MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Fire Rating for Diesel Pump House Near Barge?

8/18/2022

6 Comments

 
We are designing a barge loading/unloading slip. The product will be used motor oil. The barge slip will be protected by fire monitors. These will be supplied by a fire water pump house.

Due to space limitations, the pump house will be within a 50-ft radius of the corner of a barge (potential fire source).

The pump house will enclose two diesel pumps and day tanks and will be sprinkler protected. Only three walls of the pump house will fall within the 50-ft circle.

Question 1) NFPA Table 4.13.1.1.2 would dictate a 2-hour fire-resistance rating needed, but the IBC would lead you to believe a 1-hour rating is required. Can someone clarify which is required?

Question 2) Do all the walls and the roof need to meet the rating?

The simple solution would be to make everything a 2-hour rating. However, the pump house will have a 10'x10' door, roof hatches, and ventilation louvers. Placing these on the wall opposite to the fire source and outside of the 50 ft. circle would greatly simplify the design.

Thank you in advance!

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Chris Nelson
8/18/2022 08:19:39 am

4.14.1.1.2 calls out 4.14.1.1.3 which states:
Fire pump units supplying a local application fire protection system(s) shall be physically separated from the hazard being protected in a manner that will prevent a fire associated with the hazard from directly exposing the pumping unit.

A4.14.1.1.3 has some decent direction which may be helpful:
A.‍4.14.1.1.3
This section allows for the installation of special hazard fire protection systems such as local application water mist inside buildings that may or may not be otherwise protected. The concern is to assure that a fire associated with the process being protected does not cause an immediate failure of the pumping system. It is not the intent of this section to provide protection for the entire building or to protect the process area from an exposure fire involving that building section.

I would think you application doesnt cause immediate failure to the pump system but you know more about it than I do.

Reply
Chris Nelson
8/18/2022 08:23:00 am

But to answer your questions
1) NFPA 25 is the more restrictive so that should be used.

2) The intent is to separate the fire pump from the hazard so I say if the roof of the fire pump house could be affected, its best to rate it.

Reply
Franck
8/18/2022 10:40:14 am

The sprinkler protection would protect from a fire originating inside the pumphouse to possibly limit the damages.
But in your case, your assessment is that you have a fire exposure to tour pumphouse from the outside.
This means that it would be beneficial to provide adequate passive protection.

The 2 hours fire rating is for all exposed surfaces. This means also the roof if it is exposed by an outside fire.
By providing the access door to a wall not exposed would certainly help your design (2 h rated fire doors are not easily found for pumphouse access)

Reply
Glenn Berger
8/18/2022 11:16:03 am

The IBC provides minimum requirements. NFPA 20 should be followed as it has more restrictive requirements.

Reply
Todd E Wyatt
8/19/2022 08:52:59 am

SHORT ANSWER
The fire pump room (FPR) will be protected by an automatic sprinkler system (ASPS) per NFPA 13 as an Extra Hazard Group 2 occupancy (based on the diesel engine pump drivers) and (1) wall within 50 feet from the “fire exposure” (barge) shall be protected by a 2-Hour Fire Barrier (2FB) IF the “fire exposure” is NOT protected by a ASPS or shall be protected by a 1-Hour Fire Barrier (1FB) IF the barge (fire exposure) IS protected by a ASPS per NFPA 20.
Per IBC, the FPR is required to be protected by 1FB and/or 1HA since the FPR is protected by a ASPS.
Depending on the ASPS protection of the adjacent <50 feet “fire exposure”, the FPR shall be protected by 2FB/2HA or 1FB/1HA.

LONG ANSWER
2021 IBC (if this is the applicable, adopted Code) SECTION 913 FIRE PUMPS requires “fire pumps for fire protection systems shall be installed … (per) NFPA 20.”
This section goes on to require the fire pump room (FPR) to be protected by 2-Hour Fire Barriers (2FB) and/or 2-Hour Horizontal Assemblies (2HA) unless (1) the FPR is protected by an automatic sprinkler system (ASPS) then the fire-resistant rated (FRR) assemblies can be reduced to 1FB & 1HA and/or (2) the FPR is physically separated per NFPA 20.

2019 NFPA 20 (referenced by 2012 IBC)
Chapter 4 — General Requirements
4.14.1.2 Outdoor Fire Pump Units.
4.14.1.2.1
Fire pump units that are outdoors shall be located at least 50 ft (15.3 m) away from any buildings and other fire exposures.
4.14.1.2.2
Outdoor installations shall be required to be provided with protection against possible interruption in accordance with 4.14.1.
4.14.1.3 Fire Pump Buildings or Rooms with Diesel Engines.
Fire pump buildings or rooms enclosing diesel engine pump drivers and day tanks shall be protected with an automatic sprinkler system installed in accordance with NFPA 13 as an Extra Hazard Group 2 occupancy.
4.14.1.4 Fire Pump Buildings or Rooms with Electric Drivers.
For buildings that are required to be sprinklered, fire pump buildings or rooms enclosing electric fire pump drivers shall be protected with an automatic sprinkler system installed in accordance with NFPA 13 as an Ordinary Hazard Group 1 occupancy.

4.14* Equipment Protection.
(A.4.14 Special consideration needs to be given to fire pump installations installed below grade. Light, heat, drainage, ventilation, and potential flooding are several of the variables that need to be addressed. Some locations or installations might not require a pump house. Where a pump room or pump house is required, it should be of ample size and located to permit short and properly arranged piping. The suction piping should receive first consideration. The pump house should preferably be a detached building of noncombustible construction. A one-story pump room with a combustible roof, either detached or well protected from an adjoining one-story building, is acceptable if sprinklered. Where a detached building is not feasible, the pump room should be located and constructed to protect the pump unit and controls from falling floors or machinery, and from fire that could drive away the pump operator or damage the pump unit or controls. Access to the pump room should be provided from outside the building. Where the use of brick or reinforced concrete is not feasible, metal lath and plaster is recommended for the construction of the pump room. The pump room or pump house should not be used for storage purposes. Vertical shaft turbine–type pumps might necessitate a removable panel in the pump house roof to permit the pump to be removed for inspection or repair. Proper clearances to equipment should be provided as recommended by the manufacturer's drawings.)
4.14.1* General Requirements.
The fire pump, driver, controller, water supply, and power supply shall be protected against possible interruption of service through damage caused by explosion, fire, flood, earthquake, rodents, insects, windstorm, freezing, vandalism, and other adverse conditions.
(A.4.14.1
A fire pump that is inoperative for any reason at any time constitutes an impairment to the fire protection system. It should be returned to service without delay. Rain, intense heat from the sun, blown freezing rain, blowing sand or dust, flood, rodents, insects, and vandals are adverse conditions to equipment not installed in an acceptable protective building or enclosure. At a minimum, equipment installed should be shielded by a roof or deck.)

Table 4.14.1.1.2 Equipment Protection

Pump Room/House : Fully sprinklered
Building(s) Exposing Pump Room/House : Not sprinklered
Required Separation : 2 hour fire-rated or 50 ft (15.3 m)

Pump Room/House : Fully sprinklered
Building(s) Exposing Pump Room/House : Fully sprinklered
Required Separation : 1 hour fire-rated or 50 ft (15.3 m)

Reply
Patrick Nelligan
8/22/2022 12:22:04 pm

I understand everything above and special thanks to @Todd for the in-depth explanation. However, I have one question regarding Diesel Fire Pump Rooms in a fully sprinklered building. Since they must be designed to EH2 which requires a minimum 90-120 minute water supply duration requirement, should not the walls and ceiling meet those minimum requirements as well? Or am I missing something all together? I guess that is two questions. Thanks for you input.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT