Does an In-Building Riser require a thrust block?
I commonly see either mechanically-restrained pipe and fittings, or, an In-Building Riser (IBR) used when a fire service stubs into a building. Is a thrust block required for the IBR? https://www.watts.com/products/plumbing-flow-control-solutions/risers/ibr2 I can't seem to find any verbiage on the product data for Ames' IBR one way or another. Thanks for clarifying my confusion here. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Alex
4/29/2022 07:24:36 am
Hi,
Reply
Ryan Hinson
4/29/2022 09:00:42 am
The IBR itself, is considered restrained since it meets the criteria set forth in NFPA 24 (2013) Section 10.8.1.1 which requires compliance with EITHER Section 10.8.2 - thrust blocks, OR 10.8.3 - restrained joint systems.
Reply
Glenn Berger
4/29/2022 08:13:03 am
I would provide the thrust block. Typical a non-restrained joint will be placed at the 5 foot connection point to the exterior water supply and just a flanged or groove connection just above the building floor. I do not consider either of these as being truly a restrained or fused joint.
Reply
Eric
4/29/2022 09:36:56 am
By the code and spec sheet, Alex has the answer already. However from a real-world standpoint I feel it would depend on if you are installing just the IBR and another contractor would be connecting to it and installing the remainder of the underground piping, or if you have ownership of the entire underground scope of work. If you only have partial ownership I'd put in a thrust block as insurance, since you have no control over what happens to the other side of the connection.
Reply
Wes
4/29/2022 09:39:01 am
Eric - really appreciate your input here. Alongside Glenn Ryan & Alex's input I've already learned a lot this morning!
Reply
Ken Thackery
4/29/2022 10:34:50 am
NO! We have put 100's of these in the ground over the last 30 years, none have come out of the ground. Don't try to overcode this because of lack of experience, don't worry about the rest of the UG line if you're not contracted to install it. Rod the IBR to the UG pipe. Not required by any code, stop trying to change it lol.
Reply
Wes
4/29/2022 10:36:40 am
Asking for knowledge Ken; not trying to change anything. : )
Reply
Jack G
4/29/2022 01:50:30 pm
The underground to the building riser must be fully restrained to prevent separation along the push on joints. Nfpa 13,24.
Reply
Casey Milhorn
4/29/2022 03:16:15 pm
I agree with ALMOST everyone on this. If you are installing all of the fire line, then do what needs to be done to restrain it. Rod and/or thrust block. A little common sense goes a long way here. If you are only doing the 5' out, I would definitely rod AND thrust block. If the utility contractor fails to connect to your rods, then you still have the TB to at least keep your end from pushing out. Who knows how much abuse the run-in is going to see during concrete pour, site traffic, and the utility contractor when connecting. This applies to even the SS lead-ins in my book. Don't ever assume the utility contractor knows what they are doing.