Dry-Pipe Water Curtain for Open Parking Garage?

1/19/2023

6 Comments

 
I am working on a 4-story multifamily building that's above a 1-level parking garage on the ground floor.

The exterior wall is less than 10-ft fire separation distance to the property line, requiring the exterior wall it to be 1-hour fire-resistance-rated.

Since it is an open parking garage, I need a lot of openings within this wall to provide ventilation. Denver has an amendment that allows 50% allowable openings with water curtains per NFPA 13.

Since the parking garage will have a dry system, is this even possible?

It seems like a very odd condition but again I need over 25% opening within the wall to comply as an open parking garage.

​​​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Anthony
1/19/2023 07:25:08 am

Assuming you're describing a water curtain as outlined buy NFPA 13-16 8.15.4.1, 15.17.2 and 11.3.3 yes you can use a dry system.

I would however look at a dry(pneumatic) pilot deluge system dedicated to your water curtain(s). otherwise, you'll have to add the curtain to your calc and the pipe sizes will get huge.

Big caveat here: This is not a proscriptive design method in NFPA 13 so you're out on a limb here a bit. I mean to say this sounds like a rule made up by a building official not an FPE. You may want to consult NFPA 80A and 15 as well as FM 1-20.

Reply
Todd E Wyatt
1/19/2023 08:32:35 am

Here is the prescribed requirements for the referenced “Water Curtain’s” per an amendment to 2021 IBC 903.2.11.1.4 :

2022 DENVER BUILDING CODE & DENVER FIRE CODE
Section 903.2.11.1.4 Exterior wall openings is added as follows:
903.2.11.1.4 Exterior wall openings.
Where exterior wall openings are permitted by Table 705.8 of the Denver Commercial Building Code to be up to 50 percent of the exterior wall area openings shall be protected by closely spaced sprinklers, 6 feet on center and located within 6 to12 inches of the wall. The sprinklers shall distribute a minimum of 3 gpm per linear foot of wall opening. The building shall be protected by an automatic sprinkler system complying with the Section 903.3.1.1 or 903.3.1.2. The sprinkler system hydraulic design shall comply with the “Water Curtain” design method in accordance with NFPA 13.

The referenced Table 705.8 limits the maximum allowable area (MAA) of exterior wall openings (EWO) based on Fire Separation Distance (FSD). A FSD of >5-feet & <10-feet permits a 25% MAA of EWO. The Denver amendment (903.2.11.1.4) permits this to be increased to 50% if a “Water Curtain” is installed.

An “open parking garage” requires “two or more sides” to have “uniformly distributed openings” including an aggregate length of openings of not less than 40% of the tier perimeter and an aggregate area of openings of not less than 20% of the tier total perimeter area :

2012 IBC
406.5 Open Parking Garages
Open parking garages shall comply with Sections 406.2, 406.4 and 406.5.
406.5.1 Construction
406.5.2 Openings
For natural ventilation purposes, the exterior side of the structure shall have uniformly distributed openings on two or more sides. The area of such openings in exterior walls on a tier shall be not less than 20 percent of the total perimeter wall area of each tier. The aggregate length of the openings considered to be providing natural ventilation shall be not less than 40 percent of the perimeter of the tier. Interior walls shall be not less than 20 percent open with uniformly distributed openings.
Exception: Openings are not required to be distributed over 40 percent of the building perimeter where the required openings are uniformly distributed over two opposing sides of the building.
Open Parking Garage
406.5.2.1 Openings Below Grade
Where openings below grade provide required natural ventilation, the outside horizontal clear space shall be one and one-half times the depth of the opening. The width of the horizontal clear space shall be maintained from grade down to the bottom of the lowest required opening.

Reply
David T Williams
1/19/2023 09:47:02 am

Often the reason an "open" parking structure is provided is to avoid the costs of fire protection sprinklers and ventilation.... since you already have sprinklers in the structure it would seem that the cost of a ventilation system could be significantly lower than the water curtain you are talking about.

Reply
Brian Cockburn
1/19/2023 10:06:09 am

I've done water curtains on dry systems as you describe quite a few times. They are certainly possible. Every time I've done this there has been a code consultant who prescribed the performance requirements (flow, pressure, k-factor, etc.) so I didn't have to come up with them. I recommend you find a consultant to help you with that as well.

Reply
Franck
1/19/2023 10:09:54 am

I an always confused with the use of water curtains as an alternative to rated fire walls. From an insurance loss prevention perspective, if you need a rated fire wall, it has to be a passive protection, i.e.: independent from your automatic system, including the water supply.
Why? Because if tou have an appropriately designed sprinkler system, you don’t need a rated fire wall, unless your automatic protection is impaired. So having a sprinkler protection for active protection AND water curtain for the “passive” protection does not answer the possible issue of losing the water supply (common impairment for both systems).

Then, if your parking is not sprinkler protected, which could be allowed for open structures, you may have a total loss in your building.
There has been a series of recent events with total loss and hundreds of damaged vehicles in open parking structures.
One interesting loss is the one that happened in Liverpool (UK) on New Year’s night of dec 31 2017. Just google “liverpool car park fire” for more information.

Reply
Glenn Berger
1/19/2023 05:26:09 pm

Yes, providing a water curtain in a dry system is definitely permissible.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top May '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    Nfpa-409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT