The IBC Table 722.6.2(1) states that 1/2" gypsum has a fire resistance rating (FRR) of 15-minutes, while 3/8" OSB (the product used for TJI joist webs) is 5-minutes.
NFPA 13-2019 Section 19.3.3.1.5.2(4) Item (10) discusses an exception to hydraulically calculating the system at 3,000 sqft remote area if joist channels are firestopped into volumes not exceeding 160 cubic feet. Most volumes created by composite wood joists are much smaller than the 160 cubic feed stated in the standard, which means that gypsum board would only be required every 4th- or 5th- joist in most situations. However, would the 3 or 4 layers of 3/8" OSB (the web of each joist) across 3- or 4-bays meet the equivalent of the 1/2" gypsum requirement? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
2 Comments
2/17/2022 08:31:17 am
You would have to get performance testing to show that the layers of OSB would be equivalent. Also, they would all have to be placed together and not spaced at 2' on center like TJI typically are.
Reply
Jesse
2/17/2022 09:05:09 am
Agree with Travis. You'll need to get some test data on the combustibility. I think it likely you'll need to either a) extend the design area to 3,000 sq. ft. or b) fill with NC insulation.
Reply