MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Fire Hydrant Required for Small Remote Building?

3/27/2024

11 Comments

 
I have a project that is a building 10-ft x 20-ft and is used only for electrical equipment. The building is remotely located, 10 miles from the nearest town.

Would a fire hydrant be required for such a structure?

If not, what code exception would allow the omission of a hydrant?

Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Matt C.
3/27/2024 08:42:39 am

I assume you're somewhere in the US, judging by your use of 'miles' haha. I can't speak for any jurisdictional requirements but here in Ontario (Canada), on its own, no there wouldn't be any requirement for a water supply unless the building area exceeded 600m^2 (~6460 sqft). What is your code of reference? IBC?

Reply
Sean Kyer
3/27/2024 08:51:15 am

Yes, it is in the USA, and the project is being built according to IFC/IBC 2018 ed.

IFC starts at zero square feet for each construction type. The building is not meant to be occupied but workers will occasionally enter the building.

Reply
Jesse
3/27/2024 08:47:23 am

This is a great case of your milage may vary. Having worn the AHJ hat in the past, I wouldn't have required a hydrant for a remote 200 sq. ft. building. That merely tank water on the first due Engine Co.

Reply
Richard W Mercer
3/27/2024 08:59:41 am

A few questions:

What is the Construction Code used by the Jurisdiction?

What is the Occupancy Classification of the structure under the Constuction Code?

How far away is the closest hydrant? Or is this a Rural Area not provided with hydrants?

Reply
Dwight Havens
3/27/2024 09:35:53 am

Subject to modification by local law, water supply requirements can be found in IFC, Chapter 5, Fire Service Features. Section 507, Fire Protection Water Supplies is the applicable section. The base requirement is that you have to have an "approved" water supply. Approved means "Approved by the Fire Code Official."

If adopted, Appendix B, Fire-Flow Requirements for Buildings applies. If not adopted, it can be used as guidance by the Fire Code Official in approving the available water supply in accordance with Section 507. Section B103, Modifications, is the section commonly used to address the question you raised. As you can see, under the IFC, it is up to the Fire Code Official to make the final determination, unless the local requirements allow an appeal to a higher authority.

Reply
Conrad
3/27/2024 02:47:33 pm

As Dwight stated, Appendix B is useful for IFC jurisdictions.
I have seen approval for remote buildings that are other than one and two family dwellings where the design is similar to a 200-400 sq ft building (like a shipping container) with 10-30 ft clearances to combustibles (gravel is popular) and fire extinguisher(s) on the plan.

IFC Appendix B Section B103.1 Decreases
The fire code official is authorized to reduce the fire-flow requirements for isolated buildings or a group of buildings in rural areas or small communities where the development of full fire-flow requirements is impractical.

In case the jurisdiction follows NFPA 1:
18.4.3.1 Decreases in Fire Flow Requirements
18.4.3.1.1*
Fire flow requirements shall be permitted to be decreased by the AHJ for isolated buildings or a group of buildings in rural areas or suburban areas where the development of full fire flow requirements is impractical as determined by the AHJ.
18.4.3.1.2
The AHJ shall be authorized to establish conditions on fire flow reductions approved in accordance with 18.4.3.1.1 including, but not limited to, fire sprinkler protection, type of construction of the building, occupancy, development density, building size, and setbacks.

Reply
Jack G
3/27/2024 09:56:01 am

IBC table 102 requires /1 hydrant.
If you are doing that then I d install sprinklers also.
At a .15 it comes to about 30 gpm. About 2 k gallons.
Maybe a pressure tank.
I d install a fdc at street to a hydrant near the building. Install sprinklers off the main.
Install a small pressure tank with supervisory water off the tank.
Automatic fill from the well.
Had to do this for a day care center in the middle of no where.
Worked. Had 2 kitchen fires. Put out the fire and automatically refilled.
Expensive!

Reply
Wes
3/27/2024 10:01:34 am

IBC Table 102?

A larger daycare center (much more critically occupied building) with a kitchen would make a little more sense to protect than a remote electrical building, in my opinion. My guess is the daycare center was required to be sprinkler protected, whereas this application would not be.

Reply
Glenn Berger
3/27/2024 09:59:32 am

This subject is one that the authorities will give a more direct requirement of rules to be followed.

I do not expect that once a fire respondent arrives on site that there will be anything left to save.

Reply
Todd E Wyatt
3/27/2024 11:15:26 am

SUMMARY
Coordinate with the AHJ (e.g. Fire Marshal) the requirements for the fire protection water supply per IFC-2018 based on the building’s Occupancy Classification(s) (OC) and/or Specific Building Areas and Hazards which determines where an automatic sprinkler system (ASPS) is required.

EXPLANATION
The adopted scoping Code (e.g. IBC-2018) determines where an automatic sprinkler system (ASPS) is required to be installed based on the building’s Occupancy Classification(s) (OC) and/or Specific Building Areas and Hazards (per IBC-2018 903.2.1 - 903.2.11)

IBC-2018 903.2 Exception permits the exclusion of an ASPS in “… spaces or areas in telecommunications buildings …” but this may not be applicable to your Project.

Based on the assign OCs, the project may not require an ASPS so the associated “FIRE DEPARTMENT CONNECTIONS” for the ASPS per 903.3.7 is not applicable.

Review of the IFC-2018 Chapter 5 Section includes references to “FIRE DEPARTMENT CONNECTIONS” but only those associated with “Hydrant for standpipe systems” (505.5.1.1) and in the Fire Command Center (508.1.6. (13.6)).

IFC-2018 includes requirements for “Fire Protection Water Supplies” which includes 507.5 Fire Hydrant Systems and where they are required (507.5.1).


Reply
Todd E Wyatt
3/27/2024 11:15:52 am

REFERENCES
IFC-2018
507 Fire Protection Water Supplies
507.1 Required Water Supply
An approved water supply capable of supplying the required fire flow for fire protection shall be provided to premises on which facilities, buildings or portions of buildings are hereafter constructed or moved into or within the jurisdiction.
507.2 Type of Water Supply
A water supply shall consist of reservoirs, pressure tanks, elevated tanks, water mains or other fixed systems capable of providing the required fire flow.
507.5 Fire Hydrant Systems
Fire hydrant systems shall comply with Sections 507.5.1 through 507.5.6.
507.5.1 Where Required
Where a portion of the facility or building hereafter constructed or moved into or within the jurisdiction is more than 400 feet (122 m) from a hydrant on a fire apparatus access road, as measured by an approved route around the exterior of the facility or building, on-site fire hydrants and mains shall be provided where required by the fire code official.
Exceptions:
1. For Group R-3 and Group U occupancies, the distance requirement shall be 600 feet (183 m).
2. For buildings equipped throughout with an approved automatic sprinkler system installed in accordance with Section 903.3.1.1 or 903.3.1.2, the distance requirement shall be 600 feet (183 m).
507.5.1.1 Hydrant for Standpipe Systems
507.5.2 Inspection, Testing and Maintenance
507.5.3 Private Fire Service Mains and Water Tanks
507.5.4 Obstruction
507.5.5 Clear Space Around Hydrants
507.5.6 Physical Protection

IBC-2018
Section 903 Automatic Sprinkler Systems
903.2 Where Required
Approved automatic sprinkler systems in new buildings and structures shall be provided in the locations described in Sections 903.2.1 through 903.2.12.
Exception: Spaces or areas in telecommunications buildings used exclusively for telecommunications equipment, associated electrical power distribution equipment, batteries and standby engines, provided that those spaces or areas are equipped throughout with an automatic smoke detection system in accordance with Section 907.2 and are separated from the remainder of the building by not less than 1-hour fire barriers constructed in accordance with Section 707 or not less than 2-hour horizontal assemblies constructed in accordance with Section 711, or both.
903.3.7 Fire Department Connections
Fire department connections for automatic sprinkler systems shall be installed in accordance with Section 912.

Section 912 Fire Department Connections
912.1 Installation
Fire department connections shall be installed in accordance with the NFPA standard applicable to the system design and shall comply with Sections 912.2 through 912.6.
912.2 Location
With respect to hydrants, driveways, buildings and landscaping, fire department connections shall be so located that fire apparatus and hose connected to supply the system will not obstruct access to the buildings for other fire apparatus. The location of fire department connections shall be approved by the fire code official.
912.2.1 Visible Location
Fire department connections shall be located on the street side of buildings or facing approved fire apparatus access roads, fully visible and recognizable from the street, fire apparatus access road or nearest point of fire department vehicle access or as otherwise approved by the fire code official.
912.2.2 Existing Buildings
On existing buildings, wherever the fire department connection is not visible to approaching fire apparatus, the fire department connection shall be indicated by an approved sign mounted on the street front or on the side of the building. Such sign shall have the letters "FDC" not less than 6 inches (152 mm) high and words in letters not less than 2 inches (51 mm) high or an arrow to indicate the location. Such signs shall be subject to the approval of the fire code official.
912.3 Fire Hose Threads
Fire hose threads used in connection with standpipe systems shall be approved and shall be compatible with fire department hose threads.
912.4 Access
Immediate access to fire department connections shall be maintained at all times and without obstruction by fences, bushes, trees, walls or any other fixed or moveable object. Access to fire department connections shall be approved by the fire code official.
Exception: Fences, where provided with an access gate equipped with a sign complying with the legend requirements of this section and a means of emergency operation. The gate and the means of emergency operation shall be approved by the fire code official and maintained operational at all times.
912.4.1 Locking Fire Department Connection Caps
The fire code official is authorized to require locking caps on fire department connections for water-based fire protection systems where the responding fire department carries appropriate key wrenches for removal.
912.4.2 Clear Space Around Connections
A working space of not less than 36 inches (762 mm) in width, 36 inches (914 mm) in depth and 78 inches (1981 mm) in h

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT