MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Does "Vertical Change in Elevation" Affect ESFR?

4/20/2023

7 Comments

 
Does NFPA 13 2022 Section 10.2.6.1.1.3 about "Vertical Change in Ceiling Elevation Greater Than 36 in." apply to all types of sprinklers?

I have a contractor who argues that the paragraph does not apply to ESFR sprinklers.

The design has a change in elevation of 14-feet and the last sprinkler on the high-bay side is 8'-4" feet horizontally from the vertical plane. 
Picture
Thanks for helping settle the disagreement here. 

​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Tim
4/20/2023 08:12:14 am

Chapter 10 is for standard uprights and pendents. Section 9.5 applies to ESFR except where modified by Chapter 14.

14.2.1 General.

All requirements of Section 9.5 shall apply except as modified in Section 14.2.

Reply
Brian Gerdwagen
4/20/2023 08:16:46 am

Perfect answer. Chapter 10 does not apply to ESFR.

Reply
Jesse
4/20/2023 08:25:46 am

He's right. This doesn't apply to suppression mode sprinklers.

Reply
Todd E Wyatt
4/20/2023 08:33:33 am

Tim is correct ...

As a former AHJ, we used to call this "cherry picking" from the Code and/or referenced Standard.

Some Design Professionals will respond to an AHJ-identified noncompliance issue by finding a portion of the Code and/or Standard that supports their argument BUT is not applicable. We then have to explain how to reference the Code and/or referenced Standard as well as explaining that referenced Standards (e.g. NFPA 13) are only applicable as defined by the scoping Code (e.g. IBC)

As you pointed out, this Standard’s subsections (e.g. 10.2.6.1.1.3) is part of “Chapter 10 Installation Requirements for Standard Pendent, Upright, and Sidewall Spray Sprinklers.”

ENHANCED CONTENT
Chapter 10 contains the specific requirements for the installation of standard pendent, upright, and sidewall sprinklers. The requirements in this chapter are in addition to the general requirements found in Chapter 9 and contain more detailed requirements regarding the spacing, deflector position, obstruction rules, and clearance requirements applicable to these types of sprinklers. These requirements had been contained in Sections 8.4, 8.6, and 8.7 of the 2016 edition and were then moved to create Chapter 10 for the 2019 edition.

“10.1 General” states “Standard pendent, upright, and sidewall sprinklers shall be selected for use and installation as indicated in this chapter and shall be positioned and spaced in accordance with Section 9.5.”
“10.2” subsection is for “Standard Pendent and Upright Spray Sprinklers.”
“10.2.6” sub-subsection is for “Deflector Position (Standard Pendent and Upright Spray Sprinklers)”
10.2.6.1 Distance Below Ceilings.
10.2.6.1.1 Unobstructed Construction.

... until we finally get to the referenced sub(x5)section :

10.2.6.1.1.3
The requirements of 10.2.6.1.1.1 shall not apply for light and ordinary hazard occupancies with ceilings of noncombustible or limited-combustible construction where either 10.2.6.1.1.3(A) or 10.2.6.1.1.3(B) applies.

Reply
James Evans
4/20/2023 08:37:51 am

In my book the sprinkler at 8'2" off the wall is over spaced. In too many situations there would be a rack at that elevation change either with this owner or with future tenants. It is always the best practice to space to that much of an elevation change no matter what the code indicates. This is not "good design".

Reply
Casey Milhorn
4/20/2023 02:23:43 pm

In laymen's terms the 3' elevation change rule is a common sense exception allowed for light and ordinary hazard occupancies only, and only up to 3'. Over 3' wouldn't be allowed for light and ordinary, so why would it be okay for storage/ESFR type occupancy or sprinklers? Activation time, the sprinkler activating nearest the heat source, and coverage are all issues at play here. NFPA many times says as much by NOT saying anything as to saying something. The intent of NFPA 13 is clearly to not allow what you have drawn in your schematic.

Reply
Panos
4/20/2023 02:24:47 pm

After a second look at the Standard, it seems to me that sub 10.2.6.1.1.3 is probably not the best subsection to justify that the specific design is not correct.

The whole 10.2.6.1 section is about Distance Below Ceilings.

Section 9.5.3.2 Maximum Distance from Walls however goes:

"9.5.3.2.1 The distance from sprinklers to walls shall not exceed one-half of the allowable maximum distance between sprinklers."

The last sprinkler is more than 6 feet from the wall, not complying. Can't think of a way to go around this section.

I agree with James.


Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT