MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Foam/Water Deluge System with Less Than K5.6?

3/23/2020

4 Comments

 
I have an existing foam/water deluge system covering vessels and sprinklers providing area coverage for pool fires. The sprinklers are smaller than K-5.6. The owner wants us to match the existing sprinklers. 

In your opinion, is this acceptable?

For reference, NFPA 13 (2013) Section 8.3.4:
8.3.4 Sprinklers with K-Factors Less than K-5.6 (80).
8.3.4.1 Sprinklers shall have a minimum nominal K-factor of 5.6 (80) unless otherwise permitted by 8.3.4...
8.3.4.2 For light hazard occupancies not requiring as much water as is discharged by a sprinkler with a nominal K-factor of K-5.6 (80) operating at 7 psi (0.5 bar), sprinklers having a smaller orifice shall be permitted, subject to the following restrictions:
(1) The system shall be hydraulically calculated.
(2) Sprinklers with nominal K-factors of less than K-5.6 (80) shall be installed only in wet pipe sprinkler systems or in
accordance with the limitations of 8.3.4.3 or 8.3.4.4.
(3) A listed strainer shall be provided on the supply side of sprinklers with nominal K-factors of less than K-2.8 (40).
8.3.4.3 Sprinklers with nominal K-factors of less than K-5.6 (80) shall be permitted to be installed in conformance with 11.3.2 for protection against exposure fires.
8.3.4.4 Sprinklers with nominal K-factors of K-4.2 (57) shall be permitted to be installed on dry pipe and preaction systems protecting light hazard occupancies where piping is corrosion resistant or internally galvanized.


NFPA 15 (2017) Section 7.3.3. Flammable and Combustible Liquid Pool Fires
Water spray systems designed to control pool fires resulting from a flammable or combustible liquid spill fire shall be designed to apply a net rate of not less than 0.30 gpm/sqft of protected area.


I think my new design will require nozzles spaced at 100 square feet if the k-factor needs to be smaller than k-5.6 under NFPA 13.

Also, do you know of any non-aspirating nozzles that are listed for foam?

​​​​​​​​​​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
4 Comments
RyanO link
3/23/2020 10:31:24 am

What are you adding protection to, specifically (area deluge w/ SSU, spray protection using directional nozzles, etc)?

Reply
Dan Wilder
3/23/2020 10:48:03 am

You need to confirm that the sprinkler is listed with the existing foam. If it is, then matching existing for change out should not be an issue.

If you are adding to the system I would think your foam supply may take a hit and you would need to adjust accordingly.

Reply
Ryan Hinson
3/23/2020 11:21:38 am

What were the applicable standards used for the initial design? NFPA 11 governs foam systems and NFPA 16 governs foam-water spray systems. NFPA 16 requires adherence to NFPA 15 unless otherwise specified. NFPA 16 does not require strainers in upstream FW piping. NFPA 15 (2017) does...under certain conditions:
- if the free-passage through the discharge is less than 3/8" per Section 6.4.6.1
- where the water is likely to contain obstructive material per Section 6.4.6.1
- intrinsic strainers at the nozzles are required if the free-passage is less than 3/16" per Section 6.4.6.3 (it must be noted that many petrochemical entities outright do not allow these types of nozzles since they are prone to plugging)
- Where strainers are required above, they must be able to remove solids of sufficient size to plug nozzles(normally, 1/8" is sufficient but must be verified where small K-factor nozzles are being used)

Is there already a strainer in the upstream piping? Does replacement of existing components with like K-factor nozzles require the addition of a strainer that was not there before?

Keep in mind that the hydraulics of a foam-water deluge system must be balanced to between 100% and a maximum 120% variation from specified discharge rate of the nozzle in accordance with NFPA 16 (2019) Section 7.10.1.1.1.

A standard sprinkler is an example of a non-aspirating nozzle per NFPA 16 Section 6.2.2. NFPA 11 (2016) Section 3.3.3.3 defines a non-air-aspirating discharge device as a device designed to provide a specific water discharge pattern...like a sprinkler. These are explicitly allowed to be used with foam deluge systems and are actually REQUIRED on wet-, dry pipe-, and preaction systems per NFPA 16 Section 6.2.3.

While the manufacturers I have discussed listings with have indicated that foam use in their nozzles does not affect the individual UL/FM listing/approval of the sprinkler, individual listings are not enough and the foam has very specific listing requirements and limitations regarding the 'listed system' per NFPA 16 Section 6.2.1 which includes discharge devices and proportioning equipment. This may include specific application densities dependent upon the specific hazard. I have found that many foam manufacturers also manufacture sprinklers/nozzles and may only list their foam with their nozzles. Consultation with both the foam- and discharge device manufacturers is highly recommended. Per one of the manufacturer's Listing and Approvals data sheet, refer to the UL listing guide or FM approval guide for the most current listing information as well as historic product listings.

Good luck.

Reply
Mike
3/23/2020 12:44:22 pm

NFPA® 16

Standard for
the Installation of
Foam-Water Sprinkler and
Foam-Water Spray Systems

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT