MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Does 52,000 SF System Area Apply Horizontally?

12/18/2023

13 Comments

 
We have a car park area which is part of a bigger development that we are sub-dividing into different pressure zones due to it being a very tall building. The three levels of car park in total are less than 65-ft (20 m) high, but they are very long and wide. My question is about sprinkler control valve areas.

I know for ordinary hazard the restriction per floor from one riser is 52,000 sqft (4830 sqm) with no restriction as you go up.

Does that mean for a wide, low-level building, say on 1 level, do we need a system riser for each 52,000 sqft?

This seems pretty onerous to me, as FM Global do not even insist on this. Here in England, the restriction is 12,000 sqm x 10 floors per valve.

I'm being asked by the authorities to allow the valves, but is that restriction of 52,000 sqft (4830 sqm) per valve set on a single floor set in stone?

Can we do something based on hydraulic calculation that is more user friendly?

Thanks in advance.
13 Comments
Glenn Berger
12/18/2023 08:10:59 am

The 52,000 square feet is published in NFPA 13, as such that is the closest to being "set in stone" as possible.

Reply
franck
12/18/2023 08:26:00 am

No deviation allowed.
And I would fully discourage to go further with occupancies like a car park.
If you are in the UK, you should be aware of the big car park fire at Sylvester a few years ago in Liverpool.

Reply
David Kendrick
12/18/2023 09:36:30 am

Researching the reason for the 52,000 square feet might give reason to consider modification.
Originally pipe schedule systems were calculated using pencil, paper, slide rules and logarithmic tables.
There were two spacing rules for fire sprinklers, 130 square feet and 100 square feet.
The maximum number of sprinklers calculated was 400. So Light Hazard, Ordinary hazard I, II & III at 130 square feet times 400 heads is 52,000 square feet.
Extra hazard I & II is 400 heads times 100 square feet for a total of 40,000 square feet.
At the time calculating a system was labor intensive using the technology of the day.
With today's technology that really isn't an issue if the pipe layout is known. However insurance companies risk / loss data is structured around the system size limits.

I was privileged to have worked for two of the men that did a lot of work to creating computer programs that sped up system calculations. Linwood McCool and Hasu Doshi were acknowledged in the NFPA handbook several years ago for their work along with others on the hydraulics committee.

52,000 and 40,000 aren't magic numbers. They're the result of the practical limitations at the time system size limits were set up.

Reply
Kim O
12/18/2023 09:52:06 am

Yes, 52,000 square feet is as large as a system can be on one level. It is in NFPA 13. That's for Light and Ordinary Hazards. It's 40,000 for Extra Hazard.

Reply
Casey Milhorn
12/18/2023 09:55:37 am

I believe there is a proposed change coming to NFPA 13 to increase the areas by 150%. I haven't seen an update on this in the last month or so. Not sure where it currently stands.

I agree if you can calculate it, it should be allowed. The only concern I would have is when a system has to be down for maintenance or modification purposes. There can definitely be an argument about limiting area for that. I like where NFPA 13 currently falls on zoning by floor.

But until NFPA 13 is changed and adopted by the local AHJ (as part of the applicable building code) then you will more than likely be required to keep it under the required sqft area.

Reply
Dan Wilder
12/18/2023 09:59:06 am

As allowed, and depending on which edition year being referenced, yes 52K ft² is the maximum for any single zone regardless of building height or breadth of a structure for the occupancy you stated.

If the zones need to match the ventilation zones, that is more a performance-based approach. This would very likely lower the total system areas to match the ventilation zones which is a common approach for several large footprint occupancies I have worked on in the past.

As Franck was alluding to, anything with car lifts and/or stackers including those newer automated retrieval units, EV parking and/or EV storage should all be reviewed heavily for design approaches including egress, ventilation, suppression, water supply, and drainage.

Reply
Ray Hardy link
12/18/2023 10:10:08 am

Thanks to everyone for your responses- much appreciated. Just to clarify, can a sprinkler control valve set serve risers in individual stair cores, with zone valves on, each covering 52,000 ft2 or is the restriction on the control valve itself covering 52,000 ft2 per floor? If we had one set of control valves covering 2 risers in a stair could we allow 52,000 ft2 x 2 on the same floor with a branch from each riser? Hard to put into words so I hope I’ve made it clear. Thanks again.

Reply
Connor R
12/18/2023 12:44:39 pm

NFPA-13-2019 4.5.1 states "The maximum floor area on any one floor to be protected by sprinklers supplied by any one sprinkler system riser" shall be 52,000 sq ft for Ordinary Hazard.

NFPA-13 defines System Risers as "The aboveground horizontal or vertical pipe between the water supply and the mains (cross or feed) that contains a control valve (either directly or within its supply pipe), a pressure gauge, a drain, and a waterflow alarm device."

This means that if you have exceeded the maximum area that can be fed from any one system riser on a given floor, an additional riser must be provided back to the water supply. The point of connection to the water supply is typically adjacent to the building water service entrance, although some sites will have underground or aboveground water supply loops to feed the fire protection systems.

You could potentially argue for an "express main" type situation where you have one larger riser control manifold at the water service entrance which splits to feed both stairs, although that would leave the whole system vulnerable to being taken offline if anything happens to that single riser. If you're already running a riser up each stair, it is prudent to run them both all the way back to the water service entrance and have separate control valves, waterflow alarms, pressure gauges, and drains for each riser.

In general, if the area per floor exceeds 52,000 sq ft, an additional sprinkler riser is provided back from the water service entrance or from a site water supply main. This would allow up to 52,000 sq ft to be protected by each riser for a given floor for Light and Ordinary Hazard occupancies, for a maximum of 104,000 sq ft split across two systems. Areas beyond that would require additional risers.

Reply
franck
12/18/2023 10:16:46 am

The size limitation is not only for technical reasons related to layout and optimized pipe sizing. Of course systems are better designed today than in the old time of pipe schedule installations. But there is still a financial or risk limit.
As indicated above, it is not uncommon to have a sprinkler system impaired. If your sprinkler system is impaired on 52 000 sq ft (or less) it is a lesser financial / risk exposure than with a much larger installation.
Many insurance companies in the US make loss estimates based on a ´Normal’ scenario (what if there is a fire and everything works as it should), called NLE (Normal Loss Expectancy), and a more critical scenario where one system is impaired (pump, sprinkler riser…), called PML (Probable Maximum Loss).
The larger the sprinkler system, the bigger the PML and the more expensive the insurance premium.

Reply
Jesse
12/18/2023 12:49:39 pm

Yep, the 52,0000 is pretty solid. And all of the reasons described in replies above mine are why

Reply
Dwight Havens
12/18/2023 04:01:14 pm

I think an explanation of the reason for the size limitations would help. This will require research in the NFPA codes and standards, and the building codes that were in effect at the time this requirement was established. My understanding is that the area limitations were based on a desire to minimize the risk presented to the building and the occupants, should a system be out of service. From a code perspective, this limits the resource needed to establish a fire watch, or the need to shut down the use of that portion of a building while the system is out of service. I also seem to remember, early in my career, that the 52,000 square feet, (or 40.000 square feet in some cases) corresponded with the maximum allowable fire area at that time, thus subdivision to limit loss potential was also used.

Reply
Pete D.
12/19/2023 09:20:41 pm

It's per level.
If your structure is 53ksqft per level and 3 levels, you will need 2 risers. If you have a long, narrow structure, and you're slightly over the maximum area allowed per system, it may play in your favor that you're required to add a second system riser from a hydraulic design standpoint. Shorter runs will keep the pipe diameter down.

Reply
sean
12/31/2023 06:06:13 pm

anytime you go over 52k sq.ft. you need to have another system.
Many times once you hit 3 floors you need to start looking at floor control systems from one of the many requirements. It also depends on what version, there have been some recent changes.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT