What is the recommended practice to protect Battery Energy Storage Systems (BESS)?
NFPA 855 states that if the BESS is not a walk-in unit, then fire suppression is not required. How do you define a "walk-in unit"? If any suppression is not required in side the unit, is there any requirement for systems protecting the outside? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Pete H
8/16/2023 06:45:49 am
From NFPA 855 (2023):
Reply
chad putney
8/16/2023 08:16:00 am
IMO--- Aspirating smoke detection (not vesda specifically) is best to catch it and then inerting agent like nitrogen. Siemens has a good product line for both.
Reply
Chad
8/16/2023 08:21:11 am
.....If we are specifically talking about Li-Ion
Reply
Kris K.
8/16/2023 08:22:39 am
First off make sure you're looking at the 2023 version of NFPA 855 - the 2019 version was a terribly written code.
Reply
Dan Wilder
8/16/2023 08:24:40 am
Pete got the first half.
Reply