I'm being asked to provide sprinkler protection for emergency electrical feeders for a highrise hotel. NFPA 70 (2014 Edition) Article 700.10.D.1 states:
"Feeder Circuit wiring shall meet one of the following conditions: 1) Be installed in spaces or areas that are fully protected by an approved automatic fire suppression system." The conduit runs exposed tight to deck, and also through non-sprinklered, non-combustible ceiling cavities. I'm worried that we'll be required to sprinkler the entire concealed space where there is unprotected conduit installed - or would it be acceptable to provide localized coverage? Does anyone have experience with this or know of any guidelines for this application? This is a first for me in my 20-years, historically I've always seen this type of conduit be encased in concrete or handled by one of the other (4) options listed in the NEC. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
Jonathan Sullivan
7/30/2021 08:35:45 am
Interesting question, the NEC commentary states that fire protection is required above and below the ceiling for this scenario.
Reply
Kim
7/30/2021 09:59:12 am
We are sprinkling a new hospital. W/i the FPE drawing, they spec'd "Life Safety Sprinklers" above certain conduit racks.
Reply
Jessica Lutz
8/30/2021 01:26:08 pm
Any updates to your situation?
Reply
James Phifer
8/5/2021 08:56:29 am
We had this exact situation at a prison facility and our AHJ made us conform to the requirements of NFPA 13: (2016 ed) 8.15.1.5
Reply
Jessica Lutz
8/6/2021 01:21:06 pm
Thank you James! This section is very helpful.