|
A fire sprinkler system for a single building requires a tank for water storage as there is only a well at this project's remote site. We're considering using a diesel pump with a pump house adjacent to an aboveground water storage tank.
What type of fire pump would you recommend for this scenario? The building is only Ordinary Hazard Group 1, so I'm expecting an approximate pump size of 500 gpm, 75 psi, 50 HP. There will not be much suction pressure since the water storage tank will not be pressurized. Posted anonymously by a member for discussion. Discuss this | Submit a Question | Subscribe
11 Comments
RJ
3/13/2019 10:08:15 am
Look at this website: www.talcofire.com I have used these for a project like the one you described.
Reply
Rusty Scott
3/13/2019 10:24:28 am
Had a somewhat relatable project but with a 100 psi, 1,000 gpm horizontal split case fire pump with an elevated tank. Due to structural cost reasons we switched to building a custom concrete type vault under the building and sump and used a vertical turbine fire pump. I would say talk to a pump rep I use Patterson and Peerless alot. Both guys are very knowledgeable and deal with a large variety of pump projects beyond just fire related. My pump rep's often inform me that when we go below 750 gpm they like to use a vertical in-line pump, but that's also with a city connection and not a gravity tank. Hopefully this is helpful.
Reply
Kelly
3/13/2019 10:29:33 am
You should probably look into the environmental requirements of the site and make sure diesel will not require extra permits or be flat out prohibited in the area. I have run into this in a couple of states - just make sure you coordinate with the civil or environmental engineer on the project.
Reply
John P Malescio
3/13/2019 10:40:14 am
I had a similar project, although it was much larger. I would speak to your fire pump representatives to get a starting point. I had a 150k gallon above ground tank and I used a horizontal split case pump. The NPSH was well above what I needed for the pump even when the tank was 90% empty.
Reply
James
3/13/2019 10:51:15 am
If you have the room for it, a horizontal split case lasts long, is very efficient and easy to service.
Reply
PETE
3/13/2019 11:33:33 am
1) I would make sure that your suction tank and pump don't need to also supply the fire flow demand. I've designed suction tanks that are 450,000 gallons. The supply has to provide the greater of the fire flow and the overhead demand, not both per NFPA 1/ IFC. This is an AHJ question. He/she may not require private hydrants for fire flow on the site.
Reply
WES
3/13/2019 12:49:23 pm
Pete,
Reply
WES
3/13/2019 12:53:02 pm
I see now that the 2015 IFC B105.3 clarified that it is the greater of the automatic sprinkler system, plus hose, or fire flow. Thank you Pete!
Mike
3/13/2019 06:50:04 pm
Diesels in some states need to be Tier 4 emissions. The exhaust system for these is as costly as the pump and driver. Very expensive But sometimes necessary because of lack of electrical supply.
Reply
Danny
3/13/2019 07:40:24 pm
I think it would be wise for anon to hire an FPE to do a complete evaluation.
Reply
Joe Meyer
3/14/2019 06:35:51 am
Danny,
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop Oct '26 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
November 2026
PE PREP SERIES |
RSS Feed
