MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Does a Duct Near Ceiling Need Sprinkler Above?

1/31/2024

11 Comments

 
I understand if a duct is wider than 4-ft (1 m) that there needs to be a sprinkler under the duct.

But what if the duct is just below the ceiling? Does a sprinkler also need to be above the duct?

I have a group of ducts with a combined with of 16'-6" (5 m) with the highest point of the duct 10 inches (25 cm) under the ceiling.

Does there need to be a sprinkler above and below the ducts?

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Anthony
1/31/2024 08:07:30 am

Plain reading of code says yes. You might be able to convince an AHJ that its not necessary in non combustible construction. A few points to keep in mind: the possibility of a fire inside the duct, more probable activation of the sprinkler due to the height, and the protection of the structure in relation to escape time for the occupants.

Reply
Patrick Drumm
2/2/2024 12:06:12 pm

Anthony, which code section would you be referring to? My initial thought was the answer to this question is no, because you are covering floor space, but I could be convinced if I had a code reference or specific language to reference.

Reply
Patrick Drumm
2/2/2024 12:20:42 pm

Apologies Anthony, with a little more thought I think I understand where you were going. You're probably asking, "If the duct is 10" below the deck and spanning 16'-6", how do you meet the 1" to 12" deflector below ceiling requirement for unobstructed construction, or the 1" to 6" below the structural members up to a maximum distance of 22" for obstructed construction. In that case, how to you meet the deflector requirements? Code dictates heads above and below, but I understand all the commonsense arguments against below.

Reply
Glenn Berger
1/31/2024 08:24:02 am

This is a simple case of needing to evaluate the obstruction caused by ductwork with respect to sprinklers to the side of the obstruction.

I cannot provide a specific answer until I know where sprinkles are placed within the room.

Reply
Amod kumar Singh
1/31/2024 08:38:43 am

following

Reply
Dan Wilder
1/31/2024 08:40:27 am

What hazard and how deep are the ducts?

My thought is since sprinklers would likely be required in the middle of the total obstruction width (maybe you could use 2 on the sides with arm-overs under to get the spacing <15' (4.5 m) pending hazard spacing requirements), but dropping a sprinkler at the ceiling and another in the middle beneath the obstruction should not be too far out of the normal path and may provide a better layout pending branch line direction (it would be completely obstructed . I would keep the adjacent sprinklers close to the side of the duct to minimize the total ceiling level spacing (or lack of).

Common sense would say that the 10" clear (9" more than likely with deflector distance) provides no useable protection so it's omission would not be a loss but getting an AHJ to buy off on that is a whole other process.

I don't think there is a specific section defining this however, 13-19' - 9.5.5.3.1.5 allows sprinkler omission below obstructions that are 24" (<600 mm) or less above the floor or deck, that may be one option to help argue not putting sprinklers above the duct outline.

Another thought may be anything greater than 18" (450 mm) below as that is delineation between use of the obstruction tables and when obstructions are only considered when over 48" (1.2 m) wide. You're providing protection below so nothing above isn't going to reduce total protection.

Third may be calculating the space above the duct and argue that a ceiling pocket allowance allows up to 1000 FT³ (28 m³) (essentially available hot gas collection) without protection so another + as to omission of protection above that duct that is already "addressed", while not specific to this application.

Reply
Franck
1/31/2024 09:44:13 am

With the duct only 10 in. below the ceiling, you will have problems to provide your pipes and sprinklers on top of it + hangers...
No to mention the fact that the water distribution pattern from the sprinkler located in this tiny place will not be ideal... Remember the 18 in. rule between the deflector and the top of any storage/combustible element to protect... Dan pointed it out (but then you still need to convince the AHJ).

If the roof is non-combustible and you don't run cables or other combustible element above the ducts, I won't protect it above. But certainly below.
And consider the obstruction from the sides of your ducts for the other sprinklers in the area that will be placed at the ceiling level.

Reply
Jesse
1/31/2024 10:23:53 am

It would be good to know the building construction. If this is a NC building and the duct is up at the deck, I don't see a benefit in protecting above it. The duct will inhibit the spray pattern from developing.

Reply
Dave
1/31/2024 11:00:48 am

I agree with Franck here (when would I NOT agree with Franck?), You are protecting the floor area, not the top of the duct. Once the obstruction exceeds 4 ft wide, it becomes problematic. Even if you did have the 18 in. to develop the spray pattern above, that is a large shadow area below the sprinklers. Is there any space (or can you negotiate a space) between the individual ducts? I have sometimes been allowed to use the fairly new 9.5.5.3.1.2(2) (2019 ed.) placing a pendent sprinkler between and just below the ducts not more than 3 in. from the edge(s) of the obstruction(s).

Reply
DE
1/31/2024 01:46:11 pm

Agreed 100%. Just a note, if you do use that section, the sprinkler needs to be intermediate type. Got caught on that before!

Reply
David Rowe
1/31/2024 11:38:57 am

One of the sprinkler vendors did a webinar a couple of years ago addressing this question and I think he made a good point. Where's the heat going to go? Obviously heads above the duct are seriously obstructed, but if the heat bypasses the heads beneath, how long might it take for those heads to eventually actuate? But if the heat gets to a head above the duct, even though it may not provide good coverage, at least we set off a flow switch and get the fire department rolling.

I believe that's the reasoning behind the rules for cloud ceilings. If the area around the cloud exceeds 20% of the total ceiling area, heads are required above and below. If you replace the word "duct" with "cloud" in your scenario, the answer seems much clearer.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT