The local fire department wants us to document that a facility provides the minimum fire flow for their outdoor mulch storage piles.
I can't find any NFPA requirements for wood chip or mulch storage; only setback distances. Anyone have input on how to establish minimum Fire Flow for outdoor storage like this? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
Chad
11/13/2023 09:47:16 am
Axa has a generic outdoor storage guideline for this. For a calc, I would accept Axa's formula.
Reply
Jesse
11/13/2023 10:17:31 am
I would second Chad's citing of the FM data sheet. I would probably ask the AHJ what fire flow they want and then calc it to see if the supply meets their requirement.
Reply
Franck
11/13/2023 11:09:58 am
FM global is definitely the answer to that question if you consider mulch equivalent to wood chips.
Reply
Dan Wilder
11/13/2023 11:39:23 am
This is textbook Insurance or FPE territory and at a minimum a request from the responding AHJ's as to their SOP.
Reply