MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Floor Control Valves on Each Stair in Highrises?

1/14/2020

12 Comments

 
I have a question that a architect brought up to me.  He is saying that on a highrise (11 stories) it is a fire code requirement to have floor control valves on both stairwells. I cannot find anything that states this in any of the NFPA books. The square foot of each floor is small and is NOT separated into zones.

Does an 11-story high-rise require floor control valves on both stairwells?

​​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
12 Comments
Mike L
1/14/2020 07:54:17 am

Kind of sounds like the architect is confusing some code requirements.

A high-rise building is required to have a floor control valve at every floor. Assuming your systems are smaller than 52,000 sf, then only 1 control is required per floor.

A high-rise is typically required to have a standpipe hose valve in EACH required egress stairwell.

Reply
Mln3d
1/14/2020 09:44:50 am

Unless it is a justificational adopted code requirement. Some AHJ’s require floor controls to alternate that way if you need to drain down the system it doesn’t completely impair the system. i.e. if you only had floor controls on one stand pipe and drained a floor down.

Reply
Thomas Jones
1/14/2020 10:06:51 am

It isn't an FM building or Marriot correct? Marriot has their own fire code that requires a control valve in each stairwell.

Reply
Anon.
1/14/2020 10:32:37 am

Some AHJ's require this. Last I checked, City of Seattle for example has such a redundancy requirement, but in hydraulic calcs, one cannot take advantage of both supplies simultaneously.

Reply
Diaaeldin Mostafa DM
1/14/2020 11:05:05 am

As per NFPA13 , Only one sprinkler riser with floor control valve per 52,000 ft2 . If NFPA 101 is asking for stand pipes so it shall be provided inside firemen stair or smoke stop lobby or fire fighting lobby

Reply
RY
1/14/2020 11:43:49 am

How high is your building? It is not an NFPA requirement. It is in the IBC... in PA we follow IBC 2015 and it is on page 58. 403.3.1 Number of Sprinkler Risers and Systems Design...
"Each sprinkler system zone in buildings that are more than 420 feet in building height shall be supplied by no fewer than two risers. Each riser shall supply sprinklers on alternate floors. If more than two risers are provided for a zone, sprinklers on adjacent floors shall not be supplied from the same riser."
Hope this helps!

Reply
ML
1/14/2020 12:02:49 pm

Yes, heard of this too.

Reply
Thomas Reinhardt
1/14/2020 01:50:28 pm

If you use the International Fire Code Section 903.4.3 states that Approved supervised indicating valves shall be provided at point of connection to the riser on each floor in high-rise buildings.(2012 edition) This reference makes no reference to both stairwells. Mr.Mostafa is correct about square footage.

Reply
Brian Gerdwagen FPE
1/14/2020 03:56:00 pm

As stated, buildings over 420 feet to the highest occupied floor must have two risers. Each of these risers will supply alternate floors and the standpipe valves in the stair. One riser will supply all the even floors, the other all the odd floors. This way if an entire standpipe is shut down, only half the building will be out of service.

You can not add up the area of floors until you hit 52,000sqft and then section those floors off with a control valve. Three story buildings and taller generally require a control valve on every floor.

Reply
Moshe
9/30/2022 07:39:19 am

According to this code will it be a problem if 2 floors in a row are the same ?

Meaning it is alternating but in 1 floor we have an issue so it is the same as below.

Reply
Jess L.
1/15/2020 12:08:04 pm

Check your building code.
It might tell you that each floor must be fed by a minimum of 2 risers, hence 2 flowswitches per floor, depending on the building height or # of floors.

Reply
Eric Tatum
10/29/2024 04:24:37 pm

if multiple 2 1/2" FHV Cabinets on a floor (and the required FHV in the stair) how many should be calculated where there are multiple tenants with one in each space? Also assuming the standard 250 gpm @ 100 psi for each, are these treated like a normal standpipe calculation?

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT