Does a Clean Agent Room Count as Protected?

11/26/2018

10 Comments

 
There's many code contingencies that depend on a fully-sprinklered building. If a room within a fully-sprinklered building is protected with a clean agent system (per NFPA 2001) and sprinklers are omitted from that room, does the building still meet the criteria to be considered fully protected and qualify for the numerous code contingencies?

Posted anonymously by a member for discussion. Discuss this | Subscribe.
10 Comments
Adam Hicks
11/26/2018 10:23:31 am

F

Reply
Kendall Nightlinger link
11/26/2018 10:33:38 am

The building would not count as Completely sprinkled, therefore would not count for allowances during building area analysis, nor for increases in MAQ.

From a FPE standpoint, clean agent is a "1 and done" discharge and does not provide for any of the effects that a sprinkler system does, nor for the required protection durations for building protection.

Clean agent systems are typically only equipment event protection as they try to prevent catastrophic equipment damage.

Good suppression design will provide a double interlock precaution system in addition to the clean agent system. Or a traditional wet pipe system, if there are concerns about water damage when there is no event, specify sidewall heads of an intermediate temperature with head guards.

This design provides extra time and a safety cushion with the intermediate temperature ordinary response heads.

This should alleviate All concerns about unnecessary damage to equipment as if we've created enough heat to activate an intermediate temperature ordinary response head, the equipment is toast anyways.

Reply
Michigan
11/26/2018 10:35:15 am

We are an IFC location, under IFC, a system complaint with NPFA 2001 without a NPFA 13 system in the room does not meet the requirements of fully sprinklered building. This also means that any Building Code "give" for a sprinklered building would not be applicable. I can try to find the code section when I return if that is necessary.

Reply
Michigan
11/26/2018 10:37:25 am

IFC 2015 edition, 903.3.1.1

Reply
sean
11/26/2018 11:07:41 am

904.2.1 Restriction on using automatic sprinkler system
exceptions or reductions. Automatic fire-extinguishing
systems shall not be considered alternatives for the purposes
of exceptions or reductions allowed for automatic sprinkler
systems or by other requirements of this code.

Reply
Pari
11/26/2018 10:51:34 am

IFC ,Section 904.2.1 : Automatic fire - extinguishing system shall not be considered alternative for the purposes of exceptions or reductions allowed for automatic sprinkler system or by other requirements of this code.

So installation of fire sprinkler system required, even the room or space is protection with clean agent.

Reply
Jennifer Olson
11/26/2018 11:14:30 am

What if it is a small telecom closet that the clean agent system is protecting? Would the telecom equipment be considered "electrical equipment" in which if the room is 2 hour rated and only houses dry electrical equipment, it does not require sprinklers and the clean agent is above and beyond?

Reply
Peter
11/26/2018 11:35:42 am

Jennifer, I think it is a stretch of the imagination to define a telecom room, a data processing room or other a low voltage control room as an electrical room for purposes of exempting it from sprinkler coverage under NFPA 13, even with the 2-hr rating and the other 3 criteria in 8.15 being met. The important thing to consider is the reasons we want the "fully sprinklered" designation is to keep fire flow demand low, to keep standpipe demands low, and to lessen the requirements for detection and others under the IFC. A key point to remember is that an exemption for a small area can be approved by the AHJ. If the AHJ is completely unwavering in his application of the code, then we can add a double-interlock preaction system with dry-pendent sprinklers to the clean agent protected area, and still have a reasonable degree of certainty that the room will stay dry. Yes, it will be at an additional expense to the owner, and yes- it will be beyond our control.

Reply
Jennifer Olson
11/26/2018 04:09:29 pm

Peter, thank you for your reply-it does help a lot. Since I cannot find a location in NFPA that defines "electrical equipment", what are the reasons that telecom equipment wouldn't be considered "electrical equipment" for this purpose? Is it that there would be more cables that would be a different fire hazard than just electrical wiring and machines?

Peter
11/27/2018 08:25:08 am

Jennifer,
It's a good question. Electrical Equipment is not defined in Ch. 3, and there is no further discussion in Annex A. I am not an absolute definitive source, but my informal interpretation is that it can be reasonably inferred from the terminology that electrical equipment is that equipment that serves the electrical power distribution for the site, or that equipment listed in the matrix under the electrical discipline. It can be further inferred that the reason the exemption from sprinkler coverage was included was to mitigate the loss of power to life safety equipment, such as an electric fire pump, due to sprinkler discharge water causing short circuits in electrical equipment. Also, if you look at 8.15.11.2. (2), the term "dry-type" most likely refers to transformers with coils that aren't filled with oil insulation. You might be able to convince an AHJ that it refers to all electrically-operated equipment (like an electric water heater closet). Of course, if you think that section of the standard could be better worded, there is a process by which you can recommend changes for the next edition.




Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT