Double-Wall Diesel Tank Require a Reservoir?

4/21/2023

16 Comments

 
Does a double wall diesel tank require a reservoir?

​Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
16 Comments
Dan Wilder
4/21/2023 08:16:31 am

Not specifically.

Some of the requirements include a dedicated fuel tank per engine, enough fuel to run for 12 hours (+5% each for expansion & sump) calculated by actual fuel consumption or 1 gallon per HP of the engine (include expansion and sump as well), and consideration of refill availability (larger, remote sites may want to increase the tank size).

Most tanks are rounded up to the next larger size just based on MFG availability/standard fuel tank sizes so there is a little built in as well.

Reply
Dan Wilder
4/21/2023 11:48:03 am

and as I read the other comments leading towards containment not additional fuel storage...ugh TGIF!

ya...see below as it's well covered.

Reply
James Phifer
4/21/2023 08:25:57 am

NFPA 20 2016 ed. 11.4.1.4.4 - Single-wall fuel tanks shall be enclosed with a wall, curb, or dike sufficient to hold the entire capacity of the tank.

There is no mention of a double wall tank needing this requirement.

Reply
Franck
4/21/2023 08:39:45 am

Normally not
Either single wall with curb/dike/... as indicated by James, or double wall with no specific requirement (the double enveloppe act as the retention capacity).
Could be advisable to have a leakage alarm in the double enveloppe (if not discovered and the double eveloppe gap is full, then it becomes a "single enveloppe" ;)

Reply
Jesse
4/21/2023 08:51:35 am

Typically a twin-hulled diesel tank does not require secondary containment

Reply
James Stever Jr link
4/21/2023 08:57:27 am

I would recommend to contact your state Environmental office for their requirements that may superceed some other code requirements from NFPA or local codes

Reply
Todd E Wyatt
4/21/2023 09:11:26 am

“Spill Control and Secondary Containment” for containers and tanks storing flammable and combustible liquids is addressed in the International Fire Code (IFC).

The IFC’s Referenced Standards (Chapter 80) includes (17) references to “tanks” including some of the following :

• API (American Petroleum Institute) : Std 2350— 4th Edition (2012) Overfill Protection for Storage Tanks in Petroleum Facilities, 3rd Edition
• UL 58—2018 Steel Underground Tanks for Flammable and Combustible Liquids
• UL 80—2007 Steel Tanks for Oil-burner Fuels and Other Combustible Liquids—with revisions through January 2014
• UL 142—2006 Steel Aboveground Tanks for Flammable and Combustible Liquids—with revisions through August 2014
• UL 2085—1997 Protected Aboveground Tanks for Flammable and Combustible Liquids—with revisions through September 2010
• UL 2245—2006 Below-grade Vaults for Flammable Liquid Storage Tanks

NFPA 30 Flammable and Combustible Liquids Code provides additional requirements for aboveground tank systems for the control of spill prevention and secondary containment.

Reply
Sunil Kumar
4/21/2023 09:33:41 am

Not Really..

Double wall is requirement is to contain the spillage/potential pool fire risk.

As long as you have adequate storage (ofc, including expansion & sump)n nothing extra is needed. I usally also provie 5-10% extra to account weekly test. Local client requirement will goversn for duration and more stringent as compare to NFPA in this reghards.

Reply
Connor
4/21/2023 10:08:03 am

This is a case where local environmental regulations will most likely govern. Most above-ground tanks containing petroleum products are subject to containment requirements, and whether or not the double wall counts as containment may depend on whether you have certain features like leak detection in the interstitial space, fill level sensing, etc.

Reply
Ivonn link
4/21/2023 10:58:08 am

If your project is with FM Global insurance , you need the double wall tank and a curb, or dike sufficient to hold the entire capacity of the tank plus one or two inches. I have seen this requirement in some specifications but is not a requirement from NFPA 20 or the local AHJ.

Reply
Panos
4/21/2023 02:01:56 pm

I once asked the FM Global guy why they require both double wall and a spill containment curbing for steel fire pump tanks.

He replied that they have recorded cases where some idiot inadvertently emptied an indoor tank inside the fire pump room while checking the secondary wall test drain!

Reply
Zack H
4/24/2023 12:29:51 pm

Thank you for this extra information. When I asked FM the same question, I got crickets in return, but I can unfortunately see that happening.

Sean Andrew Fallows
4/21/2023 01:40:29 pm

no. the second wall acts as the containment.

Reply
Andy D. link
4/26/2023 08:58:04 am

That depends upon the local codes. Double walled fuel oil tanks normally do not need any tertiary containment. The location of the tank (underground or above grade, lowest floor or upper floor of a building, etc) For diesel installations, a small day tank, installed locally, receives fuel from the main storage tanks (in NY the day tank is limited to a maximum volume of 275 gallons) .

Reply
MICHELE RIVAROLA
4/26/2023 10:57:09 am

Double walled tanks do not require additional containment but they require a drain and a leak detector

Reply
Phil Watkins
4/30/2023 03:46:31 am

Would depend on local environmental regulations which I would expect to supersede NFPA codes.

For example, in the UK the Government publishes guidance and requires a retention bund 110% capacity even when a double walled fuel storage tank is used.
They also ask for trays to catch spills from the filling point.

This is usually simple enough to do when the tank is remote from the pump set, but a bit trickier when the tank is part of the pump skid.

Hope that helps

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT