a maximum storage height. Just because they're actual storage is peaking out at 25'-0", is there any reason you can't calculate a system that would allow them to have 30'-0" or 35'-0" storage in the future? Especially with ESFR heads.

-

The difference between 46'-5" and 45'-0" just isn't that much. Can you talk to and convince the AHJ to "grandfather" in a coverage that while it hasn't been tested to a full listed/per code acceptance.... is so close that the difference is negligible and the system should still protect any conceivable fire situation long enough for fire department support, especially if there is standpipe present and high temperature heads. Especially if the architecture of the building forces you to go outside of accepted codes and standards anyway.

-

Ultimately, I know nothing about the project and can't research this fully, so again, take with a grain of salt, but maybe it's some things to think about.

Reply
Glenn Berger
2/13/2023 08:15:22 am

Storage Occupancies are difficult to provide one size fits all solution. You are pretty much on the right track in your procedures. I did not see any statement on the propose commodity to be stored.

Reply
Todd E Wyatt
2/13/2023 09:05:40 am

The scoping Code (e.g. 2021 IBC) determines “Where Required” an automatic sprinkler system (ASPS) is required per the Occupancy Classifications (OC) of the building.

The referenced standard (e.g. 2019 NFPA 13) determines HOW “sprinklers shall be installed throughout in accordance with NFPA 13.”

This building would (probably) be classified as a Group S-1 Moderate-Hazard Storage ... an ASPS is require if the building includes (1) of the (4) conditions:
1. A Group S-1 fire area exceeds 12,000 square feet.
2. A Group S-1 fire area is located more than three stories above grade plane.
3. The combined area of all Group S-1 fire areas on all floors, including any mezzanines, exceeds 24,000 square feet.
4. A Group S-1 fire area used for the storage of commercial motor vehicles where the fire area exceeds 5,000 square feet.

Assuming this building meets one of these requirements, an ASPS is required.

For buildings including “high-piled combustible storage” (HPCS), the 2021 IBC references the 2021 IFC :

Section 413 Combustible Storage
413.1 General
High-piled stock or rack storage in any occupancy group shall comply with the International Fire Code.

The 2021 IFC includes an entire chapter on HPCS : Chapter 32 High-Piled Combustible Storage. I recommend you request additional information (e.g. Commodity Classification) from the Client to determine the prescriptive requirements for the “General Fire Protection and Life Safety Features” (Section 3206) for this HPCS.

REFERENCES
2021 IBC
Chapter 9 Fire Protection and Life Safety Systems
Section 903 Automatic Sprinkler Systems
903.1 General
Automatic sprinkler systems shall comply with this section.
903.2 Where Required
Approved automatic sprinkler systems in new buildings and structures shall be provided in the locations described in Sections 903.2.1 through 903.2.12.
903.2.9 Group S-1
An automatic sprinkler system shall be provided throughout all buildings containing a Group S-1 occupancy where one of the following conditions exists:
1. A Group S-1 fire area exceeds 12,000 square feet (1115 m2).
2. A Group S-1 fire area is located more than three stories above grade plane.
3. The combined area of all Group S-1 fire areas on all floors, including any mezzanines, exceeds 24,000 square feet (2230 m2).
4. A Group S-1 fire area used for the storage of commercial motor vehicles where the fire area exceeds 5,000 square feet (464 m2).

2021 IBC
Chapter 32 High-Piled Combustible Storage
Section 3201 General
Section 3202 Definitions
Section 3203 Commodity Classification
Section 3204 Designation of High-Piled Storage Areas
Section 3205 Housekeeping and Maintenance
Section 3206 General Fire Protection and Life Safety Features
Section 3207 Solid-Piled and Shelf Storage
Section 3208 Rack Storage
Section 3209 Automated Storage

Reply
Jesse
2/13/2023 09:49:58 am

I'm curious to know commodity to be stored and roof pitch.

Reply
Jay
2/13/2023 10:26:48 am

If the roof pitch is greater than 2/12 then you can't use the high piled storage chapters of NFPA 13.

Reply
Franck
2/13/2023 02:39:51 pm

One solution, if you can find a sprinkler design solution for 35 ft stge in 45 ft bldg, is to consider a 35 ft high storage to design your sprinkler density at 45 ft.
This would be acceptable per NFPA.
It is the same, if you have 10 ft stge in 30 ft building, design as for 20 ft stge in 30 ft building.

Another solution, out of the scope of NFPA is to provide in-rack with one last level at the top tier.
It is out of the scope of any standard and need to be accepted by the AHJ, but is a solution to provide confidence on fire control.

But if your slope at ceiling is more than 17% (2:12), then no solution… out of the scope of NFPA 13 for storage and definitely not suitable for ESFR.
You can still try to convince the AHJ with a top tier level of IRAS as for high clearance, but I won’t personally accept it as it is a non-approved and not-tested solution…
Could be acceptable with saw-tooth roof, but not for peak roof.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT