We're designing an ESFR system for a warehouse where the city water can supply enough to meet our 2,000 gpm demand, but the local ordinances prevent a fire pump from being supplied directly by city water lines.
We are planning to install a 13,000 gallon bolted water tank for this reason. NFPA 22 (2013 Edition) Section 4.1.4 allows tanks to be sized so that the store supply plus automatic fill can support demand over the required duration. However, Section 4.1.5 requires break tanks to be sized for a 15-minute duration of 150% of the fire pumps rated capacity. 13,000 gallons is enough to supply our demand with the added city refill rate, but is not enough on its own for a 15-minute pump supply duration. Does Section 4.1.5 apply to my situation? I'm not using an actual break tank, but the bolted tank is being used in a break tank-like fashion. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
Dan Wilder
11/15/2023 07:23:08 am
By definition, a Break Tank is a tank providing suction to a fire pump whose capacity is less that the fire protection demand (flow x duration) so if the tank isn't providing the full capacity, you'll need to comply with the other provisions.
Reply
Jesse
11/15/2023 08:10:24 am
Agree with Dan, I think you'll need to comply with the local break-tank requirements
Reply
Steven H.
11/15/2023 08:58:44 am
Agreed with Dan and Jesse. Take a look at NFPA 22: Section 14.5.1 -- it looks like your tank is being used to meet one of the first two items listed.
Reply
Adam
11/16/2023 06:51:24 am
As I understand it, a break tank is used to break the connection to the municipal water supply. It sounds like this is a true break tank.
Reply
Sean
12/31/2023 11:31:25 pm
not allowing direct supply does not make sense why?
Reply