MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Hanging Directly from Metal Deck under NFPA 13?

10/9/2019

7 Comments

 
NFPA 13 (2016 Edition) Section 9.2.1.4.1 states:

9.2.1.4.1 Branch line hangers attached to metal deck shall be permitted only for the support of pipe 1 inch of smaller in size, by drilling or punching the vertical portion of the metal deck and using through bolts.

The Sammy X-Press has listed hangers that call out attachment directly to metal deck for pipe up through 4" in some cases. 

From a code perspective, does the section above not apply, or would this be a code approved alternative? Just looking for the code logic that would allow use of listed special materials where the section above wouldn't trump this method.

Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
7 Comments
Wayne Ammons
10/9/2019 08:39:22 am

Products specifically LISTED for use on fire sprinkler systems are allowed by NFPA 13. Below is commentary from the 2016 edition of the NFPA 13 Handbook on this particular subject:

9.2.1.4 Metal Deck
The NFPA allowance for attachment to decking material applies only to very small diameter pipe using through-bolts. With the exception of 9.2.1.4 and that for toggle hangers in 9.2.1.1.2, hanger attachment must be made to the building structure.
Hanger manufacturers have created specialty products with listings to attach to steel deck of varying gauge. It is acceptable to use these listed products, but consideration must be given to more than just the steel to which the fastener is attached. While locally the fastener might be in compliance with the minimum deck gauge requirements of the hanger manufacturer, the deck itself must still meet the requirements of 9.2.1.3.1. For example, a ceiling flange with a specific listing is to be screwed to steel metal deck as thin as 22 gauge. While connection of the ceiling flange to the 22 gauge deck might be fine, the steel deck’s span must also be checked to see if it meets the requirements of 9.2.1.3.1 for the building. It is one thing to determine that the ceiling flange not to pull out the deck, but it is another thing to see if the deck will support the water-filled pipe plus 250 lb (115 kg) as it spans between supports.


Keep in mind, commentary from the handbook is not part of the standard itself. You might also refer to the equivalency statement at the beginning of NFPA 13 to support the use of listed products not directly covered by the standard:

1.5 Equivalency
Nothing in this standard is intended to prevent the use of systems, methods, or devices of equivalent or superior quality, strength, fire resistance, effectiveness, durability, and safety over those prescribed by this standard.



Reply
Skyler
10/9/2019 12:03:38 pm

The commentary hits it on the head. It all depends on the thickness of the deck, but NFPA 13 basically says that for 1" it doesn't matter. Composite metal decks typically range from 16 to 22 gauge, with 18 and 20 being the most typical. Metal roofs on a pre-engineered purlin structure tend to be 22 or 24 gauge. Purlin thicknesses can range wildly, but they are one of the best use cases for the Sammys you referred to.

The Sammy you referred to is FM Approved for up to 2" in 22 gauge or thicker (very common), but up to 4" requires at least 12 gauge (not very common in the wild). In any case, it is important to pay attention to that listing information on the Sammy.

It's all about the metal thickness you are attaching to.

Reply
J. Wilson
10/9/2019 10:26:49 am

The point is that if it listed by manufacturer it is acceptable. Follow all manufacturer instruction your good.

Reply
Skyler
10/9/2019 12:11:21 pm

Just noticed the actual question you posed. I would refer you to the section in the beginning of the hanging chapter (9.1.1.2) that allows an Engineer to use alternative hanging methods and lists the criteria. This is very useful for non typical situations. Since you are an Engineer, I would say you can use this section to justify the use of the Sammys you referred to (just pay close attention to the metal thickness you are attaching to).

Reply
Wayne Ammons
10/9/2019 01:57:01 pm

Skyler,

Wouldn't section 9.1.1.2 (below for others reference) refer to a hanging method or device that is not already listed or approved by a nationally recognized testing agency, i.e. UL or FM? For example, a fabricated bracket to support pipe along a wall.

9.1.1.2
Hangers certified by a registered professional engineer to include all of the following shall be an acceptable alternative to the requirements of Section 9.1:
(1) Hangers shall be designed to support five times the weight of the water-filled pipe plus 250 lb (115 kg) at each point of piping support.
(2) These points of support shall be adequate to support the system.
(3) The spacing between hangers shall not exceed the value given for the type of pipe as indicated in Table 9.2.2.1(a) or Table 9.2.2.1(b).
(4) Hanger components shall be ferrous.
(5) Detailed calculations shall be submitted, when required by the reviewing authority, showing stresses developed in hangers, piping, and fittings, and safety factors allowed.

Reply
On the Clock
10/9/2019 03:34:28 pm

I agree 100% with Wayne's comments above. Note that the building structure also must be capable of supporting the load as described in NFPA #13 (2016) 9.2.1.3.1. When they first came out (and before I knew better), I was guilty of overly-liberal use of Sammy XP's. I offer this as a caution, on my projects, the structural engineer-of-record routinely prohibits, or greatly limits hanging directly to the metal deck, regardless of the gauge of the deck. And it can vary project-to-project.

Reply
Wayne Ammons
10/9/2019 04:16:39 pm

Excellent point. Whenever we (my company) wish to hang directly to the metal decking, we always get approval from the structural engineer or GC, regardless of what we know about the steel gauge.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT