|
Have a paddle flow switch for a wet system that is located on the first story riser. The riser serves the entire 3-story building.
When flowing an inspector's test on the first floor or even the third floor, the flow switch paddle only stays engaged for 10-12 seconds before cycling back and forth. Without keeping the engaged position, the alarm won't activate. Has anyone come across this before? What remedies could help the flow switch operate properly? Posted anonymously by a member for discussion. Discuss this | Subscribe
13 Comments
Bob Jeske
1/22/2019 10:14:58 am
I have seen this occur with backflow preventers installed back in the 1990's. The issue was that the backflow preventer's checks had too stiff springs installed on the backflow preventer. The manufacturer of the backflow sent us new check valves with softer springs in order for the flow switch to not cycle.
Reply
PETE
1/22/2019 11:18:13 am
Is there a pump with a pressure reducing valve on the discharge that is feeding this wet system?
Reply
JOE
1/22/2019 11:23:39 am
Nope, I was told it's just a city feed wet system.
Reply
PETE
1/22/2019 11:29:02 am
Here is what I am thinking. It ma be useful to read the Principles of Operation section on this cut sheet. https://www.systemsensor.com/en-us/Documents/WFD_Series_Manual_I56-0459.pdf
Reply
PETE
1/22/2019 11:31:17 am
With no pump, it sounds like a partially closed valve on the system is causing friction loss. A damaged valve stem will do the same thing.
Kent Wise
1/22/2019 11:54:33 am
What you are experiencing is caused by too much trapped air in your system. When you flow an inspectors test the pressure drops low enough for the clapper to open on the alarm valve. Once the clapper opens a column of water the diameter of your main riser pipe starts to flow up into the riser. The mass in motion of the water column causes it to compress the air in your riser. That compression pressure eventually exceeds the city water pressure causing the clapper to be forced closed. The pressure has to drop below the city water pressure by additional flow out the inspectors test till the whole process starts over again.
Reply
Mike
1/22/2019 12:42:03 pm
These are all great comments and I have learned some valuable insights.
Reply
Doug
1/22/2019 07:52:02 pm
I would generally recommend the same thing except he stated the paddle only stayed down for about 12 seconds.
Reply
Doug Funk
1/22/2019 05:19:59 pm
Back in the mid to late 90's we had a similar problem on many systems. Mainly it was the Ames 2000 backflow preventers. The spring on one of the checks was to stiff. The paddle on the flow switch would cycle exactly like you described.
Reply
James Armentor
1/24/2019 06:56:28 am
I've run into this same issue. I ended up loosening the tension on the return spring to get the switch to work. There is a small flat head screw at the top of the switch that holds the spring.
Reply
PETE
1/24/2019 08:29:25 am
Bear in mind that modifying the switch in a way that is inconsistent with the O&M sheet will void the listing. If the switch you're using doesn't describe this procedure and you are going to do it anyway, you might consider using Locktite or super glue on the screw threads so it doesn't fall out completely.
Reply
This issue is NOT caused by air trapped in the system!
Reply
Simon Tinaj
4/17/2025 09:33:31 pm
I have fire sprinkler system the waterflow detecter is keeping the solenoid valve energized (closed position).
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop Sept '26 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
October 2026
PE PREP SERIES |
RSS Feed
