How to Approach Heat Loss for Sprinkler Pipe?

10/14/2020

6 Comments

 
NFPA 13 states the following:

8.16.4.1.5 Water-filled piping shall be permitted to be installed in areas where the temperature is less than 40 deg F when heat loss calculations performed by a professional engineer verify that the system will not freeze.

For some reason I had always thought that Tyco or some other heat trace provider had a program available to perform these calculations. I feel there is a better way than breaking out my old heat transfer book. Our general consensus is that the risk is relatively high with these types of calculations.

I’m sure you been tasked with this before; what is the best approach to going about these calculations?

Some owners require these calculations to be performed to avoid dry-pipe systems in Florida, even though the location of the iso-thermal line would require dry-pipe systems - I feel this essentially puts all the liability on the engineer.

I'd be curious to see how others would normally approach this. In this case we would look to run calculations to justify that a wet-pipe system would be sufficient without any insulation or heat trace. Thanks in advance.

​​​​​​​​​​​​​​​​​​​Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
6 Comments
FIREPE25
10/14/2020 10:15:56 am

Do not put in a space that would be subject to freezing. If there are concerns install a dry system. Working in New England anything that is outside the heated envelope is assumed to have freeze issues.

Reply
Nolan Baker
10/14/2020 10:21:34 am

1. Determine R-Values of wall, door, ceiling, etc.
2. Assumed temperature of occupied spaces.
3. Perform heat gain calculation: Q=U x A x TD (wall)
4. Perform #3 calculation for wall.
5. Perform #3 calculation for door.
6. Perform #3 calculation for ceiling/roof
7. Determine Qtotal. If Qtotal is a positive number (gain) in BTUH, then the area will maintain a minimum of 40F.

Reply
Brian Gerdwagen FPE
10/14/2020 10:24:18 am

Get with your Mechanical Engineer, if you have one on the project. Look for the 99.6% Low temperature and use that as a guide. If the piping is installed in an unheated attic and the 99.6% is 39.9F, you are probably fine.

If you are putting things outside, you probably need to look at the age of other items on the exterior of other buildings. In Los Angeles, we never balked at putting risers on the outside of a building as long as they were tamper resistant. In Florida, you need to be aware of the area. If the only devices you see are new, they either haven't frozen yet, or were replaced after a freeze. If you see aboveground exterior piping with old FDC's and OS&Y's, you are also probably fine.

Reply
Felipe Pedraza
10/14/2020 11:51:44 am

This is a very fine line that we are looking into here in deep South Texas with little to no freezing periods that may occur in the year. After dealing with the different code requirement's for 10 years in he prevention office and understand the important and heard jobs that the engineers have in determining the correct numbers for everything that gets done. We also understand the price difference from a wet and dry system and depending on size and number of system it can make a big difference on the price. Perhaps the biggest issue that I see right now is:
1. Where is this system to be installed?
2. How long will the temperature be below 40 degrees which eventually lowers the water temperature in a pipe and will lead to freezing sooner, such as having the system in open loading dock?
4. If it is in cold storage facility, does the facility have the capabilities to bring the temperature below or close to freezing?
5. Will a system be install in an attic if so, what type of heat trace will be used and also the type of insulation?
6. Will the system be up-rights or pendant's?

These area some of the question I would ask the designers and especially the owner. I know what NFPA 13 says on the matter and this are only minimum requirements. Do talk to the local AHJ as well since they may require a dry system to be install.

Reply
David Castillo
10/14/2020 04:14:36 pm

I would suggest getting with a Mechanical (HVAC) Engineer to have the analysis done. A good HVAC engineer will use ASHRAE data files and a good heat loss/gain program that will do an hourly analysis to determine if freeze protection is required.

Reply
Mia Evans link
3/1/2022 06:01:24 pm

Thanks for helping me understand that the right calculations are needed by owners to ensure that they get the best out of the process. I can imagine how important that would be when looking for mechanical insulation for sale for your property. It would definitely give you the assurance that they will work well and protect your property's equipment and all over the years.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT