MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Does Draftstop Require Firestopping?

11/11/2022

5 Comments

 
We are a sprinkler contractor running into a new situation for an apartment building. The apartment is designed under NFPA 13R.

We have an inspector requesting that we firestop a draft stop from the corridor into an apartment.

Can you point us in the right direction whether this is required?
Picture
Thanks in advance for your help.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
Adam
11/11/2022 08:25:54 am

In Ontario Canada, the concealed open space caused by open web joists, or by roof trusses, is required to be split up into areas of certain square footages, and this 'draft stop' would be referred to as a fire block, which is of fairly minimal construction, and generally doesn't have a Fire Resistance Rating associated with it.

When it comes to penetrations, though, it does require fire stopping. Oddly enough though, ducts do not require fire dampers.

A bead of Hilti or 3M fire stop sealant does the trick.

Reply
Todd E Wyatt
11/11/2022 09:15:23 am

SUMMARY
If the floor/ceiling assembly is an approved 1-Hr fire-resistance rated (FRR) Horizontal Assembly (HA) separating the dwelling units and meeting the Type of Construction FRR requirements for the Floor Construction, firestopping the draftstop inside this FRR HA is NOT required.
Draftstops are not required to have a fire-resistance rated (FRR) but instead are required to “restrict the movement of air”. Penetrations in draftstops would only be required to “restrict the movement of air”.

EXPLANATION
Draftstopping is used to restrict the movement of air (e.g. smoke) in concealed, combustible spaces.
2021 IBC
DRAFTSTOP. A material, device or construction installed to restrict the movement of air within open spaces of concealed areas of building components such as crawl spaces, floor/ceiling assemblies, roof/ceiling assemblies and attics.

Fireblocking is used to control the migration of flame in concealed, combustible spaces.
2021 IBC
FIREBLOCKING. Building materials, or materials approved for use as fireblocking, installed to resist the free passage of flame to other areas of the building through concealed spaces.

Firestopping is used to seal around openings (through penetrations & membrane penetrations) and at joints in a fire-resistance-rated (FRR) wall or floor assembly. Firestops maintain the FRR of a wall or floor assembly intended to impede the spread of fire and smoke.
2021 IBC
MEMBRANE-PENETRATION FIRESTOP. A material, device or construction installed to resist for a prescribed time period the passage of flame and heat through openings in a protective membrane in order to accommodate cables, cable trays, conduit, tubing, pipes or similar items.
MEMBRANE-PENETRATION FIRESTOP SYSTEM. An assemblage consisting of a fire-resistance-rated floor-ceiling, roof-ceiling or wall assembly, one or more penetrating items installed into or passing through the breach in one side of the assembly and the materials or devices, or both, installed to resist the spread of fire into the assembly for a prescribed period of time.

Per 2021 IBC, a Dwelling Unit (“A single unit providing complete, independent living facilities for one or more persons, including permanent provisions for living, sleeping, eating, cooking and sanitation.”) and/or a Sleeping Unit (“A single unit that provides rooms or spaces for one or more persons, includes permanent provisions for sleeping and can include provisions for living, eating and either sanitation or kitchen facilities but not both. Such rooms and spaces that are also part of a dwelling unit are not sleeping units.”) in a Group R Residential occupancy are required to be protected by Fire Partitions (FP) with a fire-resistance rating (FRR) of 1-Hour or 0.5-Hours in buildings of Types IIB, IIIB and VB that are also protected by an automatic sprinkler system (ASPS). Fire Partitions (FP) unlike Fire Barriers (FB) are not required to extend to the underside of the floor construction but are permitted to terminate at a floor/ceiling assembly having the same FRR as the FP. FPs are required to be supported by construction having the same FRR as the FP except in buildings of Types IIB, IIIB and VB that are separating dwelling units and sleeping units from Group R-1 and R-2 occupancies.

In the example provided, the dwelling unit’s FP terminates at the underside of a floor/ceiling assembly. The unknown is the FRR of the associated floor/ceiling assembly … let’s assume it is also 1-Hour.

The Type of Construction (TC) of the building (see IBC Table 601) also determines the required FRR of the Primary Components including the Floor Construction (e.g. Horizontal Assembly – HA). The TC is determined to comply with the building’s Occupancy Classification(s) (OC) which relates to the allowables including maximum building area (by story), maximum number of stories, and maximum building height. Let’s assume the Floor Construction is 1-Hour. This would mean the building is either Type IIIA (exterior walls noncombustible & interior building elements are any material permitted) or Type VA.

2021 IBC 708.4.2 Fireblocks and Draftstops in Combustible Construction includes the prescriptive requirements for fireblocks & draftstops where “where fire partitions (that) do not extend to the underside of the floor or roof sheathing, deck or slab above” in combustible construction. 708.4.2 includes (5) exceptions that should be reviewed to see if they are applicable.

Lastly, NFPA 13R is permitted in Group R occupancies per 2021 IBC 903.2.2 where the building meets all the following conditions :
1. Four stories or fewer above grade plane.
2. The floor level of the highest story is 30 feet (9144 mm) or less above the lowest level of fire department vehicle access.
3. The floor level of the lowest story is 30 feet (9144 mm) or less below the lowest level of fire department vehicle access.

Reply
Eric R
11/11/2022 09:54:49 am

To add to this, you'll want to make sure that the construction of the corridor FP membrane meets the requirements of 708.4. In the drawing provided, it looks like the apartment side of the wall conforms with a standard UL FRR sketch, but if the corridor ceiling is not constructed in the same arrangement as the corridor wall it is possible that the membrane in question is not actually a draftstop, but instead is a continuation of the corridor's fire partition membrane.

Also, the code language for draftstops includes a line requiring the integrity of the draftstop to be maintained. So even if it doesn't require a rated firecaulk, the penetration should probably still be stuffed with some insulation.

Either way, a quick run of firecaulk seems like a simple enough add compared to a potential argument with the AHJ slowing down the project.

Reply
Cesar Flores
11/11/2022 10:08:40 am

If it's a 13r per my knowledge you consider the concealed space. If it's design 13r.

Reply
sean
11/12/2022 07:25:36 am

this is coming from chapter 7 of the IBC. But in a NFPA 13R system if the draftstopping is ommited then sprinkler protection is required in the concealed space.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT