Floor Control Valves Required in Small NFPA 13R?

8/26/2020

10 Comments

 
We are working on an 8-unit, 4-story apartment building in the City of Chicago. It's an NFPA 13R system, with two units on each floor level. The entire building (all floor levels combined) is about 14,000 sqft.

Are floor-level control valves required?

Under NFPA 13R there doesn't appear to be a requirement for floor-level control valves like there is in an NFPA 13 system (NFPA 13-2016 8.2.4.3). Even still, in NFPA 13 still allows a single control valve and flow switch when the entire building is less than the system limits of 8.2.1 (52,000 sqft for a Light Hazard system). 

Chicago has a Chicago Fire Prevention Code that requires "each floor and level of a building" with a separate control valve (15-16-400), but this and several other sections within the Fire Prevention Code apply only to NFPA 13 systems, not 13R systems.

Might be a shot in the dark but was curious if anyone has ran into this before. Thanks in advance.

​​​​​​​​​​​​​​Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
10 Comments
Justin Harrison link
8/26/2020 10:08:46 am

I actually just ran into this very same situation and Napa Fire department made us put floor controls. Seems that we should be able to use one riser as you mentioned since it was also a 13R system. Would love to get some more feedback on this if anyone can weigh in.

Reply
Mike
8/26/2020 10:21:52 am

I agree with the AHJ. They are over 3 stories which sometimes is too high for fire department apparatus access for exterior access.

Do you really want to drain the whole building and take all the systems out of service just to change a head or fix a leak?

IMO this idea is just being cheap and cutting corners just to save a few bucks, especially if you already know the requirements.

Reply
Anon
8/26/2020 10:24:25 am

Can you provide the code section from NFPA-13R that requires the FCVA?

Reply
SUBMITTER
8/26/2020 10:34:21 am

If it is trying to avoid something that is code required, yes I'd see it as cutting corners. If it's not code required though, is a contractor expected to bid and provide something the owner doesn't want to pay for?

Four floor-control valve assemblies adds at least $3500 in material, plus a dedicated drain riser, plus the riser now can't be routed within chases or within units (an 13R requirement) - they need to be in common areas (like stairs) where it either needs access panels or is run exposed which the owner is going to have a tough time with.

It seems easy enough to do, but the implications start to become costly in material and labor, plus the owner is losing a high-end finish to the stairs.

As far as drain time, we're only talking about a 120 gallon wet system, total. A 2-inch main drain on a 120 gallons shouldn't take that long to drain.

Reply
M.Newell
8/26/2020 10:39:14 am

If your 4 story building exceeds the 30’ above or below the fire department access and you are putting in a standpipe then you are required to have floor control per NFPA 14 -2019

6.3.5* Control Valves and Check Valves on Combined (Stand‐ pipe/Sprinkler) Systems.
6.3.5.1 Each connection from a standpipe that is part of a combined system to a sprinkler system shall have an individual control valve and check valve.
6.3.5.2 A listed pressure-regulating device that prevents back‐ flow shall be considered a check valve, and an additional check valve shall not be required.

Reply
SUBMITTER
8/26/2020 10:40:42 am

Good point - although not for this project. A standpipe isn't required by the adopted building code so NFPA 14 wouldn't apply.

Reply
IVONN
8/26/2020 10:39:29 am

NFPA 13R Ed.2019 , include a new section.

6.8.8 - In multistory buildings, a control valve per floor shall not be required.

But like you said , Chicago's plan review or Fire Department can ask for that

Reply
Ethan
8/26/2020 11:20:04 am

In the city I work, the individual FCVA requirement comes from a fire alarm requirement that every floor is to be monitored individually when the building is a high rise. (75 feet in NYC). So you you may have to look in the building code, but I would think you would be fine with just an alarm check valve at the incoming service.

Reply
Dat R. Huynh
8/27/2020 07:11:19 am

Here is my 2 cents....I am always provide floor control valve for any buildings (residential and commercial) with more than 2 stories and not counting the mezzanine for the purpose of testing and maintenance. As the system drain and refill will bring fresh oxygen to the system that would increase chance of corrosion inside the pipe. Drain down the entire system in a multi-stories building may also required fire watch too.

Reply
SERCH
2/14/2024 04:23:31 pm

Does anyone know if FCVA is required in both ends of a floor in order to achieve individual monitoring of each floor? in this case the building has two stairwells with vertical sprinkler fire piping and they are supplied by the main in the first floor

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT