Existing ESFR Sprinklers With FM Global Criteria?

1/31/2022

13 Comments

 
We have a project that has carpet storage, per FM Global Sheet 8-30, Table 1. In that table, there are different K-Factor options with corresponding minimum pressures.

The existing sprinkler system has k-16.8 ESFR sprinklers.

My question is whether or not I can utilize the existing k-16.8 ESFR sprinklers and just calculate them to meet the requirements of FM Global?

In this case, it's showing a minimum required demand of 30 sprinklers at only 7 psi. Am I looking at this wrong?

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
13 Comments
Alex
1/31/2022 06:54:57 am

Hi,

Yes, you can utilize the existing system if it works hydraulically.

From your question, I cannot confirm your storage arrangement/height/sprinkler type. But you are reading the table correctly: 20@7 means you need 20 sprinklers operating at 7psi.

Thanks,
Alex

Reply
Franck
1/31/2022 11:21:51 am

No, you can't use ESFR if you are using FM data sheet 8.30. The table is with standard spray sprinklers only.

Reply
Alex
1/31/2022 01:16:51 pm

Hi Frank,

Great catch. Looks like I jumped the gun on my response this morning.

Alex

Jay
1/31/2022 04:33:28 pm

Where does the table say cmda sprinklers are required? FM classifies sprinklers as either storage or nonstorage sprinklers. Many ESFR sprinklers are FM approved storage sprinklers, which can be used in accordance with 8-30 table 1 as a quick response sprinkler.

Glenn Berger
1/31/2022 08:09:56 am

The use of 7 psi for ESFR sprinklers does not sound right. Need to use the required minimum pressure for the sprinkler type utilized.

Reply
Franck
1/31/2022 11:23:03 am

Hi Glenn
This is because the table is not intended to be used with ESFR.
You're fully right, ESFR at 7 psi does not sound good at all...

Reply
Jesse
1/31/2022 08:18:45 am

I just did a rolled carpet storage using FM 8-30.

The answer is "probably not". The FM design criteria are CMSA. That sprinkler is listed for ESFR. They are two entirely separate design approaches being control-mode and suppression-mode. So unless that sprinkler carries a listing for CMSA as well (which it doesn't), it has to be ESFR.

The 7-psi is indeed correct and you're balancing ceiling level sprinklers with the i-rack automatic sprinklers.

While hydraulically you may get it to calc, that ESFR sprinkler is dependent upon its end-head pressure required in its listing. You providing less psi to CMSA sprinklers.

Reply
Jesse
1/31/2022 08:21:09 am

Sorry, my answer was kinda convoluted.

No, you can't use that K=16.8 ESFR sprinkler. You may be able to use a K=16.8 sprinkler but it needs to be listed for CMSA, not ESFR.

My last FM 8-30 project I used K=11.2 with K=8 in-rack

Reply
JI
1/31/2022 08:23:29 am

You are going about this properly, the only two issues I see are the following:

1. Are the current sprinklers FM approved?
2. Are the sprinklers too old to be used and should they be changed out or have representative testing performed? Since ESFRs use fast response elements, it is required after 20 years as per NFPA 25, not sure if FM Global has a similar requirement.

Reply
Franck
1/31/2022 11:24:41 am

No, you can't use ESFR if you are using FM data sheet 8.30.
The table is with standard spray sprinklers only.

Reply
JI
2/2/2022 08:36:09 am

I cannot see where DS 8-30 talks about using only "Standard Spray Sprinklers" only. DS 8-30 says for the automatic sprinkler protection to use ceiling and in-rack sprinklers as per DS 2-0, and DS 8-9. DS 8-9 redirects to the following:

"2.3.3.2.1 Use only FM Approved sprinklers listed in the Approval Guide under the heading of Storage
Sprinklers (Ceiling-Level) for any ceiling-level sprinkler options in this data sheet."

So since this occupancy is storage, and we are using a storage data sheet this leads us to using a storage sprinkler head. For example, the JL17, and ESFR sprinkler, is considered a Quick Response storage head by the FM Approval Guide.

Franck
1/31/2022 11:20:04 am

As indicated by some above, the table 1 is not for ESFR but standard spray sprinkler (in the CMDA mode).

A few years ago, FM Global abandonned the use of density/area to go for a number of operating heads at a given pressure. And they apply that to standard sprinklers (not only CMSA or ESFR).

Roughly, when 30 sprinklers are indicated, this corresponds to the "old" 3000 sq ft area of application, while 20 sprinklers corresponds to 2000 sq ft.
And 7 psi is indicated as this is the minimum operating pressure for a sprinkler. This corresponds to a density of 0.3 gpm/sq ft with K11.2.
And then, as the minimum operating pressure for a spray sprinkler is 7 psi, you have the same pressure demand whatever the K factor above 11.2. Which is strange as the larger the orifice, the better should be the control, but the higher the density required by FM...

As a summary, what you read in table 1 is that you need a minimum density of 0.3/3000 or 0.3/2000 with IRAS, and you need a K-factor of 11.2 or more.

If you have the opportunity to have access to old version of the data sheet, at a time where FM was using density/area, you would find some very different demand... ranging from 0.2/2000 (when one level of IRAS was added for the configuration not requiring IRAS), to 0.3/3000.
With a demand of 0.25/3000 for the cubicle racks arrangement up to 15 ft (ceiling sprinklers only). But the densities of 0.2 or 0.25 gpm/sq ft are not achievable with K11.2 sprinklers, as the minimum operating pressure is 7 psi...


I know this is confusing for those who are used to NFPA 13 approach!
And this leads to many misinterpration in the field when not checked by FM Global engineers !

Reply
Franck
2/1/2022 04:47:11 am

Note also that sprinklers have minimum and maximum operating pressures.
Max is generally 175 psi.
Min is generally 7 psi for spray sprinklers.
But the minimum pressure can be slightly higher depending on the typê of sprinklers.
K25 ESFR can be listed to operate as low as 15 psi, but some other are listed to operate at least at 50 psi.
You need to check the manufacturer's data sheet to find out this minimum operating pressure.

The delivered pressure has an effect on the water droplet size as well as the delivered water spray pattern.
A too high pressure would result in finely divided droplets and non-uniform water distribution.
A too low pressure may result in an unacceptable water velocity and a too small water spray distribution pattern (elliptical shape at very high pressures).
For spray sprinklers, the best results, in term of homogeneous spray pattern, are obtained for a pressure between 0.5 bars (7 psi) and 4.8 bars (70 psi).

As ESFR have a larger orifice, a too small pressure can have adverse effect on the water droplet size and velocity and then on their efficiency to extinguish the fire (which is the aim of ESFR).

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT