Concerns/Issues in Protecting All-Glass Atrium?

10/26/2022

5 Comments

 
Looking for some insight on a project I'm reviewing.

We have an 1,800,000 sqft storage occupancy with business and assembly mixed in. It has a 2-story open foyer main entrance. The graphic annunciator and fire alarm panel are in the same location.

My problem is the 2-story space is all glass around the means of egress.

How would sprinkler protection and using the the graphic annunciator work in a all-glass space?

I'm looking to get sprinkler coverage at the glass window, which are floor-to-ceiling. Also, the outside wall in the corner of the building is all glass too.

Looking for insight on how to approach this and any concerns you might have regarding an all-glass space.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
matt
10/26/2022 08:06:59 am

are the walls required to be fire rated as part of the egress corridor? If they are required to be rated, then you can use window specialty sprinklers to achieve a 2hr rating. the sprinklers have very specific requirements for the window construction though - so keep an eye on that.

Reply
sean
11/8/2022 10:58:17 am

unless some very specific requirement came in there is an exception for two story atrium not requiring any special features.

Reply
Alex
10/26/2022 08:27:55 am

Hi,

I would first check with Table 705.5 (IBC 2021 edition) to verify your fire-resistance rating requirements for non bearing exterior walls. Assuming your fire separation distance is greater than 30 feet, your exterior wall does not require a fire rating.

Although, if you are less than 30 feet, and do not meet the fire separation distance and the construction type for 10 to 30 feet, your wall will require a (1) hour rating. If this is the case, I believe using fire rated glass is your best bet. Again, nothing changes for your sprinkler system.

I'm not sure of your question regarding the graphic annunciator. I would install it adjacent to the panel, on a non glass wall.

Thanks,
Alex

Reply
Todd E Wyatt
10/26/2022 09:15:47 am

The first step is to determine IF the scoping Code (e.g. 2021 IBC) requires an automatic sprinkler system (ASPS) for the (3-4) Occupancy Classifications (OC) identified :

A) Group S-1 Moderate-hazard Storage
B) Group B Business
C) Group A-2 Assembly (e.g. Cafeterias)
D) Group A-3 Assembly (e.g. Conference Rooms)

Per 2021 IBC 903 Automatic Sprinkler Systems, these are the requirements for an ASPS by OC :

A) Group S-1 Moderate-hazard Storage
ASPS required IF the Fire Area (FA) >12000 SF or if the FA is >3 stories above grade plan (Not Applicable) or if the FA including mezzanines >24000SF or if the FA is used for storage of commercial motor vehicles and >5000 SF.
B) Group B Business
No requirements for an ASPS.
C) Group A-2 Assembly (e.g. Cafeterias)
ASPS required IF the Fire Area (FA) >5000 SF or if the Occupant Load (OL) is >100 or if the FA is on a story other than the level of exit discharge.
D) Group A-3 Assembly (e.g. Conference Rooms)
ASPS required IF the Fire Area (FA) >12000 SF or if the Occupant Load (OL) is >300 or if the FA is on a story other than the level of exit discharge.

If the B, A-2 and/or A-3 do not meet these requirements and the Owner does not want to provide an ASPS in these areas, the building can be treated as separated, mixed OC. Per IBC Table 508.4, the S-1 OC w/an ASPS (S) would be required to be separated from the non-sprinklered (NS) OCs as follows :

S-1 (S) – B (NS) = No separation
S-1 (S) – A-2 (NS) = 2 Hour Fire Barrier (2FB)
S-1 (S) – A-3 (NS) = 2 Hour Fire Barrier (2FB)

If the entire building is to be protected with an ASPS, these OC separations are not required.

The title of this question (Concerns/Issues in Protecting All-Glass Atrium?) uses the term “atrium” which is not the condition here. “Atriums” are defined as “a vertical space that is closed at the top, connecting two or more stories in Group I-2 and I-3 occupancies or three or more stories in all other occupancies.” The condition you are referring to is a “two-story opening” (TSO) … see Section 712 Vertical Openings, 712.1.9 Two-story openings :

712.1.9 Two-Story Openings
In other than Groups I-2 and I-3, a vertical opening that is not used as one of the applications specified in this section shall be permitted if the opening complies with all of the following items:
1. Does not connect more than two stories.
2. Does not penetrate a horizontal assembly that separates fire areas or smoke barriers that separate smoke compartments.
3. Is not concealed within the construction of a wall or a floor/ceiling assembly.
4. Is not open to a corridor in Group I and R occupancies.
5. Is not open to a corridor on nonsprinklered floors.
6. Is separated from floor openings and air transfer openings serving other floors by construction conforming to required shaft enclosures.

The fire-resistance rated (FRR) protection of this TSO will be required based on 712.1.9 and possibly by the Type of Construction, specifically the FRR of the floor construction.

The “solution” to add a deluge ASPS to the glass surface of this TSO is not applicable since this only available for “atriums” per 404.6 Enclosure of Atriums :

404.6 Enclosure of Atriums
Atrium spaces shall be separated from adjacent spaces by a 1-hour fire barrier constructed in accordance with Section 707 or a horizontal assembly constructed in accordance with Section 711, or both.
Exceptions:
A fire barrier is not required where a glass wall forming a smoke partition is provided. The glass wall shall comply with all of the following:
1.1. Automatic sprinklers are provided along both sides of the separation wall and doors, or on the room side only if there is not a walkway on the atrium side. The sprinklers shall be located between 4 inches and 12 inches (102 mm and 305 mm) away from the glass and at intervals along the glass not greater than 6 feet (1829 mm). The sprinkler system shall be designed so that the entire surface of the glass is wet upon activation of the sprinkler system without obstruction;

Atriums have additional prescriptive requirements (e.g. smoke control) that will add additional costs so defining this as a “two-story opening” (TSO) is recommended.

Reply
Chris
11/1/2022 02:57:38 pm

It is my understanding that if an atrium is 55 ft or taller it does not require sprinkler protection, is this atrium that tall?

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top May '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    Nfpa-409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT