MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

How Often Are FDCs Used in a Fire?

7/6/2021

12 Comments

 
Can someone tell about how often are Fire Department Connections ever used in a real fire?

We all install FDCs but in the real world how much do Fire Departments use them?

​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments
Danial Bartle
7/6/2021 08:26:23 am

I spent 30 years in the Fire Service. For most departments, standard operating procedure is to connect to the FDC with the first or second due engine automatically, especially if there is smoke showing. They will set the pump at 150 psi because that is the pressure for the greatest flow rating of the pump.

Reply
MattC
7/6/2021 08:37:33 am

I work for an FD in Ontario, Canada - I can confirm that if there are apparent fire conditions (smoke showing, for example) the suppression staff will hook up 100% of the time. That is the typical standard operating procedure for most departments in my area, as Danial noted above.

Reply
Jon
7/6/2021 08:49:52 am

All the time. The SOPs are to at the very least hook up engine to the FDC and if theres no fire then they wont pump. But if theres a confirmed fire or the interior team charges their hoseline then the engine charges the system.

Reply
Jesse
7/6/2021 08:51:01 am

I was a career fire officer for nearly 20 years.

Every single fire. Working fire in a protected building gets FDC is connected every single time.

Reply
Glenn Berger
7/6/2021 09:16:56 am

SOP, Connect to the FDC first.

Reply
Bruce P.
7/6/2021 11:00:10 am

I am a Deputy Chief who has worked both operations and prevention.
We connect to the FDC on every fire. The first pumper responds to the alarm panel the second Engine responds to the FDC and makes the connection prepares to charge the system.

Reply
Franck
7/6/2021 11:14:41 am

The answer would be quite different in Europe, with a result very close to 0.
In France, for example, most FD think that a FDC is used to take water from the fire protection system to supply the fire trucks/hoses (not joking…).
Installation of FDC is not required by European standards, so only found at private industrial facilities insured by FM Global or companies using NFPA as the installation standard.
But, as there are more and more, and education is becoming better (so that firefighters do not consider sprinklers as a competitor to stop as soon as they arrive on site), we do hope that one day we will achieve the level of common sense you have in the US.
It is good to see that the answer from the professionals above is unanimously « of course this is the first connection we do with one of the first fire trucks ».
Indeed a good practice.
But you would also be surprised to see that governmental and public buildings have no sprinklers in Europe (including schools, museums, hospitals, retirement homes, hotels… quite scary, isn’t it ?)

Reply
Phil W
7/7/2021 02:23:12 am

Great answer (from a fellow European).
I do sometimes wonder how (in practical terms) pumping in by the FD actually helps for a system will stored water supplies (tank and pumps)?
I can understand the need to prolong a sprinkler system discharge in the event of loss of water supplies, but if the system has a particularly high flow (and pressure demand) would an FD pump be able to deliver what is required?

Reply
Roy Mares
7/15/2021 06:10:35 pm

Working with the fire service entities in my area, their mindset when responding to an incident is to use their equipment first. They feel they know the readiness and condition of their equipment when it comes to putting their life on the line with it so even if the facility has a pump and water storage, they prefer to hook up and take over the supply. Same mindset with in facility hose reels/racks. They will not use them and bring in their own hose packs to connect to required hose connections throughout the facility. FDC has a sign with pressure and flow required for the max delivery of the building system.

Chad
7/6/2021 11:25:44 am

Its not used every time the building fire alarm goes off but, as the others have stated, there is a fire engine, in place, ready to hook up to it at almost all type of alarms for the structure. And if there is any fire, an engine pumps until they are ordered to disconnect. even if its just a single head operating, with fire present, its getting pumped.

The reality is the majority of FDCs never get used but, when there is fire, they all get used.

Reply
Matthew Mueller
7/6/2021 11:55:08 am

Every. Single. Time. In 15 years in the Fire Service, SOP was second due engine connected to the FDC on every automatic alarm. Charge to 100 psi upon orders of first in unit, or command.

Reply
Mike Patti link
7/6/2021 12:00:34 pm

The FDC is there to supply the fire protection system in the event of fire. When the first-due engine arrives and fire is showing, or multiple reports enroute confirms a fire, that apparatus will connect to the FDC EVERY TIME.
( It doesn't exist just for show)

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT