|
When doing a Forward Flow on a Sprinkler System what is the Minimum # that Fire Marshals are looking for?
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Pete H
3/20/2024 06:40:18 am
From NFPA 13 (2016 edition):
Reply
Bruce Seiler
3/20/2024 09:18:57 am
The minimum flow rate should be the highest demand for the sprinkler system including any inside hose allowance. Outside hose allowance does not need to be considered for the forward flow test since it wouldn't be required to flow through the backflow. So, if you had a light hazard occupancy with calculations with design criteria of 0.10/1500, your demand would be (minimum) 250 gpm including the 100 gpm outside hose. You would be required to flow a minimum 150 gpm for the forward flow test. One thing to note, NFPA does not require the residual pressure be documented, however we document this number to ensure the actual system demand is being met. We had two cases where the flow rate was met, but the residual pressure was a lot lower than anticipated due to a valve that was not fully open. This problem could also be shown during a 2-inch drain test, but not always due to a lower flow rate. Again, not a requirement, but another good way to ensure the water supply is as expected.
Reply
Jack G
3/20/2024 10:11:34 am
Off the top of my head :
Reply
Jeff
3/20/2024 10:31:52 am
2020 NFPA 25 - 13.7.2.1
Reply
Brandon
3/20/2024 03:08:20 pm
NFPA 25 2017 edition.
Glenn Berger
3/20/2024 10:44:56 am
The purpose of the forward flow test is to measure the pressure loss in the system of the backflow prevention assembly. The minimum flow rate required is the calculated sprinkler flow for the system(s) being protected.
Reply
Randy Kimbro
3/20/2024 11:29:59 am
Hi Glenn, as an AHJ I respectfully disagree. The forward flow is not to measure pressure loss. It is designed for two criteria. First, to exercise the backflow preventor to ensure it opens fully. And second to measure the riser flow rate (pitot reading) to ensure it meets or exceeds the required GPM as documented on the riser hydraulic tag. Those annual tests are extremely valuable for the fire department to have confidence that the sprinkler system will discharge water as designed in case of a fire.
Reply
Dan Wilder
3/20/2024 11:50:55 am
It's to exercise the valve components to the working flow conditions expected. There is no requirement to record pressures for this specific activity within NFPA 25. Good practice to record a residual pressure, sure, as it provides good data year to year for possible water supply investigation substantiation.
Reply
Dan Wilder
3/20/2024 11:59:24 am
Specifically for 25, just meeting the flow rate as noted by others.
Reply
Jesse
3/20/2024 01:27:35 pm
Lotta good answers here but I want to reiterate what Dan said. The difference between 2016 and earlier versions of NFPA 13 will look different than those governed by 2019 and 2022
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop Oct '25 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
November 2025
PE PREP SERIES |
RSS Feed
