Firestop Needed for Sprinkler Penetration?

1/7/2019

13 Comments

 
Is it necessary to provide a UL firestop for a sprinkler through a fire-rated partition?

I would think that since the penetrating item is a sprinkler that it would not require an actual UL firestop penetration, however I am having trouble finding a code reference to back up my thoughts. My scenario is a sidewall going to through a vertical double layer gypsum partition. 

Posted anonymously by a member for discussion. Discuss this | Subscribe
13 Comments
Edward Glynn link
1/7/2019 10:22:34 am

Yes fire stop is required anytime a penetration is made in a
rated wall and must be equal to the rating of the wall being penetrated.

There firestop manufacturer websites that detail how to fire stop and maintain rating of the wall being penetrated.

In addition, the piping also has a determination on the fire stop being used.

If it is steel piping, any number of firestops may be used.

If it is CPVC piping, you will need to consult with the manufacturer of the CPVC pipe for a listed of approved firestop brands and types listed for use with their particular CPVC piping.

For example, 3M IC15 2 hour rated firestop is listed for use with CPVC pipe but IC25 4 hour rated is NOT listed for use with CPVC piping.

IBC 706.9 requires that all penetrations of fire walls comply with section 714.

There are multiple details contained in Section 714 which will give the specifics of the requirements for the penetration matching your specific project.

Reply
Mike
1/7/2019 10:34:21 am

Edward,

I've never seen this before. I thought there was an exception for fire sprinklers.

I am not sure the listing of the sprinkler would be maintained since the fire stopping would interfere with the escutcheon and that is part of it's listing. Not to mention the clearance required for the installation of caulking.

Reply
James Phifer
1/7/2019 10:46:03 am

NFPA 13, 2016 edition, prohibits the use caulking to seal the penetrations.

6.2.7.4 The use of caulking or glue to seal the penetration or
to affix the components of a recessed escutcheon or concealed
cover plate shall not be permitted.

Reply
Kevin Anderson
1/7/2019 10:30:38 am

I actually posted this question and after doing some more research I found the following from IBC 2012 Edition Section 714 Penetrations

714.3.2 Membrane penetrations. Membrane penetra­tions shall comply with Section 714.3.1. Where walls or partitions are required to have a fire-resistance rating, recessed fixtures shall be installed such that the required fire-resistance will not be reduced.

Exception 5:
The annular space created by the penetration of an automatic sprinkler, provided it is covered by a metal escutcheon plate.

Reply
Sue Byrne
1/7/2019 05:37:57 pm

Kevin, this is exactly what we accept as long as it is a metal escutcheon and it is the escutcheon and fire sprinkler assembly that is making the penetration in the rated wall or ceiling.

Reply
Randy Day
2/5/2019 10:36:47 am

Note that a membrane penetration is not a through penetration, which a sprinkler probably is.

Reply
Franck Orset
1/7/2019 10:53:32 am

Just the point of view from the Insurance Industry (might be other different points of view).
A fire wall or fire partition is a passive protection.
A sprinkler system, deluge system, gas protection systems... are active protections.
In some circumstances, both are required as they complete each other.
Normally the passive protection is a security when there is no fire protection anymore (impairment, overtaxing of the system...).

In your situation, it could be considered acceptable to leave an opening as you will have a sprinkler protection. But you will lose the benefit of the passive protection in case of impairment of the sprinkler system.

I don't know if you are familiar with Normal Loss Expectancy (NLE) scenarios and Maximum Foreseeable Loss (MFL) or Probable Maximum Loss (PML) scenarios, but the adequate fire separation might change them a lot.
In your case, the NLE is the same with or without fireproofing material in the penetration (because the sprinkler system is considered active in NLEs and the fire will be controlled within the room).
But the MFL/PML might be completely different as the fire is considered to possibly spread through the wall if the sprinkler protection is not operational.

It is the same with openings in fire walls that are "protected" with deluge systems/water curtains. For NLE, the protection of the opening with a deluge system is the same as with rated fire doors. But for MFL/PML, the result is completely different (as the opening is considered wide open without protection if no fire door is provided).

Not blocking correctly the opening might have an impact on the final insurance premium and might result in recommendations from the Insurance Company. Even if the pipe is for a sprinkler head.

Reply
Dave L.
1/7/2019 11:09:41 am

^What Kevin said ^
Single membrane penetration per the IBC exception vs. through-penetration.

Reply
Dave L.
1/7/2019 11:12:03 am

...but be careful if you happen to have back-to-back penetrations; I believe that could then be considered a though-penetration.

Reply
Sue Byrne
1/7/2019 05:35:09 pm

In my jurisdiction we allow for the fire sprinkler metal escutcheon in a snug fitting opening making the penetration. This would mean that only metal fire sprinkler escutcheon would be going through the opening. We do not allow fire sprinklers to be fire caulked around. If the pipe is going through the rated wall or ceiling, then the pipe would need to be sealed around appropriately.

Reply
Dale Proctor
10/30/2019 11:23:37 am

Read NFPA 101 (2018) paragraph 8.5.6.4 .

Reply
Patrick Turner
6/16/2020 03:56:36 pm

I understand sprinklers are allowed in fire rated ceilings provided it is covered by a metal escutcheon plate. My question is what provisions are required/allowed in a NFPA 13D system when monitoring the control valve is not required. What if the owner turns the valve off? I would think that would be easily determined during a post fire investigation and the owner would be deemed responsible, but what would waive the sprinkler contractor from that in this case? Asking the insurance agents on here that have responded. Thank you.

Reply
Christina
2/3/2023 02:19:56 am

I have a similar question. If a wet system has a sprinkler head penetrating an exterior wall (insulated metal panel wall outside a mechanical ductwork plenum), is it required to be fire sealed? How much distance does there need to be between the cut opening surrounding the actual pipe? Can the opening be sealed with firestop or sealant? If not, can the sprinkler head have a metal escutcheon plate on the exterior that closes the gap in the opening to prevent air infiltration and the freezing of pipes in extremely cold temperatures (or possible water infiltration by wind driven rain)?

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT