How to Address Warehouse with Boats on Racks?

1/25/2024

12 Comments

 
Does anyone have experience in designing suppression for a warehouse that will store boats on racks?

I will appreciate any information. 

Which standard would even be applicable? Do we treat them like high-piled combustible storage per Chapter 32 of the IFC?

What will be target hazard considering the fuel in the boat? Is there any limitation that how much they can keep inside the boat?  

Thanks for the input on this; I'm having a hard time on where to get started.

Editor's Note: A Fire Protection Research Foundation on Marina and Boatyard Indoor Rack Storage Sprinkler Protection has been submitted and can be viewed here: PDF LINK

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments
Dan Wilder
1/25/2024 07:25:06 am

Not addressed within NFPA 13 directly and should really be handled via an FPE for Design Criteria creation and/or alternates. Also, getting the insurance provider involved will be very helpful.

FPRF Report from 2008 - https://nfpa.access.preservica.com/uncategorized/IO_734d0846-227e-4cbf-b41d-67a91a155e2b/

NFPA 303 - 21' Section 6.2.4 - Annex indicates the design density should be with Group A plastics stored on solid shelves per Ch. 17 of NFPA 13 and sprinkler type & layout should be of "Sound Engineering Judgement"

6.2.4.1* Where boats are stored on multilevel racks in buildings, an approved automatic fire-extinguishing system shall be installed throughout the building unless otherwise permitted by 6.2.4.2 or 6.2.4.3.

You will likely need a standpipe system as well.

Reply
Pete H
1/25/2024 07:29:47 am

A standpipe system is likely required as per NFPA 303 (2016) 6.3 and 6.4.

https://www.meyerfire.com/daily/design-criteria-for-stacked-boat-storage-facility

A previous thread on the subject.

Reply
Glenn Berger
1/25/2024 08:15:56 am

Utilizing statements made in the question:

Rack storage - Start with NFPA 13 Storage Sections. Storage arrangement potential will need to be defined.

I would assume, but needs verification, that the boats are de-fueled. If not, seek additional guidance from NFPA 30.

Follow-on by what are the applicable potential construction and finishing types. Group A Plastics may be a very good fit.

Reply
Todd E Wyatt
1/25/2024 08:40:32 am

The Occupancy Classification (OC) determines the requirements for the automatic sprinkler system (ASPS). The storage of “boats” would be classified as a Group S-1 Moderate-Hazard Storage.

Per the scoping Code (e.g. 2021-IBC), an ASPS is required in Group S-1 if it meets (1) of the (4) conditions per 903.2.9 (see REFERENCES below). If required (or provided), the ASPS is required to meet NFPA 13-2019.

High-pile stock or rack storage of “combustible storage” in any OC shall comply with IFC-2021. Depending on the materials in the boats, they may or may not meet the Code’s definition of “combustible.” Fiberglass, for instance, is non-combustible and will not burn. It has been designed to withstand up to 1000°F or 540°C, and even if it reaches this temperature, it will at the maximum melt away.

If it is determined that the boats are considered “combustible”, the IFC-2021 for high-pile stock or rack storage shall be met per Chapter 32 High-Piled Combustible Storage as well as Chapter 3 General Requirements.

REFERENCES
IBC-2021

Chapter 3 Occupancy Classification and Use
311.2 Moderate-Hazard Storage, Group S-1
Storage Group S-1 occupancies are buildings occupied for storage uses that are not classified as Group S-2, including, but not limited to, storage of the following:
Dry boat storage (indoor)

Chapter 9 Fire Protection and Life Safety Systems
Section 903 Automatic Sprinkler Systems
903.2 Where Required
903.2.9 Group S-1
An automatic sprinkler system shall be provided throughout all buildings containing a Group S-1 occupancy where one of the following conditions exists:
1. A Group S-1 fire area exceeds 12,000 square feet (1115 m2).
2. A Group S-1 fire area is located more than three stories above grade plane.
3. The combined area of all Group S-1 fire areas on all floors, including any mezzanines, exceeds 24,000 square feet (2230 m2).
4. A Group S-1 fire area used for the storage of commercial motor vehicles where the fire area exceeds 5,000 square feet (464 m2).

Chapter 4 Special Detailed Requirements Based on Occupancy and Use
Section 413 Combustible Storage
413.1 General
High-piled stock or rack storage in any occupancy group shall comply with the International Fire Code.

IFC-2021
Chapter 3 General Requirements
User note:
About this chapter: Chapter 3 provides general requirements for asphalt kettles, combustible waste material, ignition sources, motion picture projection rooms and film, open burning, recreational fires, portable outdoor fireplaces, open flames, powered industrial trucks and equipment, smoking, vacant premises, vehicle impact protection, fueled equipment, indoor displays, general storage, outdoor pallet storage, hazards to fire fighters, landscaped roofs, laundry carts, mobile food preparation vehicles, additive manufacturing (3D printing) and artificial combustible vegetation. These are intended to improve premises safety for everyone, including construction workers, tenants, operations and maintenance personnel, and emergency response personnel.
Chapter 32 High-Piled Combustible Storage
User note:
About this chapter: Chapter 32 provides guidance for reasonable protection of life from hazards associated with the storage of combustible materials in closely packed piles or on pallets, in racks or on shelves where the top of storage is greater than 12 feet in height, or 6 feet for high-hazard commodities. It provides requirements for identifying various classes of commodities; and general fire and life safety features including storage arrangements, smoke and heat venting, fire department access and housekeeping and maintenance. This chapter attempts to define the potential fire severity and, in turn, determine fire and life safety protection measures needed to control and in some cases suppress a potential fire. This chapter does not cover miscellaneous combustible material storage as regulated in Section 315.

Reply
Todd E Wyatt
1/25/2024 08:46:46 am

See also "Design Criteria for Stacked Boat Storage Facility?" ... https://www.meyerfire.com/daily/design-criteria-for-stacked-boat-storage-facility

Reply
DAvid T Williams, FPE
1/25/2024 09:55:42 am

Whew... I think about all that I have learned since 2005, when we completed my one and only heated rack storage boat building (maybe four tiers high). I remember one of the main issues with the State of WI was whether a boat was a motorized vehicle that needed garage ventilation (whether fueled or not). I couldn't find my records on what I did for design, although they recently replaced the boilers. At that point we didn't have that much guidance on what to install for fire protection, so I think it was just a OH2 design. Now... what did the contractor provide? it was definitely reviewed by WI Code folks (Madison so they were tough).

Jesse
1/25/2024 12:40:58 pm

I'll reiterate the importance of involving the insurer. They'll likely assign one of their HPR loss control folks to it.

Reply
Dwight Havens
1/25/2024 02:24:50 pm

Unfortunately we have burned enough of these facilities to know they do burn. We also don't appear to have the advantage of having had fires in protected facilities, with known protection levels, which have successfully controlled. If we could find examples of facilities that were protected, but burned to the ground, or, facilities that we protected, and had a fire with successful control, we might learn something. At this point NFPA 303, an experienced FPE, and the Insurer would be your best bet.

Reply
Safety
1/25/2024 04:11:12 pm

Keep in mind when designing boat storage racks.
Fire sprinklers and hose streams fill boats up with water quickly adding weight that most engineers may not include in design.
A 3/4" drain hole (typical) or bilge pump not going to do much.

Have a loaded rack of boats collapse during suppression is not going to be a friendly conversation in review.

Reply
Dwight Havens
1/25/2024 04:41:03 pm

Excellent point. All Incident Commanders be trained to recognize this.

Reply
Joe Meyer
1/26/2024 07:25:04 am

Thankful for a contributor who emailed a copy of a 2008 Fire Protection Research Foundation Study on "Marina and Boatyard Indoor Rack Storage Sprinkler Protection".

I've posted a link to this report in the "Editor's Note" with a link right below the question on this page.

Reply
Krauss Maffei Sacro Mateo link
9/2/2026 08:55:24 am

Boat storage seems simple until you start thinking about fuel, rack height, sprinklers and all the extra weight during a fire. Working around marinas and boatyards, you really see how many small safety details have to come together.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT