MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

ESFR Allowed On Return-Bend?

1/26/2022

9 Comments

 
Are there any restrictions (by code) for using a return bend on an ESFR pendent sprinkler?

We have structure in both directions, with 21-inch deep beams which requires the pipe be installed underneath the beams.

Thanks in advance!

​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Alex
1/26/2022 07:02:59 am

Hi,

Return bends are a type of arm-over where it is piped from the top of the branch line/main (rather than from the side or bottom). This helps avoid sediment and mineral accumulation within the pipe.

Return bends are not required by code for sprinklers with a K-factor larger than 11.2 (NFPA 13 (2013) 8.15.19.5). The thought here is that a larger orifice will allow sediment to pass and not block waterflow.

I believe you are simply wondering if you can use an arm-over to protect underneath an obstruction. If that's the case, yes. Although, as always, you need to make sure the system works hydraulically. You still want to ensure the sprinkler contractor installs the sprinkler per the manufacture guidelines (sprinkler arms parallel with arm over, XYZ).

Thanks,
Alex

Reply
Anthony
1/26/2022 08:01:54 am

As Alex said there no code that says you can't.


Some options:

Can you run the pipe in parallel to the beams?

Maybe do several small (2 heads per side) tree system with lines up in the beam pocket?

I hoping its just a few bays or that's going to be an expensive install.

The return bends are going to kill your calcs.

Best of luck!

Reply
Jesse
1/26/2022 08:08:03 am

The purpose of the return bend is typically with particulate matter occluding smaller orifice sprinklers. Since you're dealing with ESFR that isn't an issue, and there is nothing that prevents you from doing this. However, it does create some hydraulic challenges you need to deal with on the engineering side.

Reply
Emil Ohler
1/26/2022 08:27:38 am

Just a thought, if your piping is installed below the beams could you install the piping low enough to allow upright ESFR's

Reply
JASON YEAGY
1/26/2022 08:33:35 am

I'm assuming your using return bends to attain a desired deflector distance from the deck. My understanding is that as long as the added pipe and fittings are included in the hyd calcs, you'd be able to install ESFR on a return bend....that, or use upright ESFR on sprig.

Reply
Franck
1/26/2022 09:11:38 am

In addition to the comments above, I have already seen such installations in the past.
One of them was related to a retrofit of an existing system, where the initial sprinklers were installed upright and they changed them with pendent ESFR.
As long as the hydraulic calculation with the extra length for fittings works, there is no reason against.

Reply
Jack G
1/26/2022 09:54:05 am

In the past , Walmarts in particular, when arming to an ESFR under units our in pockets with piping like a return bend for deflector distance compliance, I ve found “ you can’t do it with 1 inch “. Run a calc for the flow and pressure you need. Probably 1.5 inch minimum.

Reply
Brian Gerdwagen FPE
1/26/2022 10:20:10 am

In addition to the above guidance, make sure that you do not create an obstruction to the sprinkler of your own branch line piping. I have used return bends on ESFR sprinklers many times in existing construction, but it isn't ever easy.

Reply
danefre
1/27/2022 09:52:15 am

We do it all the time. Branchlines tight to the beam and offset a minimum 1'-2" horizontally away from the ESFR pendent since the branchline is an obstruction. The pendents are installed on a return bend and end-of-line fitting. If you nail the measurements you don't have to hang the armover but you probably should.

Requires additional calcs.

Heads can't be closer than 8'-0 regardless of beam obstructions for most jurisdictions.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT