We have a project with exposed sprinklers and pipe in a washdown area that is for full sterilization with 100+ degree water.
What are the best practices used to prevent accidental sprinkler from the hot washdown water, if any? We also have a space with waterproof (sealed) walls and ceilings using pendents and sidewalls - any tips on good practices for a room like this? On the fire alarm side, we've found plastic cover/guards that will provide a reasonable level of protection from the washdown. I appreciate any design suggestions, thanks. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Alex
11/23/2021 06:40:21 am
Hi,
Reply
Rusty Scott
11/23/2021 09:17:28 am
100 degree Fahrenheit water, potentially up to 130 degree Fahrenheit water max
Reply
Glenn Berger
11/23/2021 08:18:24 am
My recommendation would be to install 200F sprinklers.
Reply
Rusty Scott
11/23/2021 09:18:18 am
guards are for notification devices not detection devices
Reply
Shane
11/23/2021 08:33:14 am
Not to be over technical with this situation and adding extra work and cost. Would just using the 3mm cellophane baggies we use for spray paint booths be sufficient. The air temp should remain safe for the sprinkler link and protect the sprinkler from corrosion. Also, it was mentioned the system is exposed so there are no existing escutcheons for the plastic cover to attach to, right?
Reply
Dan Wilder
11/23/2021 08:33:26 am
Couple of items to note:
Reply
Jesse
11/23/2021 08:41:04 am
I've seen and protected various iterations of hot wash rooms, and have seen multiple configurations. So not really sure how yours is presented.
Reply